Needing Help with my 1kw array, and a 40 AMP MPPT at 24 Volts...
DigitalSolar
Registered Users Posts: 1 ✭
Good Evening!
I am still getting my feet wet and am looking for experienced advice. I have an Epever 40 AMP Tracer AN charge controller that says it can handle 1040 watts of solar in the manual. The conundrum I am in, is I can not figure out a way to configure it, no matter what I try to think of it ends up being over 100Volts ( charge controller max voltage) 5 in series 2 parallel 22.3 is the open voltage of these 100 watt panels, I have 10 of them. or I end up having 2 panels left out in the cold 4 in series 2 in parallel, only being able to use 8 out of the 10 panels because I would not want to have 2 sets of 4 in one string and a set of 2 in a third string right?
Any help would be GREATLY appreciated, if there is just no way to get 1000 watts of solar connected though a charge controller that says it will take 1040, I may end up having to buy a new controller I suppose, but I bought this one because it said it could handle 1040..
Thanks!
Thanks!
Yeah, got to plan ahead and work within the constraints of the charge controller. You could do 3 strings of 3 to maximum effect with what you have or search for a charge controller that will handle then 5 in series. Something like the Outback FM60 might be the cheapest I can think of that allows for 150 volt strings. Of course the other option is seeing if the Epever can be 'over paneled' and buy 2 more panels and do 3 strings of 4 panels...
You could do 5 strings of 2 panels, but even if Epever did say that was okay, I would work with what boB Gudgel has said about needing 30% voltage above the VMP, to charge effectively. boB and Robin did some of the early work building MPPT charge controller when they owned Outback and now with Midnite.
I went back and read you post. I assumed it was a 24 volt system. If you have a 12 volt system, 5 strings of 2 panels would be fine.
My original 24 volt system, had 2 arrays of 5 strings of 2 - 200watt panels on 2 different charge controllers. You do need a combiner box for more than 2 strings.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
With a 40A controller it must be a 24V nominal system 2 series 5 parrallel would be 44.6 VOC, about perfect and yes a combiner with overcurrent protection for each string. The real output would be somewhere around 75% of the rated output in most cases or something in the neighborhood of 32A in full perfectly aligned sun.Photowhit said:I went back and read you post. I assumed it was a 24 volt system. If you have a 12 volt system, 5 strings of 2 panels would be fine.
My original 24 volt system, had 2 arrays of 5 strings of 2 - 200watt panels on 2 different charge controllers. You do need a combiner box for more than 2 strings1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
I believe the desired voltage should be VMP above the charging voltage, NOT VOC.mcgivor said:With a 40A controller it must be a 24V nominal system 2 series 5 parrallel would be 44.6 VOC,Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
This might help with any over paneling worries.
I think your best option will be to upgrade to a higher capacity controller. Look at Epever'sTracer 5420 and 6420, their 50A and 60A controllers, respectively. They make both 150, and 200V max versions. I would pay a bit more to get the 200V model. What I would do is first contact the seller you purchased from and ask if you can upgrade to a bigger model.If you can't return your controller to the seller with the option to buy an upgrade, then maybe you could sell it "new, open box" on Ebay. Recoup a fraction of the price that will help pay for the upgraded controller.If you are really stuck with keeping this 40A controller, then just utilize 9 of the panels and wire them in a 3S3P configuration. Keep in mind that with more than 2 parallel strings of panels, they must be fused/breakered for short-circuit protection.If you decide to buy 2 additional panels, you could wire them in a 3S4P configuration without much worry of overloading the controller. Assuming you are not likely to ever see greater than 85% output, the math would be (1200W/26V charging) X 0.85 efficiency =39A.
System 1) 15 Renogy 300w + 4 250W Astronergy panels, Midnight 200 CC, 8 Trojan L16 bat., Schneider XW6848 NA inverter, AC-Delco 6000w gen.System 2) 8 YingLi 250W panels, Midnight 200CC, three 8V Rolls batteries, Schneider Conext 4024 inverter (workshop)