permanent magnet dc motor used as a generator

Connected a dc motor to a bicycle as a generator and would like to charge my 4 100ah agm deep cycle batteries when my solar panels are not providing power. what kind of charge controller can be used? it produces up to 60 volts and a steady 30 volts would be easy without much of a work out. 12 volt battery bank.
Tagged:
Comments
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
would a dc permanent magnet wind turbine charge controller
work?
A question about how much money you want to sped, and how good of cyclist you are...
As Mike says above, the battery is what really regulates the battery bus voltage (as long as the battery is large enough to accept the charging current--Typically around 10% to 20% of the Battery AH capacity... I.e. 100 AH battery * 10% = 10 Amps "optimum" charging current).
More or less, one way to regulate the battery state of charge is to simply stop pedaling when the battery is full (roughly 14.4 to 15.0 volts held for 1-6 hours -- Depending on the battery type/capacity/how deeply discharged).
Then there are charge controller options:
- When battery is full, the charge controller simply cuts off the current in a rapidly pulsing manner. Not great for regulating a generator--But may work. https://www.solar-electric.com/c40.html
- You can take the same C40 charger, and place it in "dump mode"... When the battery nears/reaches full charge, the controller "dumps" or shunts current to a load bank (resistors, a 100 Watt 12 volt filament lamp, etc.). This keeps constant current (on average) from your generator and keeps the pedaling force constant.
And there are MPPT and various other charge controllers/energy conversion devices... And depends on how much wattage you can output when pedaling, your motor specifications, how much you want to spend, etc.More or less, your genset is probably rated at 10 amps from 0-30 or 0-60 volts (approximatly). The "torque" of the generator is roughly proportional to the amount of current being drawn from the generator (say 0-10 amps). Above 10 amps, the genset will probably overheat or simply not output much more current. Say you can pedal at 100 Watts for 30-60 minutes... The current output by the genset would be:
- Power = Voltage * Current
- I = P/V = 100 Watts / 14.0 volts charging = ~ 7.14 Amps
At this level, there is not much reason to use a DC Converter to "match" the motor output to charging the battery bank.However, if you can pedal at 200 Watts with your motor:
- 200 Watts / 14 volts = 14.3 Amps
Or more current than the genset can output at 14 volts.So a solution would be to use a MPPT (Maximum Power Point Tracking) solar charger or a DC to DC converter to take higher voltage/lower current form the genset and efficiently down convert to the voltage needed by the battery bank... For example:
- 200 Watts / 10 amps (maximum torque) = 20 Volts at the genset (and 10 amps output)
- 200 Watts / 5 amps (1/2 torque) = 40 Volts at the genset (and 5 amps output)
A DC to DC converter is a "buck mode switching power supply". And can down convert to battery charging voltage and help the genset output more power than a "simple" connection to the battery bank.https://www.solar-electric.com/mosumpsochco.html
For MPPT type charger (internally, it is a "buck mode switching power supply"), the controller above should be a good fit to your application.
The other possible option is to use a DC to DC buck mode converter--Probably set for current regulation mode:
https://www.amazon.com/Converter-DROK-Voltage-Regulator-10V-75V/dp/B071LGTTRN
You could program it to both voltage regulate (14.4 volts for charging AGM batteries) and adjust the maximum current (to let you adjust the power harvest from the genset (pedal faster with lower torque, pedal slower with higher torque, etc.)... I am not sure if you would be happy with this unit, but at $30, it is "relatively cheap" to experiment with.
In the end, is the cost worth it? Assuming you can to 10 amps into 14 volt battery bank (140 Watts) for 1 hour (that is typically more than the "average" person can probably do... That is ~10 AH of current into your 400 AH battery bank or ~2.5% ... To even charge by 10%, you would need to pedal very hard for ~4 hours...
Are more solar panels or even a gasoline genset an option?
-Bill
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
If using the drok buck converter, I'd use a stable input source (eg 3 x 9v batteries wired in series =~18v) to adjust output voltage (~14.4v).
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Regarding the drop in voltage--In theory:
- 20 AH / 400 AH capacity = 0.05 or 5% of capacity drain.
With AGM batteries, it is difficult to accurately estimate State of Charge... Hot vs Cold batteries, how long they have been resting (typically 3+ hours of no load/no discharge for "resting voltage") can all have an effect.And since you cannot (easily) measure Specific Gravity, you are left with load testing and resting voltage.
And if the batteries are old and/or sat for a long time (>6 months) unused/uncharged, then there could be sulfation, with does make "big AH" batteries "smaller/lower capacity".
-Bill
As Bill noted, voltage isn't especially accurate in judging state of charge, but 12.5v could be ~85-90%. At 90%, that's about 40ah x 12v = 480watt-hours. You'd be in pretty good shape put out 100-150watts on the bike, and keep that up for ~3-4hrs to charge 480watt-hours.
What size inverter is running the 1a load? Is that [email protected] inverter output, or [email protected] inverter input?
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
When it gets close to fully charged, the battery takes less current. With regulation, voltage would be held at ~14.4v by the regulator as load current drops off. Without regulation, the voltage could continue to rise to potentially damaging levels, so you'll want to slow/stop pedalling if voltage rises above ~14.4. It won't get as full that way (unregulated), but still pretty close.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Taking the low end of the 2-300w range, that's still ~14a (7% of 400ah Capacity) vs a ~1% of C regulated absorb end amps. Enough current, I think, to raise unregulated voltage too high? If the bank is sulfated from undercharging, the effective capacity could be significant smaller, increasing the 7% current number.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter