Hello everyone, First post in a while:
I have a 48V Trojan Industrial Bank (IND17-6v x 8 batteries) on a 10,000 watt LG Array - Outback Radian 7048 hybrid system , has been in use for the last 4 years. No issues.
It appears that one of the HYDROLINK auto-watering valves got stuck approx 3 months ago and was not adding water to 1 cell. (#1 on battery #1) .....Last time visually checked all cells was in Feb. (that will teach me to rely on the auto watering system)
The water was about 2 liters low, Id say about 80% full of water in these giant batteries, cell appears slightly / partially exposed SG is reading very low... All other 23 cells are GOOD SG 1.280 +/-
My question for the experienced ones, what should be done to attempt a restore, I have refilled the battery with Distilled and started a EQ charge for 3 hours, but now thinking that maybe EQ is not a good idea?
Looking for some advice here.
Thank you!!!!!!
I have a 48V Trojan Industrial Bank (IND17-6v x 8 batteries) on a 10,000 watt LG Array - Outback Radian 7048 hybrid system , has been in use for the last 4 years. No issues.
It appears that one of the HYDROLINK auto-watering valves got stuck approx 3 months ago and was not adding water to 1 cell. (#1 on battery #1) .....Last time visually checked all cells was in Feb. (that will teach me to rely on the auto watering system)

The water was about 2 liters low, Id say about 80% full of water in these giant batteries, cell appears slightly / partially exposed SG is reading very low... All other 23 cells are GOOD SG 1.280 +/-
My question for the experienced ones, what should be done to attempt a restore, I have refilled the battery with Distilled and started a EQ charge for 3 hours, but now thinking that maybe EQ is not a good idea?
Looking for some advice here.
Thank you!!!!!!
Outback Radian 7048 Hybrid @ 240V, 2x FLEXMAX 80, 10,000 Watt LG Array, 8x Trojan Industrial IND17-6v @ 48V, Honda 6500 @ 240v LPG Conversion, 2 Wire Auto Start Module. 4 Years OFF GRID 

Comments
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
In general, a battery with exposed plates (low water/electrolyte levels) is thought to be very bad news. And, you might have some cash saved to replace that one cell if your recovery process fails.
Do you have the ability to charge that one 6 volt battery at 5% to 2.5% rate of charge? The amount of "overcharging" of the rest of the batteries in the 48 volt battery bank does put them at risk too (running hot, over EQing, plate erosion, positive grid corrosion).
If you can limit your charging to just that one 6 volt battery, it will probably lengthen the life of the rest of your bank (of course the EQing is still hard on the other two cells in that battery).
And very sorry to hear that your auto-watering system missed that one cell. That hurt$.
-Bill
Mike here is a pic of the watering system/cap. "Flow-Rite"
Normal operations are about 85F-95F.
We are in a tropical climate so, its usually about 5F over the ambient temp. Just finished a full absorb cycle they are 102F, outside temp is about 96F today.
I have attached a backup sensor to the battery and right on the cell in question for some additional monitoring. It looks to be in line with the other sensor.