100 Ah and 200Ah LiFePo in parallel- why twice the current?

If I connect 2 Batteries in parallel, one with 100Ah and one with 200Ah, why does the 200Ah charge and discharge with twice the current, if they have nearly the same internal resistance? I thought the internal resistance was the only current limiting factor. If the 100Ah would have an internal resistance of half the size it would make sense to me but it has nearly the same. I thought maybe the 200Ah needs twice the electrons in order to reach the same voltage but I am not sure if this is the right explanation.
Comments
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
If they are different types of batteries (say the 100 AH is rated for higher surge current), then you may be getting into issues with charging and discharging.
If you have a DC Current Clamp DMM (or similar)--And can measure that the current flow (charging and discharging) is roughly 2/3 rds to the 200 AH battery and 1/3rd to the 100 AH battery--That is about all you can ask for.
https://www.amazon.com/gp/product/B019CY4FB4 (mid priced AC/DC Current Clamp Meter).
You do run into some issues if "something goes wrong" (say 200 AH battery cable "opens" and you try to pull full current from the 100 AH battery--The excessive current could damage the smaller battery.
Where you would get into real trouble is if you put the two batteries in series (i.e., 12 volt + 12 volt in series = 24 volt battery bus). The dissimilar AH cells could be a mess.
-Bill
CoreMax Technology company limited
P: 086-755-28080015 M: 0086-17688915553
Wechat: Sellbattery Skype: ODMbattery QQ:3572623261
W: cmxbattery.com coremax-tech.com E: [email protected]
A: B2 MaoYuan Industry HuanGuan South Road Guanlan Long Hua BaoAn Shenzhen China.
There will be eddy currents between the cells as they charge and discharge. I am not sure why the higher capacity battery will be damaged. Please explain?
I assume you are talking about Lithium batteries?
I can make lots of arguments about paralleling cells/batteries and why that can be problematic for things like safety, adding more points of failure, etc... But the whole Li Ion battery community of manufacturers/engineers have made it their lot in life to parallel multiple smaller cells in parallel (sometimes massively parallel) monoblock batteries (albeit with the appropriate monitoring, cutoff switches, etc.--Which is another complexity in itself).
How does one string of cells not see the the other XX parallel strings of cells as anything but a smaller AH capacity in parallel with a much larger AH capacity monoblock battery.
-Bill
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Not many want less
The screen below shows the BTS for this one battery. It can show the overall state of charge also. If there were a battery failure only the bad battery would be lost.
http://members.sti.net/offgridsolar/
E-mail [email protected]
They are not inexpensive.
I do not use Simplyphi because it does not communicate/network with the power system. A few other reasons also.
http://members.sti.net/offgridsolar/
E-mail [email protected]
That is the part I do not like on any single BMS system. It improved some battery characteristics at the expense of some new ways to lose power.
That may not matter to a hobbiest as much as someone in a snowstorm or a hurricane 100 miles from town or on a boat on the ocean.
http://members.sti.net/offgridsolar/
E-mail [email protected]
Seems to me, with multiple BMSs treated as discrete inputs, the probability of "lights out" because of BMS failure diminishes as the number of such discrete inputs increases.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
For my grid tie hybrid I prefer to keep it simple. Mine is also designed so that failure of the BMS does not bring down the pack. My biggest risk is not hurricanes or snowstorms, it is PG&E power outages.
A guy down in the valley did video of all the tow trucks coming up Interstate 5 with Teslas from LA to factory repair.
http://members.sti.net/offgridsolar/
E-mail [email protected]
Xantrex MPPT 60A x 2 + MidNite Classic MPPT 250V x 2
Ohmmu 100Ah LiFePO4 Group 31 Batteries x 20 (25kWh)
Sharp 170W x 27 + YingLi 230W x 16 (8.3kW)