Fuse rating question...
icarus
Solar Expert Posts: 5,436 ✭✭✭✭
I just added 300 watts of PV to a off grid system, 3 strings of 3 12 volt panels. Each string is breakered with a 12 amp midnight breaker, and the home run is fused just before the Midnight Kid with a 30 amp conventional screw in fuse.
the midnight kid sizing tool suggests in the best (worst in this case!) scenario is that the array COULD put out 31.2 amps. My question is, this system is remote and is unattended all winter. Do I worry that leaving all three strings connected risks blowing the 30 amp fuse. (I can’t replace the fuse with out replacing the box as screw ins only come as big as 30 amps as far as I know) It can be very cold (-40 or colder) with lots of reflection off snow, so I suppose it could actually reach the 31.2 amps, but I would be surprised.
I know I could simply turn off 1/3 of the array when it is unattended, but thenI am relying on someone else who may not know, to turn the last breaker on. Do I take the risk and leave it on or play it safe?
Tony
Brain fart... I just realized that the Kid is showing battery current, not PV current. Since the PV is wired in series at ~36 VDC the maximum SC current is only ~18 amps! Duh!
GT
the midnight kid sizing tool suggests in the best (worst in this case!) scenario is that the array COULD put out 31.2 amps. My question is, this system is remote and is unattended all winter. Do I worry that leaving all three strings connected risks blowing the 30 amp fuse. (I can’t replace the fuse with out replacing the box as screw ins only come as big as 30 amps as far as I know) It can be very cold (-40 or colder) with lots of reflection off snow, so I suppose it could actually reach the 31.2 amps, but I would be surprised.
I know I could simply turn off 1/3 of the array when it is unattended, but thenI am relying on someone else who may not know, to turn the last breaker on. Do I take the risk and leave it on or play it safe?
Tony
Brain fart... I just realized that the Kid is showing battery current, not PV current. Since the PV is wired in series at ~36 VDC the maximum SC current is only ~18 amps! Duh!
GT
Comments
-
The fuse after the combiner box is not really required. The input current is less than the max (panel current, not fuse rating current).
The only reason for the third fuse is if the down stream wiring from the combiner to the Kid is rated for less 36 Amps (i.e., if wiring is >10 AWG, the wire can never overheat). Of course, since your 3x Isc * 1.25 of the existing panels is less than the final feed current rating, you don't need the fuse unless you are planning on adding more panels later.
Fuses and breakers are the Unreliable part of the system (they open first before anything wiring fails/catches fire. So, I would simply get rid of the fuse and just use your series breakers with the panels (especially if you want a reliable/unattended system).
Of course, there is the other fox in the hen house--Any Lightning possibilities? Midnite DC surge suppressor on the array side of the Midnite? Possibly on the AC output of the AC inverter (if the system has an AC inverter).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Screw in fuses? are you referring to the old style residential AC fuse panel type? I forgot about those decades ago until I read this. I wouldn't think they were DC rated
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
I may be wrong, but I don’t think in the case of a fuse (of this general size) it makes any difference. The difference between a fuse and a breaker is that the breaker has to open, and sustains an arc, causing the breaker contacts to fuse (potentially) so that it won’t open. As a fuse simply melts and opens with over current.
Feel free to correct me if I am wrong...
Tony
PS a bit of google search reveals that the DC rating of MOST fuses is ~1/2 that of the AC rating.BB. said:The fuse after the combiner box is not really required. The input current is less than the max (panel current, not fuse rating current).
The only reason for the third fuse is if the down stream wiring from the combiner to the Kid is rated for less 36 Amps (i.e., if wiring is >10 AWG, the wire can never overheat). Of course, since your 3x Isc * 1.25 of the existing panels is less than the final feed current rating, you don't need the fuse unless you are planning on adding more panels later.
Fuses and breakers are the Unreliable part of the system (they open first before anything wiring fails/catches fire. So, I would simply get rid of the fuse and just use your series breakers with the panels (especially if you want a reliable/unattended system).
Of course, there is the other fox in the hen house--Any Lightning possibilities? Midnite DC surge suppressor on the array side of the Midnite? Possibly on the AC output of the AC inverter (if the system has an AC inverter).
-BillBB. said:The fuse after the combiner box is not really required. The input current is less than the max (panel current, not fuse rating current).
The only reason for the third fuse is if the down stream wiring from the combiner to the Kid is rated for less 36 Amps (i.e., if wiring is >10 AWG, the wire can never overheat). Of course, since your 3x Isc * 1.25 of the existing panels is less than the final feed current rating, you don't need the fuse unless you are planning on adding more panels later.
Fuses and breakers are the Unreliable part of the system (they open first before anything wiring fails/catches fire. So, I would simply get rid of the fuse and just use your series breakers with the panels (especially if you want a reliable/unattended system).
Of course, there is the other fox in the hen house--Any Lightning possibilities? Midnite DC surge suppressor on the array side of the Midnite? Possibly on the AC output of the AC inverter (if the system has an AC inverter).
-Bill
Lightning is an ever present possibility. I don’t have any surge protection, and in 20 years haven’t needed any, but tomorrow is another day.
Tony -
Per Little Fuse ...
- The DC Voltage rating of a fuse is not the same as the AC Voltage rating
- Typically, the DC Voltage rating is about 50% of an AC Only Voltage Rating
- The DC Voltage rating, is a safety rating that should never be exceeded
- If used in a DC circuit, the fuse must be DC Rated
-
If you are simply maintaining batteries over winter, I don't see a problem. A full battery bank in the morning, will start charging slowly as the sun angle changes, by the time the sun is high enough that the panels could produce 31A, the batteries are fairly full and cannot accept 31AThe failure mode is 5.4 cloudy days, and the sky clears at solar noon. Boom, full power into the batteriesPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mvas said:Per Little Fuse ...
If used in a DC circuit, the fuse must be DC Rated. Extinguishing a DC arc is much more difficult than an AC arc ... an AC arc is self extinguishing 120 times per second.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
@icarus said
Bill, My reason for the fuses is it gives me an easy disconnect 100’ from the combiner box, and it protects the wire in the event of some catastrophic CC failure that might release “reverse”(battery) current into the wire. My theory has always been to protect wiring at each end if there is a potential current source at both ends. Overkill? Probably.
Lightning is an ever present possibility. I don’t have any surge protection, and in 20 years haven’t needed any, but tomorrow is another day.
Tony
Fuses are not a reliable means of disconnect especially under load, wether DC or AC rated. Consider a MIG welder which operates at ~18V DC, the arc can span a distance of 5mm, melting steel at a modest 30A. As the fuse is removed, unscrewed in this case, the action is slow which is the perfect conditions to develop an arc, DC circuit breakers have a quick action along with arc quenching to reduce or eliminate the possibility of arc induction.
DC circuit breakers are not expensive, my recommendation is to replace the fuse with a DC circuit breaker, for safeties sake. Also consider the polarity of the circuit breaker, the positive terminal, should be connected to the side with the highest potential energy, in order for it to provide optimal protection, not all have polarization however.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
All good points, thank you all.
My described fuses are in an old fashioned service box with a handle disconnect. The fuses are just in the fuse holders, so I can disconnect the PV current with the service handle. I think I will just lest sleeping dogs lie...until I have a failure.
Tony
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed