Unusual heavy crystal formation on NEGATIVE terminal
williaty
Solar Expert Posts: 60 ✭✭
This is a new one on me. This is from a battery power system that has over time become a glorified UPS rather than a daily use system. It's been on float for.... well... a VERY long time because it's easy to forget the system is even there. I was startled to remember its existence today and figured I'd better do a safety check since the batteries are relatively old at this point. To my surprise and annoyance, when I opened the battery box, I was greeted by HEAVY blue-green corrosion on the NEGATIVE (not positive) terminal of the battery that serves as the negative terminal for the whole bank. There's also some copper-brown colored tendrils shooting out of the crystal formation as well. The negative terminal of the battery in series with the real offender also has some of the same crystals on it though to a much smaller extent.
1) What is this/why is it on the negative terminal (I'm used to seeing greener crystals on the positive terminals only on cars)?
2) What's the safest way to deal with it?
3) Does it indicate I need to do some kind of maintenance or repair?
Thanks as always!
1) What is this/why is it on the negative terminal (I'm used to seeing greener crystals on the positive terminals only on cars)?
2) What's the safest way to deal with it?
3) Does it indicate I need to do some kind of maintenance or repair?
Thanks as always!
Comments
-
Blue/green is copper. Yellow is sulfur. Somehow, acid has gotten to the cables or terminals. Either acid mist from charging, or simply the vapor.The cables need to be taken off, when it's safe to power down the system. Then with a toothbrush & baking soda water, clean the terminals. If you are lucky, only the terminals have corroded, and they are likely thick enough to safely reuse. Lightly wipe the battery terminal down with baking soda water, but don't let any get into the vent cap areas. You may need new nut/bolt, if so, use SS.If you discover the cable strands are the source, then you need new cables, when acid wicks into cables no way to clean it, and the conductors are compromised /eaten awayPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
They're AGM batteries, so they weren't supposed to do this at all. *grumble*
I can see it's eaten the nickle plate off the terminal ends and exposed the bare copper. I have no way to see if it extends up under the heat shrink tubing to the cabling. I hadn't even thought of that.
-
Normally, lead battery terminals would be anodic to the copper wire, so galvanic corrosion would result in the loss of lead to the copper cathode. This is common, for example, where copper water distribution pipes are directly connected to lead mains.
In this case though, the constant float voltage maybe overcoming the galvanic voltage, so you get electrolytic corrosion (forced reversal of anode/cathode) instead of galvanic? The electrolyte could be from the battery, or could be environmental (eg salt water mist). Once cleaned up, and if needed, wire replaced, a coating of vaseline over the connection should help avoid contact with electrolyte and slow the process.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
NO-OX-ID A-SPECIAL Is the best product made for battery connections. Not expensive and superior to other terminal coatings.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Looks like copper sulphate crystals, copper with sulphuric acid, would probably the nesesary ingredients, but the question is why or if are the batteries venting, if so, too high a voltage perhaps, what are your charge settings, is there an EQ involved, is temperature compensation utilized , all relevant questions. Are the batteries in a ventilated box or otherwise? Too long without discharge, saturating the batteries and effectively overcharging... rolling stones gather no moss, comes to mind. All speculation naturally.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I've experienced corrosion on my battery terminals although I would clean it off before it got this bad. I'm making up a second set of cables so that I can change them out and clean off the terminals every few months. I figure #4 cables are large enough for a maximum current of 40 amps in my system.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
-
corrosion seems heaviest at bolt terminal, not the wire end.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
How sure are you that the batteries have been only in float without some short regular charging such as when a solar charge controller comes on each morning and charges for a few minutes possibly overcharging the batteries causing venting?
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
-
Absolutely sure. It's a manual charge controller. I have to twiddle dials to change it from float up to Bulk/Absorb and then back down when the amps drop.
-
Does this controller have a name and model #?
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
It's a CC/CV power supply from a company called Volteq. It's the 30A/30V model.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed