3 phase off grid system?
Hi there,
I had an inquiry from a guy that wants an off grid system to provide 3 phase power. Currently he is running his whole off grid operation off a 125kW Genset that is 480 Volt line to line and 277 volt Line to neutral. The Gen is currently powering up several houses, butcher shop, and all the out-buildings.
I realize I need to gather more info and will do so when we visit the site, however just trying to do as much back-round research as possible before hand. If we get this job, will be an interesting project, potentially large scale.
My first thought is to keep the Gen for back up and to run his HUGE loads when needed, but have an off grid system to power all the other daily loads as required......(that may not even require the system to be 3 phase but just stack as many inverters as necessary.........)
Thanks for any dialogue on the topic.
Comments
For this large of system--You probably need a Power/Electrical Engineer to work with you/the customer. Many pieces of equipment can be wired to run on 480 or 208/240 VAC three phase (but not all).
It sounds like the butcher shop may be the only thing running 3 phase power (the refrigeration compressor). The rest of the housing is probably running 240/120 VAC split phase (around Burnaby Canada?). Either the genset has step down transformers, or there are some spaced around the property.
Going back and identifying loads--Looking for conservation opportunities, etc.--Should be a big part of the process... For folks that have never done any conservation before, reducing energy usage by 50% can be obtained (insulation, new/energy efficient compressors/refrigeration/heat pumps/LED Lighting/etc.).
What does the sunlight look like (good sun exposure or trees/deep in valley/marine layer/etc.)?
http://www.solarelectricityhandbook.com/solar-irradiance.html
Burnaby
Measured in kWh/m2/day onto a horizontal surface:Average Solar Insolation figures
If the large energy usage is seasonal (freezing fish/game/cattle) for a relatively short period of the year (or deep winter), a Genset may still be the most cost effective for short/peak periods of energy usage. And use Solar for base loads (homes, outbuilding lighting, etc.).
Good Luck,
-Bill
Finding out what the loads are, is crucial . refrigeration, meat saw for cutting frozen meat.
Moving heating loads to gas could be huge, getting 2 houses off of electric stoves, and electric water heaters, baseboard heating....
Trying to rewire an existing compound from 3ph, to split phase, would be real messy, spend the $ for 3ph stackable inverters. But gotta find out the actual load requirement.
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Look at the wiring of the compound and where the power center will be located. You would be lucky if it was in the middle of the chain.
http://members.sti.net/offgridsolar/
E-mail [email protected]
Depending on what are the three phase loads--There are ways of using single phase power to run three phase equipment (capacitor start, large 3 phase idler motor--sort of like a motor/generator set, VFD (variable frequency drives), etc.).
And you have the choices of flooded cell lead acid, AGM or other sealed batteries, and lastly the LiFePO4 type (not including the others such as Nickel Iron "Edison" type batteries, etc.).
Without knowing more about the installation, it is probably not worth even guessing at this time.
-Bill
This is an EU version there are split phase examples as well, using 3 separate units can be done but my opinion it'would be easier with a single device.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
https://forum.solar-electric.com/discussion/17986/is-the-system-set-up-right/p1
Not saying this will happen with this project--But getting a competent power engineer at the beginning is going to be a big help.
-Bill
http://members.sti.net/offgridsolar/
E-mail [email protected]
I am partial to XW because I have designed and used them since the start. Really everything out there in the world is based on what XW did and continues to do. You are in the land (Burnaby) of XW and support is driveable.
I would use one of Schneiders design engineers as that will go a long way if there are problems down the road. There probably won't be either.
http://members.sti.net/offgridsolar/
E-mail [email protected]
https://solar.schneider-electric.com/installer/dave-angelini-offgrid-solar/
http://members.sti.net/offgridsolar/
E-mail [email protected]