Connecting multiple solar panels and controllers to a single battery bank
Matty
Registered Users Posts: 36 ✭✭
I have 2 identical 100W solar panels each with a built-in PWM controller connected to 2 x 130Ah 12V batteries wired in parallel. The 2 panels connect to a bifurcated cable with Anderson plugs so that a single O ring connects to each battery terminal. I enquired with another solar panel supplier about adding one of their 300W panels which also has a PWM controller. They said that you must only use one controller per solar panel array / battery bank. My 100W panels each have their own built-in controller and they are hard wired so I can’t see how I could modify the wiring to make them both charge through one controller. The supplier of those panels didn’t say anything about using a single controller with both panels. I’d like some clarification about connnecting multiple solar panels and controllers to a single battery bank.
Comments
-
I have 3 pv arrays feeding 3 controllers (2 mmpt & 1 pwm type), plus 2 AC chargers connected to a single 48v bank. It generally works fine.
Multiple panels (an array) to a single controller is fine, providing wiring is done right for the controller used.
Multiple charge controllers (esp. mppt type) connected to a single panel/array can be an issue and should generally be avoided.
Multiple charging sources to a single battery/ bank is generally fine. A potential issue can be controllers changing charge state independently (eg one goes to float before others). In general, this isn't a big issue though.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Contrary to the advice I was given, is it actually more problematic connecting multiple solar panels to a single shared controller as opposed to each panel having its own dedicated controller?
So each solar panel connected to a battery bank can and should be independent of the other and charge through its own dedicated controller?
I also have an inverter connected to the battery. If I connect more panels to the battery then I’m potentially going to run out of space on the terminals to fit the O rings and washers onto. Is there some kind of adapter available to solve this problem and create more terminal contact space or is the solution to use fewer and higher wattage panels?
-
Matty said:Contrary to the advice I was given, is it actually more problematic connecting multiple solar panels to a single shared controller as opposed to each panel having its own dedicated controller?
So each solar panel connected to a battery bank can and should be independent of the other and charge through its own dedicated controller?
I also have an inverter connected to the battery. If I connect more panels to the battery then I’m potentially going to run out of space on the terminals to fit the O rings and washers onto. Is there some kind of adapter available to solve this problem and create more terminal contact space or is the solution to use fewer and higher wattage panels?1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Multiple panels to a single controller can be fine, as long as the wiring and controller are right. I have a total of 18 x 250w panels wired in two array of nine, through two mppt controllers, to a 48v bank. Also a third array of 2 x 300w panels, through a pwm controller to the same bank.
In your case, the 300w panel with inbuilt controller may or may not work. A panel that size would typically have a working voltage of ~38v, and with a pwm controller would likely be for a 24v nominal bank. It may be wired internally as 2 x 12v nominal panels in parallel though, with a shared 12v nominal pwm controller. If so, it could be added in parallel with your existing 12v nominal panels.
Rather than stacking more on crowded battery terminals (inefficient and potentially unsafe), what's often done is to have a single pair of heavy wires going from battery/bank to a positive and a negative buss bar. These can be bought premade (eg from our hosts), or can be DIY from copper bar or tube stock and SS bolts. Controllers, inverters, etc are connected to the buss bars (with wire and breakers/fuses sized for the particular device).Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
mcgivor said:Matty said:Contrary to the advice I was given, is it actually more problematic connecting multiple solar panels to a single shared controller as opposed to each panel having its own dedicated controller?
So each solar panel connected to a battery bank can and should be independent of the other and charge through its own dedicated controller?
I also have an inverter connected to the battery. If I connect more panels to the battery then I’m potentially going to run out of space on the terminals to fit the O rings and washers onto. Is there some kind of adapter available to solve this problem and create more terminal contact space or is the solution to use fewer and higher wattage panels? -
Estragon said:Multiple panels to a single controller can be fine, as long as the wiring and controller are right. I have a total of 18 x 250w panels wired in two array of nine, through two mppt controllers, to a 48v bank. Also a third array of 2 x 300w panels, through a pwm controller to the same bank.
In your case, the 300w panel with inbuilt controller may or may not work. A panel that size would typically have a working voltage of ~38v, and with a pwm controller would likely be for a 24v nominal bank. It may be wired internally as 2 x 12v nominal panels in parallel though, with a shared 12v nominal pwm controller. If so, it could be added in parallel with your existing 12v nominal panels.
Rather than stacking more on crowded battery terminals (inefficient and potentially unsafe), what's often done is to have a single pair of heavy wires going from battery/bank to a positive and a negative buss bar. These can be bought premade (eg from our hosts), or can be DIY from copper bar or tube stock and SS bolts. Controllers, inverters, etc are connected to the buss bars (with wire and breakers/fuses sized for the particular device).
These are the specifications for the 300W panel. I believe it’s designed for 12V battery systems.• 300W Rated Maximum Power• ±3% Tolerance• 18V @ Pmax (VMP)• 16.6A @ Pmax (IMP)• 21.6V Open Circuit Voltage (VOC)• 22.55A Short Circuit Current (ISC)• 1000V DC Maximum System Voltage• 10A Maximum Series Fuse Rating -
No, I wouldn't say it's ideal or even preferable to have a separate controller for each panel. It very much depends on the specific application, but in most, multiple panels on a single controller works fine.
It does appear to be 12v nominal panel(s). Not sure about a 10a max series fuse with Imp of 16.6a though?
Adding fridge/freezer to a system generally moves system size up a notch or two. A typical AC fridge is ~1500wh/day, and needs an inverter big enough to start it. A single 300w added panel is unlikely to support this addition on a daily, year-round basis. It may work for something like a weekend summer cabin though.
Boosters can also use a fair bit if left on 24x7 (I think mine would be on the order of 5-600wh/day + inverter losses). I turn mine off when not in use.
As @mcgivor suggests, you may be getting to a point where it's worth thinking about what a future ideal system might look like. Alternatively, you could go ahead with some extra pv for extra loads, and maybe a generator for now.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Estragon said:No, I wouldn't say it's ideal or even preferable to have a separate controller for each panel. It very much depends on the specific application, but in most, multiple panels on a single controller works fine.
It does appear to be 12v nominal panel(s). Not sure about a 10a max series fuse with Imp of 16.6a though?
Adding fridge/freezer to a system generally moves system size up a notch or two. A typical AC fridge is ~1500wh/day, and needs an inverter big enough to start it. A single 300w added panel is unlikely to support this addition on a daily, year-round basis. It may work for something like a weekend summer cabin though.
Boosters can also use a fair bit if left on 24x7 (I think mine would be on the order of 5-600wh/day + inverter losses). I turn mine off when not in use.
As @mcgivor suggests, you may be getting to a point where it's worth thinking about what a future ideal system might look like. Alternatively, you could go ahead with some extra pv for extra loads, and maybe a generator for now. -
DC fridges do tend to take less to run - the DC chest fridge/freezer on my boat runs in the ballpark of what you suggest or a bit less if it's only filled with precooled stuff. DC also avoids running an inverter big enough to start an AC fridge, which could use a few 100s of wh/day. Overall, maybe 1/2 the consumption of a typical AC fridge, so the extra panel may well support the load.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Estragon said:DC fridges do tend to take less to run - the DC chest fridge/freezer on my boat runs in the ballpark of what you suggest or a bit less if it's only filled with precooled stuff. DC also avoids running an inverter big enough to start an AC fridge, which could use a few 100s of wh/day. Overall, maybe 1/2 the consumption of a typical AC fridge, so the extra panel may well support the load.
-
The calculation for the refrigerator 864Wh would be based on a 100% duty cycle, probably a good way to estimate on the safe side, the amount of harvest really depends on location, both geographic and physical. The 12VDC refrigerator seems very efficient with no inverter needs but it is important to remember the solar modules need to be in direct sunlight without shading of any sort and positioned correctly.
This is not the easiest task on a mobile application, usually means parking in an open area, or by using a movable array, either way it's prudent to not build too conservatively based on proposed useage, most successful off grid users have more capacity than needed to not only get through times of poor sun, but also to recover from these times.
From the information provided regarding panels with their own controllers I'd be inclined to use multiple modules in parallel with a single controller, rationale is there would be a single charging algorithm which is more precise than multiple sources.There are excellent PWM controllers available at reasonable costs, some of which can be programmed to suit specific needs of the battery, naturally cost is relative to the individual but a professional unit can be had for less than $200, down to a generic one for $50 or less.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
What I've found with DC vs AC units is the DC (at least the common Danfoss based ones) tend to be better at keeping stuff cool than getting them cool. Some have provision to adjust speed, but even on high speed they tend to cool slower than an AC unit.
Overall consumption varies a lot with box insulation, ambient temp, etc. My boat unit isn't all that well insulated, and uses ~750wh daily. A similar sized but heavily insulated unit I built in the cabin uses ~150wh/day.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Estragon said:What I've found with DC vs AC units is the DC (at least the common Danfoss based ones) tend to be better at keeping stuff cool than getting them cool. Some have provision to adjust speed, but even on high speed they tend to cool slower than an AC unit.
Overall consumption varies a lot with box insulation, ambient temp, etc. My boat unit isn't all that well insulated, and uses ~750wh daily. A similar sized but heavily insulated unit I built in the cabin uses ~150wh/day. -
mcgivor said:The calculation for the refrigerator 864Wh would be based on a 100% duty cycle, probably a good way to estimate on the safe side, the amount of harvest really depends on location, both geographic and physical. The 12VDC refrigerator seems very efficient with no inverter needs but it is important to remember the solar modules need to be in direct sunlight without shading of any sort and positioned correctly.
This is not the easiest task on a mobile application, usually means parking in an open area, or by using a movable array, either way it's prudent to not build too conservatively based on proposed useage, most successful off grid users have more capacity than needed to not only get through times of poor sun, but also to recover from these times.
From the information provided regarding panels with their own controllers I'd be inclined to use multiple modules in parallel with a single controller, rationale is there would be a single charging algorithm which is more precise than multiple sources.There are excellent PWM controllers available at reasonable costs, some of which can be programmed to suit specific needs of the battery, naturally cost is relative to the individual but a professional unit can be had for less than $200, down to a generic one for $50 or less.
Given I already have panels each with their own built-in controller that I can just plug in and go, is the benefit of using a single controller worth the potential additional cost of another unified controller (not sure whether I could just use one of the existing ones) and the time to research how to rewire the system to make sure I know what I am doing? -
If the evaporator is a box type with a door, I've found frozen food stays frozen in the freezer box in the boat chest fridge/freezer. Warm food/drinks will eventually get cold, but just take longer than an AC fridge. The effect of high ambient temp will depend on the box insulation, if not a chest type, frequency of door opening.
To help with power consumption we sometimes get a block of ice and put it on the bottom of the chest fridge/freezer. It lasts quite a while.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
If the panels already have controllers, I see no good reason to use any additional controllers. As mentioned above, having multiple controllers on a bank is generally fine.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
@MattY said
Given I already have panels each with their own built-in controller that I can just plug in and go, is the benefit of using a single controller worth the potential additional cost of another unified controller (not sure whether I could just use one of the existing ones) and the time to research how to rewire the system to make sure I know what I am doing?
Can you provide a link to the panel with integrated controller, as well as the 300W controller, or do you know the specifications? There are different charge algorithms for different battery types, whilst it is possible to have multiple controllers work if all follow the same charge profile, not knowing the the specifications makes it difficult to say definitively one way or another. Having a single controller with a display, can provide information at a glance wether the battery is charging, discharged, in float or some other state, they also provide low battery cut out to protect against completely discharging the battery.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:
@MattY said
Given I already have panels each with their own built-in controller that I can just plug in and go, is the benefit of using a single controller worth the potential additional cost of another unified controller (not sure whether I could just use one of the existing ones) and the time to research how to rewire the system to make sure I know what I am doing?
Can you provide a link to the panel with integrated controller, as well as the 300W controller, or do you know the specifications? There are different charge algorithms for different battery types, whilst it is possible to have multiple controllers work if all follow the same charge profile, not knowing the the specifications makes it difficult to say definitively one way or another. Having a single controller with a display, can provide information at a glance wether the battery is charging, discharged, in float or some other state, they also provide low battery cut out to protect against completely discharging the battery.100W Folding Solar Panel Kit 12V, A grade Monocrystaline cells & PWM Solar ControllerIP65 rated, 10A waterproof regulator mounted to solid steel standMaximum Power 100WOpen Circuit Voltage (Voc) 21.60VShort Circuit Current (lsc) 6.00AMaximum Power Voltage 18VMaximum Power current(lmp) 5.56AWorking Temperature -40C to +85CTolerance +-3%300W 12V Portable Camping Folding Solar Panel & PWM Solar Controller300W Rated Maximum Power±3% Tolerance18V @ Pmax (VMP)16.6A @ Pmax (IMP)21.6V Open Circuit Voltage (VOC)22.55A Short Circuit Current (ISC)1000V DC Maximum System Voltage10A Maximum Series Fuse Rating-40C - 85C Operating TemperatureClass A-Cell GradeMonocrystalline Silicon Cell Technology -
The charge controller specifications are the most important, what type of battery are they designed to charge, AGM, GEL, Flooded lead-acid or some other type, each have particular voltage requirements, so it's important to have the correct value. For example, if one is designed for flooded lead acid, it would damage an AGM lead acid by overcharging, conversely if designed for AGM, it would undercharge a flooded battery. These characteristics may not appear immediately but will result in problems over time if not the correct values. These are the very basic requirements, batteries in hot or cold environments need compensation to increase or decrease voltage depending on temperature, better quality controllers have this capability with a teperature sensor attached to the battery.
In short it depends entirely on expectations, saving money is often more expensive, in the long run.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I have never heard of solar panels with built in controllers so I can not comment on that. I have two systems side by side that can be coupled. I use MidNite controllers for charging and it works fine. The controllers do not equally share the charging duties with one controller going to adsorb or float before the others. Most times I will have one Classic 150 and one Kid on each bank, but when I have inclement weather all four controllers are assigned to one bank. I only parallel the bank's when using very large loads due to the fact that the batteries are not a matched set. One bank is 4 X new interstate L-16's and the other are 4 X Rolls-Surette S-530's L-16's salvaged from recycle, they are over 10-12 years old or older. This works well as when separated they get a full charge and get to 1.265 s.g. And are equalized. No problems at all. Sometimes the Kid controllers are assigned to other duties. My systems are allways changing, sometimes daily.
on the referigerator , I am using two Grape Solar GS-5 units. These have a Chinese knockoff of the Danfoss compressor , The Colku. I am using 200 -250 watt hour per day per unit. Have Chinese volt/amp/watt meter on each unit for data logging. Use is in 38 foot fifth wheel travel trailer which is used as a house in mountains. Heated space at 65 degrees. Grape Solar has since exited the referigerator business, too bad , these are great units. Purchased at Home Depot Online for about $800 / one unit.
Hope this info is useful
david2 Classic 150, 2 Kid, 5 arrays 7.5 kw total 2ea. 2S6P Sharp NE-170/NE-165, 1ea. 12P Sanyo HIT 200, 2ea. 4/6P Sanyo HIT 200, MagnaSine MS4024AE, Exeltech XP-1100, 2 Banks L-16 battery, Rolls-Surette S-530 and Interstate Traction, Shunts with whizbangJr and Bogart Tri-Metric, iCharger i208B dc-dc buck/boost converter with BMS for small form lithium 8S 16650 or LiFePO4, -
Hi,I'm in the process of designing my off-grid PV system which will be located in the rural Philippines, where solar components are not readily available and shipping stuff in is costly and time consuming. Therefore, I'm trying to design the system for maximum resilience.My initial paper design is to feed my 8KW PV array into a 600AH 48V LFP battery bank and to run 2 separate 5KVA DC-AC inverters (output 230VAC) off of the same battery bank. Each inverter will be connected to a completely separate distribution panel. Each DP will feed separate household branch circuits.My question for the more experienced solar system experts is whether connecting 2 separate inverters to a single LFP battery bank is OK? Do I need to sync the inverters, even though they are connected to completely separate loads?.Any advice would be much appreciated.
-
Feeding two incompatible inverters from a single battery would be fine as long as the outputs of each inverter are isolated from one another, if the inverters are able to sync their outputs then it could be possible to connect outputs in parallel, but from the information provided, it would be safe to assume this is not the case.
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Estragon said:I have 3 pv arrays feeding 3 controllers (2 mmpt & 1 pwm type), plus 2 AC chargers connected to a single 48v bank. It generally works fine.
Multiple panels (an array) to a single controller is fine, providing wiring is done right for the controller used.
Multiple charge controllers (esp. mppt type) connected to a single panel/array can be an issue and should generally be avoided.
Multiple charging sources to a single battery/ bank is generally fine. A potential issue can be controllers changing charge state independently (eg one goes to float before others). In general, this isn't a big issue though.I'm a newbie to solar, but as I laid in bed last night I remembered the solar info I read that if panels are connected together especially in parallel, the system would only be as good as the weakest link. So it makes perfect sense to have a separate controller with each panel. I just bought 3 new 100W panels and they all came with a free 30 PWM controller. That sent me a clear message that I won't drag down any other panels that might be shaded if all the panels are separated by controllers. -
Sparkyspirit said:Estragon said:I have 3 pv arrays feeding 3 controllers (2 mmpt & 1 pwm type), plus 2 AC chargers connected to a single 48v bank. It generally works fine.
Multiple panels (an array) to a single controller is fine, providing wiring is done right for the controller used.
Multiple charge controllers (esp. mppt type) connected to a single panel/array can be an issue and should generally be avoided.
Multiple charging sources to a single battery/ bank is generally fine. A potential issue can be controllers changing charge state independently (eg one goes to float before others). In general, this isn't a big issue though.I'm a newbie to solar, but as I laid in bed last night I remembered the solar info I read that if panels are connected together especially in parallel, the system would only be as good as the weakest link. So it makes perfect sense to have a separate controller with each panel. I just bought 3 new 100W panels and they all came with a free 30 PWM controller. That sent me a clear message that I won't drag down any other panels that might be shaded if all the panels are separated by controllers.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:Estragon said:I have 3 pv arrays feeding 3 controllers (2 mmpt & 1 pwm type), plus 2 AC chargers connected to a single 48v bank. It generally works fine.
Multiple panels (an array) to a single controller is fine, providing wiring is done right for the controller used.
Multiple charge controllers (esp. mppt type) connected to a single panel/array can be an issue and should generally be avoided.
Multiple charging sources to a single battery/ bank is generally fine. A potential issue can be controllers changing charge state independently (eg one goes to float before others). In general, this isn't a big issue though.I'm a newbie to solar, but as I laid in bed last night I remembered the solar info I read that if panels are connected together especially in parallel, the system would only be as good as the weakest link. So it makes perfect sense to have a separate controller with each panel. I just bought 3 new 100W panels and they all came with a free 30 PWM controller. That sent me a clear message that I won't drag down any other panels that might be shaded if all the panels are separated by controllers.
-
I'm a newbie to solar, but as I laid in bed last night I remembered the solar info I read that if panels are connected together especially in parallel, the system would only be as good as the weakest link. So it makes perfect sense to have a separate controller with each panel. I just bought 3 new 100W panels and they all came with a free 30 PWM controller. That sent me a clear message that I won't drag down any other panels that might be shaded if all the panels are separated by controllers.
Better keep asking and sleeping before you decide, because something is not right with what you posted.
I have 25 panels, wired properly into 2 controllers, and all works fine after 10 years.. no need to have 25 controllers
Remember - these are SOLAR panels, not shade panels. A panel in shade, produces next to nothing..
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
I have 3 PWM controllers charging my batteries. I don't believe there is a problem but then again I am not a techie. I have a meter measuring input to the main controller which today measured 750 Wh over today's sunny eight hours. Happy enough with that. Any extra from the other two much smaller controllers is a bonus.
7 x 150w panels through PWM TriStar TS-45, into 220 AH Crown battery bank.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed