Conext SW 4048 inverter

Issue - inverter energizes for a few seconds then powers off. 

System is as follows
48v, 100ah lifepo4 battery
Schneider electric Mppt 60/150 charge controller
Conext SW 4048 inverter
Midnite solar e-panel
9, 320w solar panels - 3 strings with 3 panels each
Combiner box for PV
SCP for the inverter
Conext gateway combox

All wiring has been completed per the wiring diagram provided by schneider electric. Closing the breaker to energize the charge controller, the charge controller energizes appropriately.

 When I close the breaker to energize the inverter (with the charge controller energized) the inverter energizes for a few seconds then powers off. Multimeter reads 55.4v on the inverter breaker terminal before closing inverter breaker. Once closed, voltage rapidly drops to around 3v. Battery support said this behavior is by design when the battery protection mechanism engages. 

Battery monitor shows a spike at the point of the breaker closing. Then Sharp drop.

If I leave the charge controller off and close the breaker to the inverter, inverter powers up.

In addition, I have the SCP attached to the inverter via the xanbus connection. If I also connected the conext gateway combox via the xanbus, the same behavior is displayed. Inverter energizes for a few seconds then powers off.

So this looks to me like I don't have enough power supplied to energize all the equipment. I've been looking for troubleshooting/diagnostics information on the inverter but haven't been able to find anything other than the install guide.

Charge controller appears to be functioning properly as it shows bulk, float, and absorption charge appropriately. 

Thanks for any assistance

Comments

  • mcgivormcgivor Solar Expert Posts: 3,739 ✭✭✭✭✭✭
    When the battery is connected to the inverter initially it draws high current to charge the capacitors, this may be higher than the BMS will tolerate thus disconnects the load, most likely case.  
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS 
    Second system 1890W  3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.  
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
  • mike95490mike95490 Solar Expert Posts: 9,251 ✭✭✭✭✭
    Try getting/using a 250w incandescent Flood Lamp and use that too slowly precharge the inverter capacitors.  it  may wake up and complain about low voltage, but eventually power on, and  THEN flip the breaker

    Batt +  ----------- 120V 250W flood lamp  ----------------- + inverter input

    The idea is to bypass the breaker and allow the  flood lamp to limit current flow till the caps get charged up to 24v.

    But you have a bigger issue,  Your inverter is way larger than your small Li battery can safely support.  you may be triggering the battery BMS several times a day - won't that be fun.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

Sign In or Register to comment.