Victron 10000 va inverter blew up
yrtrnc
Solar Expert Posts: 54 ✭✭
The dThe damage is concentrated in this area on top of the communication cables. There was a burnt smell and the overload led was on when i checked the unit. What caused this error? We don't have high loads, only a kettle 1800 w was on at the time.
Tagged:
Comments
-
Lightning would be a first guess, any electrical storms present when this occured?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
No, no lightning storms! The only clue I have is that a 32 amp rcbo tripped once before this happened. The 32 amp rcbo is connected to a 2000 w grill and a 1800 w kettle.
-
There has been drilling going on lately, could it be that one of the wires was drilled through and line and neutral is in contact? Would this damage the inverter like this? There are no signs of high load spikes in the log files!
-
yrtrnc said:There has been drilling going on lately, could it be that one of the wires was drilled through and line and neutral is in contact? Would this damage the inverter like this? There are no signs of high load spikes in the log files!
Dead short line - neutral inside the case has no OCP .
10Kw inverter, I hope it was a 48V unit. Something had to have gone very badly wrong to blow up like that
> The 32 amp rcbo is connected to a 2000 w grill and a 1800 w kettle.
What is a rcbo ? 2000 grill and 1800 kettle are not insignificant loads. Together, they would draw about 80A from a 48 v battery, or about 40A each. Either of those is over 32A
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
No, no one was drilling anywhere near the inverter. The drilling was on the house walls, I was just considering if they hit a wire. But how would that cause a fault. The rcbo in the house tripped once, I put it back on. Everything seemed fine then later it blew. If there was a fault with the circuit why didn't the rcbo trip again.
-
The drilling was a week ago BTW.
-
Perhaps, a loose connection on the AC out, or the DC into the inverter?
Most high quality inverters, used in off-grid systems, will shut down within milliseconds, when the AC output is dead shorted -- long before almost any circuit breaker can trip (generally).
Good luck, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Hard to tell from the image but it could have been a capacitor failure, the residual current circuit breaker, RCBO, which is a ground fault main breaker for the benifit of those who aren't familiar with the term, would have tripped on any external short.
How old is the inverter, could you post a wider image which would show where exactly the fault occured?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
On top of the communications cables. The damage is to the wires coming from the transformer and connecting to a board with a bunch of mpx x2 capacitors and a couple of fuses. The inverter has only been used for 6 months. Also, no loose connections.
-
That was a pretty hefty burst of current thru that wire, to totally vaporize the insulation off it . Whatever caused it, it was bad.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
I checked the circuits in the house one by one. And found continuity between line and neutral on one of the circuits. I traced it to an ip rated socket on the outside wall. Looks like Hager rcbos are shit after all. But how a short circuit within the property would cause an inverter to blow up is beyond me. Any thoughts?
-
A short in a branch circuit would likely cause failure in the smallest conductors if the overcurrent is sized greater than it current carrying capacity of the conductors downstream of the RCBO, likely smaller than the one in the image. Furthermore inverters tend to self protect against short circuit faster than a breaker can react due to the trip curve criteria, thus the damage may be unrelated to the RCBO's performance.
There is a difference between a dead short and a ground leakage, a dead short would be the same as a load, both live and neutral carrying equal current, a leakage, or residual current is the differential between the current carried in the live and neutral conductors. Therefore in a short condition the rated amp capacity of the device would be relied upon as an overcurrent protection device, there would be no imbalances to cause a leakage trip.
Regardless the best course of action would be to contact the dealer to initiate an RMA (return merchandise authorisation) for a warranty claim, it could have been something simple as a bad crimp which caused overheating, something that is possible even with the best products on the market. My opinion, for what it's worth, is its unlikely the fault was caused by a short circuit but the manufacturer may see things differently, your call on the information provided.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Hager Residual Current Circuit Breaker with Overcurrent Protection devices (RCBOs) provide MCB overload protection and RCD earth leakage protection (protects against electrical shocks by direct or indirect contact). A range of sensitivities and current ratings are available for use in residential, commercial and industrial applications.
System 1) 15 Renogy 300w + 4 250W Astronergy panels, Midnight 200 CC, 8 Trojan L16 bat., Schneider XW6848 NA inverter, AC-Delco 6000w gen.System 2) 8 YingLi 250W panels, Midnight 200CC, three 8V Rolls batteries, Schneider Conext 4024 inverter (workshop)
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed