What is considered a "charge cycle"
pabloesguapo
Solar Expert Posts: 116 ✭✭
My battery bank is a little small this time around (630Ah),
but it's what we could afford. On an average overnight,
the battery bank drains down to about 55%, SOC, without
any "intervention" by the generator. I have the Mate 3s AGS voltage
start set at aca 55%. One of these days, I'll be able to afford a
Flexnet DC and be able to set a voltage stop point too. Currently, I'm
setting a "quiet time" stop point, so the generator doesn't
charge the batteries too much, and we waste all that free sunshine
but it's what we could afford. On an average overnight,
the battery bank drains down to about 55%, SOC, without
any "intervention" by the generator. I have the Mate 3s AGS voltage
start set at aca 55%. One of these days, I'll be able to afford a
Flexnet DC and be able to set a voltage stop point too. Currently, I'm
setting a "quiet time" stop point, so the generator doesn't
charge the batteries too much, and we waste all that free sunshine
the next day. I'd rather not burn all that propane if I don't have
To.
My questions are:
-is this an advisable course of action in the first place?
-is it better for the batteries to partially charge them like this, to prevent their SOC
To.
My questions are:
-is this an advisable course of action in the first place?
-is it better for the batteries to partially charge them like this, to prevent their SOC
from going too low, or am I inadvertantly adding charge cycles to
these batteries, thereby shortening their overall lifespan?
-is a generator assisted partial charge, set to end just before dawn,
considered a charge cycle, or the beginning or end of one?
Thoughts? Suggestions?
these batteries, thereby shortening their overall lifespan?
-is a generator assisted partial charge, set to end just before dawn,
considered a charge cycle, or the beginning or end of one?
Thoughts? Suggestions?
27 Kyocera panels, 6,500w
24 CG2 6v batteries, 48v, 630Ah
Midnite Classic 150 & Classic 150 Lite in "follow me" mode
(2) Outback fx3648 inverters
Generac ecogen 6kw backup generator
24 CG2 6v batteries, 48v, 630Ah
Midnite Classic 150 & Classic 150 Lite in "follow me" mode
(2) Outback fx3648 inverters
Generac ecogen 6kw backup generator
Mate3s
Comments
-
In theory, a cycle is "any charge" then "discharge"... Charge by 5% and discharge by 5% is a "cycle". You can find charts that have cycle depth vs cycle life... A first approximation is that a 25% discharge battery will last 2x longer vs a 50% discharge cycle battery (a 25% cycle battery bank may last 6 years, and a 50% discharge battery bank may last 3 years--made up numbers). For example:
https://www.solar-electric.com/learning-center/deep-cycle-battery-faq.html/
Typical deep cycle lead acid Cycle life vs depth of discharge... 25% = 2,000 cycle life; 50% = 1,000 cycle life
More or less--For lead acid batteries, they take "time" to recharge. A 50% cycled battery can take roughly 10% rate of charge is 5 hours to "charge" and another 6 hours to "absorb" (battery bank takes less current as battery is >~80% State of Charge to 100% state of charge... So you are looking at almost 11 hours of charging (very rough estimate) when 50% cycled--Longer than the sun is up and charging for most people.
A 25% cycled battery only need around 2.5 hours (10% rate of charge) + 2 hours of Absorb for ~4.5 hours of charging--Fully charged by early afternoon.
More or less, FLA batteries are very efficient charging (close to 100%) as they charge from 0% to 80% State of charge (bulk). From 80% to 100% SoC, they become less efficient (absorb charging phase).
So--If you can load your propane genset >~50% of rated output (propane and gasoline gensets are generally most fuel efficient >=50% loading). And charge battery bank up to ~80% SoC (say genset very early charging in the morning for 3 hours @ 10% rate of charge) then stop the genset, and for >80% SoC, let the solar charging finish charging from 80% to 100%...
So, basically run the genset just enough so you can get your battery bank finished charged with the solar array.
Just to give some numbers to above (note using 10% here--13% or a bit more is OK too):- 630 AH * 10% rate of charge = 63 Amps
- 63 amps * 59 volts charging = 3,717 Watts
- 3,717 Watt charging / 0.80 charger efficiency = 4,646 VA (sort of Watts) estimated Genset loading
- 6,000 VA genset * 0.80 suggested max continuous loading = 4,800 VA max loading (suggested)
Note that a larger battery bank would need a larger solar array/genset to keep 10% rate of charge (usual minimum suggested by FLA battery manufacturers).
People the cycle their FLA battery banks a lot... There is a school of thought that you can cycle (for example) 50% to 75% every day, and only need to charge to >90% once a week (one vendor said once in 30 days)... And the FLA batteries will not sulfate while actively cycling (battery setting below ~75% SoC for hours/days/weeks sulfate and eventually fail--Sulfation is not reversible--Desulfators are out there but have a "mixed" bag of results. Better not to let the batteries sulfate in the first place).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Reviewing your energy usage before going even larger--Always a good idea. Usually cheaper to conserve energy than to generate it.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks. That all pretty much falls in libewith what I'm doing.27 Kyocera panels, 6,500w
24 CG2 6v batteries, 48v, 630Ah
Midnite Classic 150 & Classic 150 Lite in "follow me" mode
(2) Outback fx3648 inverters
Generac ecogen 6kw backup generatorMate3s -
You need to monitor your battery charging . If you are reaching a full charge daily, you don't need generator
If you find you need to run generator, run it in the morning, so your charger most efficient to recharge low batteries. Let the solar finish the charge off and save your fuel.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mike95490 said:If you find you need to run generator, run it in the morning, so your charger most efficient to recharge low batteries. Let the solar finish the charge off and save your fuel.
During my lead acid days I found using the generator in the morning was almost a gaurentee the overcast sky would clear.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 607 Discussion Forums/Café
- 301 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed