Need help choosing a charge controller
MEK1954
Registered Users Posts: 23 ✭✭
I need help choosing a charge controller I have 8-195w panels connected in series/parallel for 48 volts (2 sets of 4 panels) and the batt bank is 4- 200 amhr AGM connected in parallel going to a 12v inverter. I am sure I want to go with the outback FM80 but not sure if the 80 amp will be enough or should I split the array and use 2 FM60's.
Comments
-
A single FM80 should work fine because they can handle being over paneled by 20 to 25%. When you take into consideration derating the array output 20 to 25% due to higher temperatures in direct sun, the most the charge controller will normally see is around 1200 watts. This would also result in higher power production in low light conditions. The system appears to be well balanced.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
-
MEK1954 said:I need help choosing a charge controller I have 8-195w panels connected in series/parallel for 48 volts (2 sets of 4 panels) and the batt bank is 4- 200 amhr AGM connected in parallel going to a 12v inverter. I am sure I want to go with the outback FM80 but not sure if the 80 amp will be enough or should I split the array and use 2 FM60's.
You might also consider the MidNite Classic 150 Charge Controller. Some info, here:
Microsoft PowerPoint - Classic (midnitesolar.com)
A bit more expensive, than the OB FM CCs, but much more flexible, and in a typical system, it can cost less, depending on the system requirements/design.
2 cents worth, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Will fan noise be any consideration for the controller ? the Midnight has some noisy fans, but mine is in an outbuilding
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed