Self actuating or self resetting breakers

I normally use manually reset able breakers for the positive line from charge controller to battery.






Are there any pros and cons to using a Self actuating or self resetable breaker instead?


Tagged:

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Pro:  you don't have to chase it down to reset it
    Con:  if you get a fault and don't notice it right away, it will keep resetting till the battery is dead or the wire eventually overheats
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||