Lithium expert help needed...
Photowhit
Solar Expert Posts: 6,006 ✭✭✭✭✭
Okay, I'm NOT the lithium guy yet, I guess at some point I'll learn.
I'm trying to help someone on a solar forum with an off grid system she bought into.
I'm trying to figure out the battery bank she has. It has 4 sets of 16 of these batteries in series;
So as I read it it's a 8 ah 3.2 volt Lithium cell hope fully a LIFePo4 from the battery management system;
So math doesn't change with lithium batteries...lol.
It's still a string of 16 - 8 ah lithium batteries, for a string of 16x3.2=51.2 volts at 8 Ah or about 400 watt hours of battery each and 1.6 kWh for battery bank.
BTW - it's hooked up to a 16,000 watt inverter.
I'm trying to help someone on a solar forum with an off grid system she bought into.
I'm trying to figure out the battery bank she has. It has 4 sets of 16 of these batteries in series;
So as I read it it's a 8 ah 3.2 volt Lithium cell hope fully a LIFePo4 from the battery management system;
So math doesn't change with lithium batteries...lol.
It's still a string of 16 - 8 ah lithium batteries, for a string of 16x3.2=51.2 volts at 8 Ah or about 400 watt hours of battery each and 1.6 kWh for battery bank.
BTW - it's hooked up to a 16,000 watt inverter.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
Comments
-
16,000 Watt inverter? That is ~390 Amps @ 48 VDC.... That should be way more current than that Li Bank can support.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Yeah Bill,
Not a balanced system, but they were buying for the future larger home. The inverter uses 45 watts in power saver mode and 225 watts at idle. It appears the battery bank was sold to them as a much larger battery bank.
I was just curious if Some how I'm reading them wrong, perhaps rated at peak load or something odd...
Perhaps someone who builds lithium battery packs/banks would see something right away.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Hmm... Looks like they have 4x of these BMS units:
https://dalyelec.en.made-in-china.com/product/kwTfYhcKZmWO/China-Daly-Manufacture-Hot-Selling-in-USA-Smart-LiFePO16s-48V-100A-Common-Port-with-Uart-Communication.html
So--They could be 400 Amp total.Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I'm reading the cell in the first photo as stating 8Ah 3.2 volts.
Here's a Midnite Classic and the inverter for scale;
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Another view of the cells, 16 in series;
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
If you go with (probably) a conservative max discharge current of 1 amp per 1 AH of capacity... Each 8 AH module would be good for 8 amps (1 hour discharge rate).
- 4 modules * 8 AH per module = 32 AH @ 48 volt bank
- 32 AH * 48 volts = 1,536 WH storage (exactly what voltage for bank capacity calculation)
- 32 Amp discharge * 48 volts * 0.85 AC inverter eff = 1,306 Watts max continous AC inverter max load (pure guess)
You could have high drain cells--But what is the interest in draining a solar bank in 10 minutes or less...
8 AH does not seem to match the 21700 battery capacity (at this time anyway...).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Those look like Headway cells, like these: https://www.ebay.com/itm/203092649653
From what I can find, the max continuous discharge is 15C for each cell, or 120A. You can probably find all the specs online.Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case. -
Looks to be an experimental setup, the battery capacity is probably just sufficient to satisfy the idle demand. There is nothing wrong with how the batteries are configured, there are pros and cons to doing series then parrallel, as it is in this case, or parrallel first then series, the latter needing only a single BMS.
This is not a functional system by any means, there is enough equipment to build a substantially larger bank, the inverter however is an energy hog even in power saving mode. What is the intent? the Daly BMS costs about $50 without Bluetooth, each is rated at 100A, usually multiple BMS's are used to increase overall amperage, but the cells as configured would be incapable of delivering such a value which brings back the experimental statement.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
...but just on capacity, they are 8ah cells, but made for hiigh drain situations?Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Can't guess... That is one of the functions of the BMS--To limit maximum discharge (and charge?) current.
Using Horsefly's guess:
https://batteryhookup.com/products/4-headway-38120-hp-3-2v-8ah-lifepo4-lithium-batteries-25c-200a-super-cells
200 Amp discharge/80 Amp charge... An amazing cell.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Yep, you can do a lot.... For a couple of minutes.
Doesn't sound very practical for the inverter set up your friend has.Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case. -
The cell itself can only take 80A charge. A very imbalanced cell design also. A good learning lesson for the young lady I hope!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed