Mixing panels with different Vmp/Voc
RoySalisbury
Solar Expert Posts: 84 ✭✭✭
I want to add more capacity to my solar setup. Since I can no longer get the same panels that I currently have, I need to get different panels. However, they are no longer going to have the same specifications. I'd try to stay with the same overall wattage of the panels, but the Vmp/Voc are not the same. Currently I have 6 of the following panels:
Kyocera KD320 (320 Watt). [Vmp - 40.1, Voc - 49.5]
These are setup with 2 in series, and 3 parallel. Going the other way would put me too close to the Voc max rating of the charge controller.
The closest that I can find form "Arizona Win/Sun" is
Silfab Solar 350 (350 watt). [Vmp - 38.9, Voc - 47.5]
When I setup a new string last time they were so far out of spec (210w vs 320w) that I setup a new charge controller just for the 6 320's. However, that's not an option now. I'm using an Outback MPPT charge controller (FM60 and FM80).
My understanding is that if I put 2 more of the 350's in and hooked them in parallel, then I should be fine .. with the restriction that that all my other panels will now get degraded in voltage to the lower set. Is that right?
If so, then I guess the 'extra' 100 watt on the new panels will make up for the loss. Also, since the panels normally operate higher then the Vmp, that as long as the newer panels operate above 40.1, then I won't really loose anything.
this is all very confusing. Any guidance from some experts would be appreciated.
Thanks.
Kyocera KD320 (320 Watt). [Vmp - 40.1, Voc - 49.5]
These are setup with 2 in series, and 3 parallel. Going the other way would put me too close to the Voc max rating of the charge controller.
The closest that I can find form "Arizona Win/Sun" is
Silfab Solar 350 (350 watt). [Vmp - 38.9, Voc - 47.5]
When I setup a new string last time they were so far out of spec (210w vs 320w) that I setup a new charge controller just for the 6 320's. However, that's not an option now. I'm using an Outback MPPT charge controller (FM60 and FM80).
My understanding is that if I put 2 more of the 350's in and hooked them in parallel, then I should be fine .. with the restriction that that all my other panels will now get degraded in voltage to the lower set. Is that right?
If so, then I guess the 'extra' 100 watt on the new panels will make up for the loss. Also, since the panels normally operate higher then the Vmp, that as long as the newer panels operate above 40.1, then I won't really loose anything.
this is all very confusing. Any guidance from some experts would be appreciated.
Thanks.
Comments
-
Just found this thread from 2012 that may be what I'm looking for.
http://forum.solar-electric.com/discussion/16660/panels-in-parallel-same-vmp-different-voc
Seems to indicate that I should be fine as the MPPT will settle on the voltage and the panels will adjust the amp to accommodate. So really should not lose anything as long as the Vmp of the lower panels does not fall below the Vmp of the higher.
-
I think it's a good match. The output of the new string should be about the same as the others. Almost as though 320 watt panels were installed.
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
With a different controller you'd have more flexibility. You could wire your Kyoceras in two arrays of 3 panels, with a Vmp of 120.3VDC. But the open circuit voltage of three would be dangerously close to the 150Voc limit of your Outback controllers. However, with a Midnight Classic 200 for example, you could match 3 Kyoceras wired in series to four generic grid-tie panels running at 30.1VDC. So, 3X40.1VDC=120.3VDC≈4X30.1VDC. One string of kyoceras would be putting out ~8.0 amps at 120.3VDC, while the second string of generics would be putting out about 8.4amps at 120.4VDC.
System 1) 15 Renogy 300w + 4 250W Astronergy panels, Midnight 200 CC, 8 Trojan L16 bat., Schneider XW6848 NA inverter, AC-Delco 6000w gen.System 2) 8 YingLi 250W panels, Midnight 200CC, three 8V Rolls batteries, Schneider Conext 4024 inverter (workshop) -
Hyper Voc. on a Classic 150 would allow up to 174 volts(open circuit) for a 24 volt system and 198 volts (open circuit) for a 48 volt system.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Remember that Midnite controllers go into "safe standby" when the Vmp-array is in the "hypervolt" range (controller does not charge the battery bank during hypervolt conditions).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Would that not usually be for the brief moment at daybreak while voltage is still in Voc.? It is called HyperVoc. Granted, it's not recommended to run the controller at it's limit. Just wanted to mention the extra headroom of the classics.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
I would guess that if you had an usually cold snap, then the panel Voc-cold may be too high for the Midnite to "start"--But once the direct sun hits the panel and it begins to warm, the Voc voltage will drop to normal operating range.
I don't think there is anything wrong with designing the system this way (you would not want to design your system to operate this way every day as you will lose some energy generation--And remember if the battery bank is disconnected for service, the Hypervolt range goes to zero until the battery is reconnected)--Just a point of information that the controller goes into standby when in Hypervolt range.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
littleharbor2 said:Would that not usually be for the brief moment at daybreak while voltage is still in Voc.? It is called HyperVoc. .....
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Extreme cold plus windy in the morning is pretty rare, at least in my climate. Extreme cold tends to occur when a large high pressure area settles in, which generally brings little wind - it gets windy with lows, which brings cloud anyway. IMHO, the few times cold&windy happens is more than made up for by not having to be overly conservative in array voltage.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
The last week, I've been tripping the overcurrent on my 60A morningstar, with an array that normally puts out about 45ACold and wind matter. My inverter has tripped offline twice, from overvoltage, because the charge controllers can't throttle back fast enough in cold scattered clouds.The cold had my array delivering an extra 15APowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Wow. I've not seen that, but the sun is low and weak in the cold here - I don't think I've ever seen over STC rating, and it has to be extremely cold for me to get near Voc limit.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed