Charging LiFePo4 in a hybrid system
JJH3rd
Registered Users Posts: 10 ✭✭
I am using a solar/battery energy system that is made up of: 6.2KW of solar panels, 800AH of LiFePo4 batteries (15S2p of CALB 400AH), Solark 8K controller, 10 circuit transfer switch). Ironically, due to the storm system that came through here yesterday, our home was without grid power for more that 8 hours and the 6 circuits supplied by the solar/battery system provided power through the transfer switch as designed, so for a time I was "off-grid" and on batteries&/solar power.
Here is my question: Can I charge individual batteries if their voltage is below a defined value while the batteries are still connected in the string?
I asked SolArk about charging the bank while the controller was connected to the batteries and they indicated that was not a problem. In the charge-phase, the SolArk does, in fact charge the entire bank.
My questions are: 1) could I charge an individual cell in situ, 2) would there be any benefit to charging the individual cells?
Tagged:
Comments
-
Charging individual cells, or cell blocks within a string is not something that is usually done, the rationale being that the cells should have been ballanced prior to commissioning and doing so would cause imbalance.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
The first time I measured, (before they were put into service), the average voltage of the 30 batteries was 3.246, the maximum was 3.28, the minimum was 3.2, StDev was .022. My concern is that as I measure the batteries, in service, while under charging conditions, one or more measure 3.1 volts and they are not at the first or last position in the string.Right now it looks like more measurement is in order.
-
Sounds like they were not ballanced prior to series connection, hopefully you have a BMS to prevent individual cell voltage runaway. When nearing the fully charged or disharged state the cell voltage deviation increases dramatically, without a BMS serious damage could occur.
What charging voltage is being used?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
From the SolArk documentation:continuous battery charging output:190A3 stage with equalizationcharging voltage 54.4V
-
Most users use a lower charge voltage of ~3.400 volts per cell as there is little advantagein attempting to achieve 100%, it is also considered that limiting the voltage increases cycle life expectancy. Charging 15 cells at 54.4V represents 3.63 VPC, using this high a setting without a BMS which limits current as the voltage nears this value, would be something not recommend.
The normal practice is to disable equalization as it is not needed, my questions are, do you use a BMS and did you ballance the cells prior to assembly ?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
no ans yes
-
Without a BMS your charging voltage is too high, IMHO. Without one there is no way to limit the current and individual cell voltage may exceed 3.650V, is the charging voltage adjustable to a safer voltage say ~51V maximum?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
@JJH3rd
I have a setup similar to yours, although my LFP bank is one fourth the size, and I definitely agree with mcgivor. A 51V to 51.4V absorb setting would be the highest safe settings for your bank without a BMS. With that charge setting it should work well if you have already balanced the cells.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
Here's my basic quandary. When I examine the BMS landscape, I see that they work with the battery bank as a whole. This approach may be alright when there are a small number of batteries, less than 10 for example. The number of small voltage LFP batteries needed to get to a workable voltage exceeds that number by a large margin. In my case, to get to ~48 V & 800 AH, I have 30 batteries (15s2p). I would like to believe that a BMS I would install would provide more features than the Sol Ark controller to which the batteries are attached.At this point, I would settle for information on each cell, such as voltage and SOC for instance.I may have to construct an Arduino based monitoring system.
-
Here are two BMS that do cell voltage monitoring with cell and battery protection capability. They do not do active cell balancing. One is a Beaglebone/Raspberry Pie project, information here:
https://github.com/simat/BatteryMonitor
and the other is the Chargery BMS16 (works with 2 to 16 cells in series or series / parallel configurations) available here:
https://www.aliexpress.com/item/32850502583.html4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
Thanks for the links
-
JJH3rd said:Here's my basic quandary. When I examine the BMS landscape, I see that they work with the battery bank as a whole. This approach may be alright when there are a small number of batteries, less than 10 for example. The number of small voltage LFP batteries needed to get to a workable voltage exceeds that number by a large margin. In my case, to get to ~48 V & 800 AH, I have 30 batteries (15s2p). I would like to believe that a BMS I would install would provide more features than the Sol Ark controller to which the batteries are attached.At this point, I would settle for information on each cell, such as voltage and SOC for instance.I may have to construct an Arduino based monitoring system.
Attached is a pdf of the BMS I currently use, it is an 8 series but illustrates how it is connected, in your application the only difference would be the addition of 7 cells to meet the required voltage. They are available in many configurations depending on personal needs such as charge/discharge current and voltage. For around $100 I considered it cheap insurance considering the overall cost of the cells.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I sent a message to the Chinese manufacturer of the BMS available through IC GOGOGO and then sent links to a how-to-install and also a link to Will Prowse reviewing it:WP review: https://youtu.be/xIBlmvQWbXYThis BMS looks very promising. I just wonder about which amperage board I would need and its connection cable size.JJ
-
how about this for all 30 cells?
-
As you have 2 cells in parallel per cell block you need a 15 S BMS, the needed information would be maximum charging and dischargeing current. When I ordered mine I supplied all relevant information, the engineering department recommended one based on the figures.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
As mcivor said, a 15S BMS is called for because the parallel block doubles the amp hour capacity while the voltage remains the same. I'd also recommend increasing the BMS current capacity to better handle surges. Take a look at this one.
https://www.aliexpress.com/item/32997552090.html?spm=2114.12010612.8148356.2.42c43de2I8pAHH
4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
OK. Here my plan. What are your thoughts?Above is the existing circuit.Of course in my case the batteries are 3.2V LFP4 15S.Is this the correct placement for the BMS boards in the circuit?
-
Whilst there is nothing wrong with the configuration using 2 strings of 15 cells each with its own BMS there are some considerations that need to be considered. The maximum current would need to be limited to the maximum each BMS can process, for example if 190 A is the maximum both would need to be capable of handling that value to prevent overloading of the BMS should one disconnect for any reason as LiFePo4 will absorb extremely high current, usually 1C or greater.
The conventional method is to connect two, or more cells in parallel first then series, this would mean only a single BMS would be required as the multiple cells in parallel become one cell block. This is how small cells not much larger than an AA cell are configured, often with hundreds in parallel in automotive applications. With larger prysmatic cells it's common to parrallel 100Ah cells in parallel in order to increase capacity rather than use large 400Ah as it's reputedly a better method. Naturally doing this will require only a single BMS, there may be some perceived logic of redundancy with a dual BMS as shown, but having all the cells as a common battery keeps things simple
.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Thank you both for your help and information. I'll have to wait until the Chinese economy gets over the COVID-19 virus. I'll let you know how it works in practice.
-
JJH3rd said:I am using a solar/battery energy system that is made up of: 6.2KW of solar panels, 800AH of LiFePo4 batteries (15S2p of CALB 400AH), Solark 8K controller, 10 circuit transfer switch). Ironically, due to the storm system that came through here yesterday, our home was without grid power for more that 8 hours and the 6 circuits supplied by the solar/battery system provided power through the transfer switch as designed, so for a time I was "off-grid" and on batteries&/solar power.Here is my question: Can I charge individual batteries if their voltage is below a defined value while the batteries are still connected in the string?I asked SolArk about charging the bank while the controller was connected to the batteries and they indicated that was not a problem. In the charge-phase, the SolArk does, in fact charge the entire bank.My questions are: 1) could I charge an individual cell in situ, 2) would there be any benefit to charging the individual cells?Who am I?→ Officially and exclusively authorized agent of CALB battery in China. CALB is a leading battery manufacturer in China and the leading brand in the world.Contact mail?→ Alvinsun02@hotmail.com or Alvin@fj-calb.com
-
just a question about BMS and battery monitors - do you knnow if there are there any devices that expose state of charge from a LiFePO4 battery via a modbus register?John Gorman / SolarNetwork Foundation
e:john@solarnetwork.net
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed