Design a 24v or 48v system
Ironbull
Registered Users Posts: 15 ✭✭
Things I have....
Charge controller: Outback Flexmax 80
Batteries: 8 Trojan t105re 6v 255ah
Inverter: Samlex 24v 2000w
What I want to power....
I have 2 chest freezers, one is converted to a fridge. Combined they use roughly 1.2kwh a day. Anything beyond that is just icing on the cake.
What i need....
Solar panels sized to whatever system we come up with.
Would like to also incorporate genny support, I have 2 gennys, one is 2000w inverter and the other is 3500w inverter
Future requirements.....
To be able to expand my system if/when needed.
What would you do if you already had said equipment?
Charge controller: Outback Flexmax 80
Batteries: 8 Trojan t105re 6v 255ah
Inverter: Samlex 24v 2000w
What I want to power....
I have 2 chest freezers, one is converted to a fridge. Combined they use roughly 1.2kwh a day. Anything beyond that is just icing on the cake.
What i need....
Solar panels sized to whatever system we come up with.
Would like to also incorporate genny support, I have 2 gennys, one is 2000w inverter and the other is 3500w inverter
Future requirements.....
To be able to expand my system if/when needed.
What would you do if you already had said equipment?
Comments
-
Canadian solar panels from DNM solar. Get 6 of them 330 watts and you have an honest 2kw of charge power. Want something larger? More of the same with either an increased charge controller or another FM80.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
-
The typical voltage "limiting" hardware are solar panels (Vmp-array voltage), MPPT vs PWM charge controller (you have MPPT--Good), AC inverter input bus voltage (yours is 24 volts--Need different inverter if want 48 volts), and batteries for bank (your 8x 6 volt batteries will work fine for 12/24/48 volt bus).
If you plan on going for larger single system in the future--A 48 volt inverter + battery bank will give you more "headroom" (the Outback MPPT controller will work on 12/24/48 volts--But the size a supported 48 volt battery bus is 2x the wattage of a 24 volt bus)...- 80 amps * 29 volts charging * 1/0.77 panel+controller derating = 3,013 Watt typical cost effective array @ 24 volt bus
- 80 amps * 58 volts charging * 1/0.77 panel+controller derating = 6,026 Watt typical cost effective array @ 48 volt bus
Looking at your AC inverter (features, efficiency, Tare Losses, "search mode", remote panel, etc.) tend to help make the decision of what AC inverter (and sometimes battery voltage) limit your choices. Large Wattage inverters on a higher voltage battery bank tend to "waste" power power when driving relatively small AC loads (i.e., if the inverter draws 40 Watts * 24 hours per day just being "on", that is more power than your one of your freezers).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I currently have 255ah @48v or 510ah @24v. The only reason I considered changing inverter was so I could incorporate genny charging abilities. If there is a way to do this without upgrading inverter, I will keep what I have as far as inverter goes and if at some point I decided I need more I can go to 48v.
So I guess the question is, is there some magical charger that does this?
And next question is what is minimum panel wattage to charge what I have? -
My solar insolation number are 3.1 for a winter low and 4.9 average if that helps
-
Minimum solar to charge your bank? Well, I had 12 GC's in three series parallel strings (660Ah @ 24 volts) that I charged with about 400 watts of solar. Far too low from what is usually discussed here, but the batteries lasted 19 seasons and ran all the loads I had at the time. However, consider the 2kw I mentioned earlier. That would put you in the middle of the usual recommended charging current.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
-
Inverter-chargers can be very nice... They can be highly programmable (compared to the simple Iota type). And the inverter can include its own internal transfer switch... Run from battery, start genset, transfer from inverter/battery power to genset AC power, limit input AC power to genset rating, vary charging current based on Genset Max - AC loads = Battery current.
Generator support mode, you can run your 1,800 Watt genset and inverter-charger with generator support can add "battery power" to AC output (genset 1,800 Watts max, AC load max load = 1,800 W genset + 3,000 Watt from battery = 4,800 Watt total AC load support--Until battery goes dead, fuel runs out, or AC load drops back to less than 1,800 Watts--Then 1,800 Watt Gen - 500 W AC load = 1,300 Watt available for battery charging from genset (all numbers made up--Just example of function).
Or, you can keep the simple AC inverter, and parallel your solar charger + AC genset charger to single battery bank. Will work fine.
Argument for separate AC inverter and AC charger--If one fails, the other still works. With Inverter-Charger, if "one fails", both Invert/Charge functions are dead until repaired or replaced.
Your system is close to supporting 3,300 WH per day (my suggested aim point for a near normal electrical existence for a full off grid cabin/very energy efficient home (using propane/wood/etc. for heating/hot water/cooking/etc.). So, using your number:- 3,300 WH per day * 1/0.52 off grid AC system eff * 1/3.1 hours winter sun = 2,047 Watt array "winter break even"
Base loads should make up around 50% to 65% of your total solar power for a "reasonable" build and forget (basic maintenance) system (vs one you have to look at the hours of sun, loads, etc. every day and figure out what you are going to "run" that day). Of course, if you have a genset--This is more the issue of fuel costs, noise, etc. to run a genset vs buying more panels.
So, you can look at your base load harvest as:- 2,047 W array * 0.52 AC system eff * 3.1 hours of (winter) sun * 0.65 base load fudge factor = 2,145 WH of base load support (winter)
- 2,047 W array * 0.52 AC system eff * 4.9 hours of sun (summer average) = 5,216 Watt*Hour per day summer available energy
I try to use the math to help you decide where best to spend your money and a reasonably accurate prediction (in solar if I am within 10% of predicted output--That is pretty much "dead on" accurate for solar).
Your thoughts?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Wow that's a lot to unpack. I'm a pretty handy fella with most things, but this solar stuff is like Chinese arithmetic.
There a lot to be said about keeping things simple. I like the idea of having redundancy, meaning having separate inverter and charger in the event one quits. I dont need anything that starts my genset automatic. I will have a look at the Iota charger. I dont plan on having to use genset except for the occasional week here and there of gloomy weather.
As far as output goes, I'm just concerned with my critical loads, the 2 freezers. I have heating, lighting and cooking taken care of. Most projects will be done in spring and summer where I will need to charge cordless tool batteries and such. Anything else will be just icing on the cake.
So if I'm understanding correctly, 2000w array should get me there. If I remember correctly, 2000w array is the max for a 24v system? -
2000w sounds like a good number in most locations to me. In some locations (eg warm/hot marine climate with haze), you could go a bit bigger if you want. In others (eg cold, high altitude), a bit less.
The Iota chargers are solid, simple, relatively inexpensive units. I use a pair of 45a on my 12v bank. One thing to be aware of though is I believe they still aren't power factor corrected. Probably not an issue unless you need to run other large loads on the genny while charging.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Iota chargers here:
https://www.solar-electric.com/residential/batteries-battery-storage/battery-chargers.html?manufacturer=49
And on the opposite side, high end sophisticated battery chargers:
https://www.solar-electric.com/residential/batteries-battery-storage/battery-chargers.html?manufacturer=101
The basic Iota is inexpensive and truly outputs it rated current... The IQ4 option is great for Mains connected supplies... For off grid generator power (you turn off genset when battery charging is done), not really needed. Also the simple Iota chargers do not have a power factor corrected AC front end--They are less efficient on gensets (power factor correction, can do a separate post on that, if wanted).
The Xantrex is a very nice, but not cheap, PFC (power factor corrected) unit (which allows you to pull upwards of 20-40% more Wattage from your genset) and more programmable output options.
Based on your Outback FM 80, you can run upwards of a 3,013 Watt "cost effective" array, if you wish.
And there is the "maximum" you can run based on your battery bank size... More or less, 5% to 13% to 20% is a good range. 5% for a weekend/sunny season/emergency backup system. 10%+ recommended for full time off grid system/optimum battery charging. And 13% is usually a good max cost effective array. And you can go upwards of 20% -- But watch your charging current/battery bank temperature--The batteries can get hot at that temperature (can be a bit hard on batteries). Nominal AC generator charging is typically around 10-20% range.
So, for a 24 volt @ 510 AH battery bank, recommended charging points would be:- 510 AH * 29.0 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 960 Watts array minimum
- 510 AH * 29.0 volts charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 1,921 Watt array nominal
- 510 AH * 29.0 volts charging * 1/0.77 panel+controller deratings * 0.13 rate of charge = 2,487 Watt array "cost effective" maximum
- 510 AH * 29.0 volts charging * 1/0.77 panel+controller deratings * 0.20 rate of charge = 3,842 Watt array "practicable" maximum
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I found a source locally for these panels and would like your thoughts....
REC Peak Energy 72 series
Pmpp 310w
Vmpp 36.7v
Imp 8.53a
Voc 45.3v
Isc 9.02a
___________________
Canadian Solar
Model CS6X-315P
Pmax 315w
Vmp 36.6v
Imp 8.61a
Voc 45.1v
Isc 9.18a
Either of these panels could save me a chunk of change vs ordering online. I'm thinking 6 of either of these, 2 strings of 3? Or would that put me too close to max voltage of 150v that my charge controller can handle? -
You need to find the record low temperature in your location, and adjust Voc up for that temp.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
This is where we are hitting another "gotcha" with the standard 140-150 volts max MPPT controllers, and the getting to be common higher voltage solar panels (Vmp~36 volts and higher).
Guessing you are around Mckenzie TN, with a minimum winter temperature of 22F... You would use an Outback String Sizing Tool (download and run on your computer):
http://www.outbackpower.com/resources/technical-support/string-sizing-tool
But as a rough estimate, using Midnite's online tool (because I am running Chromebook here):
http://www.midnitesolar.com/sizingTool/index.php
You will be very close to 148 volts Voc-cold at 22F... The FM 80 has a Vmax input of 150 VDC, and a maximum startup voltage of 145 VDC... Downloading the Outback tool and putting in all the actual numbers for your panels (Voc, Vmp, Isc, Imp, etc.) is really needed here--And how cold it actually gets in your region.
If you pick 24 volt battery bank and only 2x panels in series... You will be fine. 3x panels in series--Close to maximum input voltage for the FM 80 in January.
If you pick a 48 volt battery bank and 2x panels in series--It will work, but not be optimum (MPPT controllers need a higher input voltage to work "optimally"). And with 3x panels in series, you are pretty close to maximum input voltage in cold weather.
There is nothing "wrong" with your panels, or even your Outback controller--It is just the nature of the beast and evolution of the solar panels over time, where they are installed, etc.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Going to have a well pump? What depth?
If it was me, I'd likely go 24 volt since you have a decent inverter already. Your decisions on fridge/freezer indicate energy thriftiness. Like money, it isn't what power you have so much as how you use it.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Estragon said:2000w sounds like a good number in most locations to me. In some locations (eg warm/hot marine climate with haze), you could go a bit bigger if you want. In others (eg cold, high altitude), a bit less.
The Iota chargers are solid, simple, relatively inexpensive units. I use a pair of 45a on my 12v bank. One thing to be aware of though is I believe they still aren't power factor corrected. Probably not an issue unless you need to run other large loads on the genny while charging.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
In cold dry thin air at altitude, some folks have reported higher than STC output (vs ~75% at NOCT) from arrays. Covered in snow, not so muchOff-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
I think with the FM80 these panels would world fine in strings of 2 charging 24 volt bank, but not in strings of 3 charging a 48 volt bank. I would use what you have for now as a 1200+ watt array and your battery bank and inverter should support the fridge and freezer without need to worry about generator backup in general.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Photowhit said:I think with the FM80 these panels would world fine in strings of 2 charging 24 volt bank, but not in strings of 3 charging a 48 volt bank. I would use what you have for now as a 1200+ watt array and your battery bank and inverter should support the fridge and freezer without need to worry about generator backup in general.
To be able to expand my system if/when needed. "
That array does not allow for any real expansion.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Ok so I picked up 6 of the REC 310w panels I posted above. With an option to get more when he gets more in.
At the moment I'm planning to wire 3 strings of 2 panels. Which would give me 1860w. If my math is correct, 1860x.77=1432 usable watts?
So if I over panel with another string that would give me 2480w. 2480x.77=1909 usable watts? Which is within the 2000w limit my CC can handle on 24v system.
Or would I simply be better off getting another FM80 with the added benefits of having a backup if one of the CC fails. I'm heavily leaning this direction with another 6 or 8 panels. -
As well as redundancy, having the load split between two controllers rather than one running flat out may let the pair run cooler. In theory, this may help longevity of the pair. In practise of course, YMMV.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed