1500 watt inverter - will I damage it?

I have a 1500 watt inverter and I’m looking at getting a glass plate induction cooker. The cooker draws from 100-2100 watts, I’m wondering if I don’t use the cooker over roughly 2/3 the temperature setting will that be a problem for the inverter?
Tagged:
Comments
I do not know. I have never used an Oscilloscope to measure the current profile of an induction cooker.
A good quality modern induction hot plate should have an AC input stage that prevents high current spikes--And if you can ensure that your hot plate always operates at 2/3 power (not temperature) or less, then it should be OK with your inverter.
Your inverter should be capable of near 2x rated output for a few seconds (surge current to start a motor, etc.). And even operation at full power should not "kill" the inverter--If anything, the inverter may indicate over current output and/or just shut down until load is removed/DC input power is reset.
Notice I said "power" and not temperature. Some induction cookers may have a "temperature" function--I.e., you set for simmer at boiling temperature. The cooker could use full power when a cold pot is placed on the induction coil, and dail back the power when the pot is "hot". So you may have that variable to deal with too.
Make sure you have very heavy/short DC power cables from your battery bank (positive cable with fuse/circuit breaker) to your DC input of your Inverter... You need to keep the voltage drop reasonably low and use heavy cable to avoid overheating. For example, a 1,500 Watt inverter running on a 12 volt battery bank will take:
- 1,500 Watts * 1/0.85 AC inverter eff * 1/10.5 battery cutoff voltage = 168 Amps
So, you would want fusing/breaker/wiring for the DC circuit to be rated around:- 168 Amps DC current * 1.25 NEC derating = ~210 Amps or higher (200 Amp rating would be OK too)
-BillHowever, on occasion, the inverter can get damaged. Hopefully it will not happen to you. Just too many brands/models/etc. of inverters out there to make a blanket statement about quality/function.
-Bill
Cheers
- kwastizzle
If you want to go down a dark hole--You can get some instruments to measure/monitor your energy usage... Both on the AC side and the DC side.
Some AC capable meters:
https://www.amazon.com.au/s?k=ac+power+meter&ref=nb_sb_noss_1
And some DC meters:
https://www.amazon.com.au/s?k=dc+power+meter&ref=nb_sb_noss
And/or you can get an AC+DC Current Clamp Digital Multimeter--Much safer and easier method to measure current:
https://www.amazon.com.au/Auto-Ranging-Technology-Klein-Tools-CL800/dp/B019CY4FB4 (mid-priced unit)
https://www.amazon.com.au/s?k=uni-t+ut210e&crid=2LFRYG17D3NEL (less expensive but "good enough" meter such as the UT210E)
Note: I am guessing as to what is available in Australia... And the mess with COVID and issues with China, so price and availability is all over the map.
And there are AC only current clamp meters--They are perfectly good meters, but if you want to measure DC current, you need to get one that is DC+AC capable current clamp (the meter leads for both will measure AC+DC voltage, resistance, etc.--So that you have to read the product descriptions closely--I.e., AC only clamp current, but AC+DC voltage capability).
-Bill
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.