How many amp hours does a compressor fridge consume?

MattyMatty Registered Users Posts: 20 ✭✭
edited February 11 in Solar Beginners Corner #1
I am looking at a solar setup that includes a compressor fridge (Secop / Danfoss) and I want to get an idea as to how many amp hours per day the fridge will consume. The fridge is rated to draw 2.5-5A depending on ambient temperature and whether it is in fridge or freezer mode. Does a compressor fridge draw this amount of current continuously 24/7? If so then I can expect it to consume 60-120Ah per day. Is this what I can expect or does a compressor fridge only draw charge part of the time?

Comments

  • mcgivormcgivor Solar Expert Posts: 2,566 ✭✭✭✭✭
    There are many factors which determine the duty cycle, ambient temperature, how many times the door is opened, how much product is inside, how much warm product is stocked, thermostat setting and so forth. The compressor won't run 24/7 but will cycle within the throttling range of the thermostat setpoint, perhaps 1-2 degrees plus or minus, baring leaving the door open. For the past month I've been logging my refrigerator's consumption with a power logging device, nothing has changed much with regards to content habits etcetera, but there is a clear correlation during the hot days we've had lately and consumption increase, perhaps a 15-20% increase. 

    So the real answer is it depends on all the above factors, but a rough guide would be to assume a 33-45% duty cycle, only real data logging will reveal the actual consumption. The energy guide figures provided with my unit are pretty consistent with what I've logged so far, but 1 month is less than 10% of a year, but honestly I don't see too much that would indicate an increase much above said guide figures. For the sake of system design using a 50% duty cycle probably won't lead to dissapointment, in othere words don't underestimate, for many the refrigerator is the single highest consuming load, it never sleeps, just takes naps every so often.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery bank 
    900W  3 × 300W No name brand Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah FLA 24V nominal as a backup system. 
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergencies and welding.
  • MattyMatty Registered Users Posts: 20 ✭✭
    edited February 11 #3
    mcgivor said:
    There are many factors which determine the duty cycle, ambient temperature, how many times the door is opened, how much product is inside, how much warm product is stocked, thermostat setting and so forth. The compressor won't run 24/7 but will cycle within the throttling range of the thermostat setpoint, perhaps 1-2 degrees plus or minus, baring leaving the door open. For the past month I've been logging my refrigerator's consumption with a power logging device, nothing has changed much with regards to content habits etcetera, but there is a clear correlation during the hot days we've had lately and consumption increase, perhaps a 15-20% increase. 

    So the real answer is it depends on all the above factors, but a rough guide would be to assume a 33-45% duty cycle, only real data logging will reveal the actual consumption. The energy guide figures provided with my unit are pretty consistent with what I've logged so far, but 1 month is less than 10% of a year, but honestly I don't see too much that would indicate an increase much above said guide figures. For the sake of system design using a 50% duty cycle probably won't lead to dissapointment, in othere words don't underestimate, for many the refrigerator is the single highest consuming load, it never sleeps, just takes naps every so often.
    So could I roughly work on the assumption that if the fridge draws 2.5-5A with a 50% duty cycle then it would consume around 30-60Ah per day? What I am wanting is an upper limit to use as a basis for determining the battery bank size and solar panel wattage required.
  • mcgivormcgivor Solar Expert Posts: 2,566 ✭✭✭✭✭
    That's  what I would use, a 50% duty cycle just to reduce a 'Jack in the box supprise" the refrigerator to me is the single most important load, I made many underestimated decisions in the past which cost me dearly, then again education is not free, unless it is offered for free, never underestimate, in fact double the anticipated needs, you won't regret it, the sun can be unpredictable at times.
    1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery bank 
    900W  3 × 300W No name brand Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah FLA 24V nominal as a backup system. 
    5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergencies and welding.
  • EstragonEstragon Registered Users Posts: 3,262 ✭✭✭✭✭
    I'd try to clarify the amp draw rating in terms of whether it's an average or max draw.  If max, you can use an estimated duty cycle to get average daily consumption.  The rating may be an average draw though, in which case the duty cycle would already be taken into account.

    It's may well be max draw, but given there's a potential 2-3x margin on the consumption between max and average, it might be worth clarifying.
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • 706jim706jim Solar Expert Posts: 223 ✭✭✭
    I have an 11.5 cubic foot Insignia fridge/freezer. The Energuide rating is  just over 300 Kwhr/ year or approximately 1 Kwhr per day. I think that is a good starting point as practical monitoring seems to agree with this figure. You can go back to amp hours depending on your battery voltage with the usual conversion losses.
    Island cottage solar system with 1400 watts of panels, Trace DR1524 MSW inverter, Trace C40 PWM controller 8 Trojan L16's. Insignia 11.5 cubic foot electric fridge. My 26th year.
  • MattyMatty Registered Users Posts: 20 ✭✭
    Estragon said:
    I'd try to clarify the amp draw rating in terms of whether it's an average or max draw.  If max, you can use an estimated duty cycle to get average daily consumption.  The rating may be an average draw though, in which case the duty cycle would already be taken into account.

    It's may well be max draw, but given there's a potential 2-3x margin on the consumption between max and average, it might be worth clarifying.
    That’s a good point. I’ll need to confirm this with the manufacturer. The following energy consumption rating is in the product documentation (see below). It’s not really clear. I’m not sure what the units A/HR actually means. I’m guessing they mean “Ah per hour” in which case the duty cycle may have already been taken into account. In the extreme case where both compartments are on freezer with ambient temperature over 40°C, the manufacturer quoted a rating of up to “5A”. If the duty cycle is taken into account then this would represent a potential consumption rate of up to 120Ah per day. Does this sound correct with regard to the energy consumption that would be expected of a Secop / Danfoss compressor?

    ENERGY CONSUMPTION: 

    BOTH COMPARTMENTS POWER USE AT 3​°​C (1.5 A/HR) 

    BOTH COMPARTMENTS POWER USE AT ​-18​°​ (3.0 A/HR) 

    COMPARTMENTS POWER USE SPLIT AT 3°​C / ​-18​°​C (2.5-2.8 A/HR) 

    *The energy consumption rating is based on an ambient temperature of 32C*

  • MattyMatty Registered Users Posts: 20 ✭✭
    edited February 11 #8
    706jim said:
    I have an 11.5 cubic foot Insignia fridge/freezer. The Energuide rating is  just over 300 Kwhr/ year or approximately 1 Kwhr per day. I think that is a good starting point as practical monitoring seems to agree with this figure. You can go back to amp hours depending on your battery voltage with the usual conversion losses.
    I assume that this energy consumption rating is an average and the average current draw is about 2.85A at 12V which is in the ballpark of what was quoted for the fridge that I have been examining.
  • EstragonEstragon Registered Users Posts: 3,262 ✭✭✭✭✭
    That does sound like duty cycle is already in the numbers.  A/Hr is a rate.  Ahr is a quantity.  1.5a (rate) run for 1hr = 1.5ah (quantity).  At 1.5a/hr, quantity would be 36ah.  At 2.8a/hr for combined fridge/freezer, that would be 67ah or 800wh per day, which sounds about right for a typically insulated commercial DC unit.

    My danfoss compressors can have speed set via resistor values wired into control box.  Higher speed makes it cool faster with higher amp draw.  Presumably, the "up to 5A draw" would be in a case where the compressor has the resistor value for max speed.  Running faster would mean a lower duty cycle, but my understanding is the overall consumption (ah/day) is a bit worse running at higher speed (likely because of limitations in dissipating heat).
    Off-grid.  
    Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
    Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
  • TecnodaveTecnodave Registered Users Posts: 67 ✭✭
    I have 2 Grape Solar GS-5 5.0 cu ft referigerator's running directly from 24 volt bank of L-16's One is normal temp 36-39 degrees, the other is a vegetable box running at 44-48 degrees. I have Chinese volt/amp/watt/kW totalizers on each unit, been logging them for a year now.    Cool box runs 30-35% duty cycle and is opened >12 times a day  total power per day is 300 watt hours. Veggie box runs 21-25 % duty cycle and is opened 2 times a day. Total power per day is 200 watt hours.

    these referigerator's have a Chinese knockoff of the Danfoss compressor ,  The Colku, I've seen both compressor setups up close and they are close to identical , both are DC permanent magnet motors, are variable speed. 

    Huge price difference, I was looking at >1200$ for the Sundanzer upright which I never found. I saw the Grape Solar at Home Depot online and paid about $800 for the first one delivered to my local Home Depot. It failed in about 11 months into the 1 year warranty ,  freezer compartment door hinges broke off, resulting in loss of temperature control. Grape Solar warranties it and shipped me a new one no charge. I made a patch fix for the broken one with a styrofoam plug in place of the freezer compartment. This one is the warm box now. No freezer as temp in main compartment is too high.

    Huge difference than running energy star 120 AC frig off the inverter, well worth the price difference , no regrets

    Unfortunately Grape Solar has exited the DC referigerator business.  They had a good product!

    david
  • MattyMatty Registered Users Posts: 20 ✭✭
    Estragon said:
    That does sound like duty cycle is already in the numbers.  A/Hr is a rate.  Ahr is a quantity.  1.5a (rate) run for 1hr = 1.5ah (quantity).  At 1.5a/hr, quantity would be 36ah.  At 2.8a/hr for combined fridge/freezer, that would be 67ah or 800wh per day, which sounds about right for a typically insulated commercial DC unit.

    My danfoss compressors can have speed set via resistor values wired into control box.  Higher speed makes it cool faster with higher amp draw.  Presumably, the "up to 5A draw" would be in a case where the compressor has the resistor value for max speed.  Running faster would mean a lower duty cycle, but my understanding is the overall consumption (ah/day) is a bit worse running at higher speed (likely because of limitations in dissipating heat).
    The unit Amp is already a rate (Coulombs per second). So I’m not sure what adding “per hour” actually means. It sounds like a unit of acceleration of electrical charge. Is “Amps per hour” a unit in electrical engineering?

    It does sound like the duty cycle is already taken into account. The quoted 5A draw was for when both compartments of the dual zone unit are set to freezer and the ambient temperature is extreme (> 40°C). 
  • MattyMatty Registered Users Posts: 20 ✭✭
    Tecnodave said:
    I have 2 Grape Solar GS-5 5.0 cu ft referigerator's running directly from 24 volt bank of L-16's One is normal temp 36-39 degrees, the other is a vegetable box running at 44-48 degrees. I have Chinese volt/amp/watt/kW totalizers on each unit, been logging them for a year now.    Cool box runs 30-35% duty cycle and is opened >12 times a day  total power per day is 300 watt hours. Veggie box runs 21-25 % duty cycle and is opened 2 times a day. Total power per day is 200 watt hours.

    these referigerator's have a Chinese knockoff of the Danfoss compressor ,  The Colku, I've seen both compressor setups up close and they are close to identical , both are DC permanent magnet motors, are variable speed. 

    Huge price difference, I was looking at >1200$ for the Sundanzer upright which I never found. I saw the Grape Solar at Home Depot online and paid about $800 for the first one delivered to my local Home Depot. It failed in about 11 months into the 1 year warranty ,  freezer compartment door hinges broke off, resulting in loss of temperature control. Grape Solar warranties it and shipped me a new one no charge. I made a patch fix for the broken one with a styrofoam plug in place of the freezer compartment. This one is the warm box now. No freezer as temp in main compartment is too high.

    Huge difference than running energy star 120 AC frig off the inverter, well worth the price difference , no regrets

    Unfortunately Grape Solar has exited the DC referigerator business.  They had a good product!

    david
    I believe the Sundanzer DC fridge is one of the most energy efficient units out there. Do you know whether they are still available?
  • TecnodaveTecnodave Registered Users Posts: 67 ✭✭
    Matty, 

    Sundanzer is alive and well. The chest types are the most efficient and have been the most reliable. They are available at NAWS store and many other dealers. These units are of the best quality. Their upright is less efficient due to the design difference, open the door and the cold rushes out. They are in short supply sometimes (the uprights). That is what I wanted but I could not locate at that time. The chest types are 50-60 inches wide and I live in compact spaces 

     others that I have been looking at:

    EcoSolarCool.     Looks good but I have not used one, nor seen one in person

    Grape Solar        Had some great looking units,  they have exited the referigerator business.  They still do panels

    Green Energy Innovations,     Many models , mostly uprights, Asian imports.      They have sent me catalogs but when I poke the website I find maybe another company, same name doing commercial LED lighting, not sure if they are in the business.  Uprights only only but in a size that I have never seen in America. All units  19" wide by 19" deep ????
     
       [email protected]  

    I have catalogs of product, I will email that if you cannot find that....PM me.    .pdf file.  (Adobe Acrobat required to view)

    there is one other whose name escapes me right now,


    David
  • cptdondocptdondo Solar Expert Posts: 67 ✭✭✭
    I had an Isotherm Cruise 130 with the Danfoss BD35 and Isotherm's ASU technology that I instrumented.  On a cool, overcast day it would use about 15Ah.  On a scorching hot day it would use about 70Ah.  YMMV but for a medium sized fridge those numbers should be representative.  Of course if you have a dual compressor fridge like the Cruise 195 you probably need to double those numbers and a smaller fridge would use less.
  • TecnodaveTecnodave Registered Users Posts: 67 ✭✭
    Update on geinnovations,

    geinnovations.com   Is the commercial LED lighting company
    geinnovations.net     Is the dealer I was speaking of


    from their webpage:

    recommended minimum system to support frig only:  

    92 liter unit.              120 watt panel.   100 a.h. Battery
    118  & 142 liter         160.   ".                120.    "
    158 & 178.                180.                      150
    198 liter.                     200.     ".              150.   


    I can verify, I have run my grape solar unit one 1 100 watt panel and 1 105 a.h. AGM Battery,  no problem at all,

    My catalogs have confidential dealer pricing so probably not valid for 1 quantity.

    I am not a dealer for them, they would like me to be.

    David
  • TecnodaveTecnodave Registered Users Posts: 67 ✭✭
    Matty, 

    on on the energy conversion,

    watts are volts times amps,

    12 volts times 10 amps is 120 watts,

    amp hours are amps times hours.....what is missing here is volts....so
    amp hours times volts is watt hours....or

    amps X volts  X   time (hours) is watt hours    normally expressed as kilowatt hours.    1000 watt hours is 1 kWh 

    my my grape solar units use.  13.6 volts 3.4 amps  or 27.2  volts  1.7 amps.  46 watts .  rated max draw is 95 watts,  I have never seen it draw that much.

    Also has 120 volt converter built in , have used it but did not log that.

    when using 120 volts unit will not run on my inverters  when in energy saving mode, sleep mode. The converter needs to be powered continuously.  There is a delay of maybe 15 seconds after powering up before compressor will start both in DC operation and AC operation. Do not know if this is true for the Sundanzer units

    david
  • BB.BB. Super Moderators, Administrators Posts: 28,441 admin
    TechnoDave has correctly addressed the Amp vs Amp*Hour question (Amp/hour or Amps per hour is not a useful/meaningful unit/number for us here).

    And, as Dave showed, when talking about Amps and Amp*Hours, you need to know the working voltage. Typically (from what I have seen) the DC Compressors from Danfoss are 12/24 volt capable units. And they are constant power (watts) where Power=Voltage*Current.

    Running on a 12 volt bus, the compressors draws 2x more current (amps) vs running on a 24 volt bus. However, power/energy wise, they are about the same Watts and Watt*Hours per day (remember power=volts*current, 2x more voltage and 1/2 current is same power).

    -Bill