Conext XW PRO 6848 Inverter/Charger
offgridcabin2015
Registered Users Posts: 88 ✭✭
I have decided to buy this in 2022 , in feb. 2022
I Just want to know what will i need to make it work. (Minimum items)
For example i dont' need generator add on . i don't need the distribution panel , I don't need battery monitor. I dont' need internet to monitor . I can wire it up like old school.
Trying tokeep my cost done.
So just wan the MINIMUM guts to make this work with 8 lead acid batts.
Thankyou all + MERRY CHRISTMAS and + be safe out there.
I Just want to know what will i need to make it work. (Minimum items)
For example i dont' need generator add on . i don't need the distribution panel , I don't need battery monitor. I dont' need internet to monitor . I can wire it up like old school.
Trying tokeep my cost done.
So just wan the MINIMUM guts to make this work with 8 lead acid batts.
Thankyou all + MERRY CHRISTMAS and + be safe out there.
Comments
-
If your battery meets the default specs, just plug it in. If you want to control Absorb time or Bulk voltages, 2 stage or 3 stage charging or to read any error codes you need either:
SCP ( system control panel ) lots of push button menus to navigate thru ( least expensive )
Gateway ( extra fancy wifi router with Xanbus inputs and Ethernet outputs. Can stand-alone as a transmit station, or
be wirelessly/wired to a home router. I use my cellphone as a hotspot with mine. A web browser connects to the Gateway and can monitor & modify many functions. Also has some logging functions.
Both connect to the XW Xanbus and are powered from the Xanbus. ( Xanbus is not ethernet, but uses the same cables )
I have both and use them in parallel.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Thankyou mike95490 for your reply. what is the requirement for batts?
-
offgridcabin2015 said:Thankyou mike95490 for your reply. what is the requirement for batts?
Most solar gear comes with an "average" default setting, which is "close to correct" but for longest life of your battery, the subtle tweaks to the settings needs to be done.
What size is your 48V battery ? 8 batteries sounds like they are 6V wired in series.
How will you be recharging the battery ? From the AC1 grid input of the inverter ? From a solar charge controller ?
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mike95490. (thankyou)
So your referring to the battery charge profile then right. i already have that .Thus the inverter will not be set correctly out of box i assume thus i'll need the extra pieces to config this. Thanks for that.
Yes i have Eight 6v batteries now that' ill be using on the new inverter once i buy it in the new year. I'll be taking funds out of my investments for purchase.
I also want to buy the schneidner electric 100a / 600v charge controller. This way i can wire higher voltage in two strings i'm told via the write up on amazon , thus eliminating my current combiner box.
NOt gonna lie kinda excited. do we have any wiring diagrams i can follow to wire them up to this charge controller . i'll be buying 300watt canadian panels 8 more , giving me a total of 12 panels of the same. Hurray. so i assume i can wire them up 6 together in series as one string x 2 strings right?
-
6 kW MPPT 100 600 (Part Number 865-1034). Can show one show me a diagrahm to wire up 2 arrays / 6 panels each . 300watts panels. plz. to this unit. Ty.
-
Even skipping the expense of a combiner and going for the high cost 600V controller, you will need a 600VDC rated disconnect for each PV string, for safety. Don't buy stuff till you price it out both ways
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
And visit your daily load requirements, amount of sun, etc...
More or less, to get the "rated output" of an AC inverter... We have been using the minimum Flooded Cell Lead Acid battery bank size:- 6.8 kWatt * 100 AH * 1/1 kWAtt inverter (48 VDC battery bank) = 680 AH @ 48 VDC FLA battery bank minimum suggested
- 680 AH * 58 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 2,561 Watt array minimum (sunny weather/weekend use)
- 680 AH * 58 volts charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 5,122 Watt array nominal (full time off grid)
- 680 AH * 58 volts charging * 1/0.77 panel+controller deratings * 0.13 rate of charge = 6,659 Watt array "Typical cost effective maximum"
For charging with a genset, around 10% to 20% rate of charge is typical.
A large AC inverter on a "small" battery bank--You will be hard pressed to draw near full output from the inverter.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Q: what can you peeps reccommend for a 600VDC rated disconnect for each PV string, for safety.
-
Midnight solar has some, but they are awfully expensive, getting in the 600VDC range.
That's why I suggested price out a 150VDC controller & solar vs 600V because the 600V gear gets crazy expensive.
Maybe you can get 600VDC breaker and an enclosure ?
I personally, would not wire directly from PV to controller. Just too hairy to deal with on a sunny day if something starts emitting smoke.
600VDC breaker:
https://www.midnitesolar.com/productPhoto.php?product_ID=336&productCatName=Breakers&productCat_ID=16&sortOrder=21&act=p
Disconnect enclosure ( bare )
https://www.midnitesolar.com/productPhoto.php?product_ID=507&productCatName=Breakers&productCat_ID=16&sortOrder=1&act=p
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
I use the Schneider Electric 600v DC disco all of the time. You only need one disco, and you only need to fuse more than 2 strings. It is far less expensive to use mppt-100 and it has room for you to grow. They are in the store here. Good Luck!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed