XW 4548 Wiring help!!

wirewhat
wirewhat Registered Users Posts: 1
I have a xw4548 I can not get grid power to come though it only works on batt. Power it is a 120/240 hybrid system( what ever that means) I am hoping I can send 120 vac though L1 and N and get it to kick into grid power but no LEDs light up... What am I doing wrong.
Tagged:

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    edited July 2019 #2
    the xw4548 needs 240V split phase power to qualify the Grid.  If you are only feeding it 120V (one leg of the 240VAC) it will not qualify the grid.
    Same with running a generator with it, you need a 240V generator, or a 120V generator with a 240VAC autotransformer.

    > it is a 120/240 hybrid system( what ever that means)
     It means you are going to need to either become an electrician or hire one to help you with this. This is not a simple chest of drawers kit from IKEA.
    If you don't understand split phase north american power, you won't be able to wire it properly or connect it to a split phase panel

    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||