Using a 2 watt coleman battery maintainer to keep batteries alive when not in use.
rp3703
Registered Users Posts: 129 ✭✭
Just for peace of mind, I’m trying to figure out if these coleman battery maintainers will keep my batteries alive through a Northern Ontario winter. I paired my 6V 215 AH batteries to make them 12V and attached a maintainer to each pair. The maintainers state they can deliver 15V @ 133 mAmps. Other than that, I can find no other info on them. Is it possible to make a good estimate of the viability of them keeping the batteries alive?
1860 W (6) Rensola JC310M, Classic 150, 430AH@24V (8) Deka DSGC15 FLA's, Victron Phoenix Multi 24/2500 Inverter
Powering-20.5 CuFt. Fridge, 1 HP Submersible water pump, UV, Washing Machine, Gas Dryer, Gas Stove, Lights and Receptacles
Off Grid Cottage on lake in Northern Ontario 46˚N
Powering-20.5 CuFt. Fridge, 1 HP Submersible water pump, UV, Washing Machine, Gas Dryer, Gas Stove, Lights and Receptacles
Off Grid Cottage on lake in Northern Ontario 46˚N
Comments
-
Northern Ontario winters are generally cold so self dischargeing would be of little concern if fully charged, left disconnected in an unheated space. Leaving something connected, in your absence could fail in undesirable ways. When fully charged a flooded lead acid battery will not freeze until -70°C, upon returning fully charge before use. Attached pdf provides information1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
With no controller between the panel and battery, I'd be a bit concerned there may be nothing preventing the batteries from keeping the panel warm. Maybe there's a blocking diode stopping higher voltage batteries from discharging into a lower voltage panel, but I wouldn't count on it without testing.
In a Northern Ontario winter, the batteries will be pretty cool most of the time, and have lower self-discharge. With no loads and fully charged, they should be fine from ~Oct-May.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Another voice saying just leave them alone over the winter.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
-
In case it was not obvious, I was asking whether this would work after the fact. I left my batteries like this at the end of last season and now I'm freaking out that they will be dead or after hearing from you guys, exploded with battery acid running all over the floor.1860 W (6) Rensola JC310M, Classic 150, 430AH@24V (8) Deka DSGC15 FLA's, Victron Phoenix Multi 24/2500 Inverter
Powering-20.5 CuFt. Fridge, 1 HP Submersible water pump, UV, Washing Machine, Gas Dryer, Gas Stove, Lights and Receptacles
Off Grid Cottage on lake in Northern Ontario 46˚N -
I've got a battery maintainer, and it has a red LED that lights when charging. It could be wired for forward/indicator and reverse/blocking, not sure if LED specs can handle 15Vrev bias
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
I have had very good with Battery Minders
https://www.amazon.com/BatteryMINDer-Model-2012-Maintainer-Motorcycles/dp/B005EKY1EM
On car batteries (that are rarely driven). Regular chargers and cheap float chargers would cause long term loss of water.
When the charger reads full you can move to the next set of batteries (1 or so days of charging). Reconnect every 30 days of 70f or 20c. If batteries are very cold (near or below freezing) then very low self discharge.
BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
rp3703 said:In case it was not obvious, I was asking whether this would work after the fact. I left my batteries like this at the end of last season and now I'm freaking out that they will be dead or after hearing from you guys, exploded with battery acid running all over the floor.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
> @rp3703 said:
> In case it was not obvious, I was asking whether this would work after the fact. I left my batteries like this at the end of last season and now I'm freaking out that they will be dead or after hearing from you guys, exploded with battery acid running all over the floor.
Most likely, the batteries are fine. If not, all you can do is make contingency plans. Freaking out won't make any difference to the batteries.
Earlier advice about leaving batteries alone for the winter was based on a ~Oct to May period when it's cool/cold. As it usually does, it warmed up in early May, with a few days near 30°C since, so having a maintainer may not be a bad idea.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed