Trina Solar TSM-280 Series wiring question

I need 3 panels in series. However, the specs
say Max Series Fuse 15a. My 3 panels together would be more than that. Should I use the fuses/breaker before combining or can I ignore that and use a 32a breaker after joining the string. Please see the picture of the panel babel attached.

Tagged:
Comments
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
You didn't mention whether the three panels are being connected as a series string (in which case @mcgivor is correct that current is the same as a single panel), or in parallel (in which case OCP is needed on each). Depending on the application, one way or the other of wiring could be best.
Edit... missed the ref to series in your post
Where/if the strings are paralleled, current adds, so OCP should be added on the parallel to combiner circuit and sized to protect the chosen wire size on that circuit.