Soft starter/vfd help
burcusa
Registered Users Posts: 2 ✭
Hi,
I am new to this board as I just moved into an off grid house about 3 months ago. I have a 24 V system with generator back up. My generator is a Perkins 10.5kw diesel generator (40A/leg). I just bought a new table saw. When I bought the saw I asked the salesperson about energy requirements and they said it need a 230V/20A circuit (but only used 13.8A at full load). So I wired that circuit in directly off the generator. Tried to start the saw and it stalls out the generator.
So I call the manufacture of the saw and they tell me that the electrical requirements that they advertise only apply to on grid (no mention of this anywhere in the owners manual). They tell me that they think there is a work around, but would not tell me what it is. They also let me know that I can't return the saw. Next I call the store I purchased it from and they to tell me I can't return the saw and they give me no help in how to set it up so that it will work.
So I am on my own. After many hours talking to folks and internet research, I find that maybe a soft starter or a VFD will be the solution. I see that Schneider electric sells many options. So I call Schneider electric and the square D tech line and am told that they think this product would work but were not able to help me choose which one to order (they did offer to help me if I have installation questions though.. ). Anyways, does anyone here have expertise with these products? If so, am I on the right path? If so, which of these products soft starter or VFD will work best with my application, and how do I choose which size of the product to purchase?
Thanks in advance,
Mike Burcusa
I am new to this board as I just moved into an off grid house about 3 months ago. I have a 24 V system with generator back up. My generator is a Perkins 10.5kw diesel generator (40A/leg). I just bought a new table saw. When I bought the saw I asked the salesperson about energy requirements and they said it need a 230V/20A circuit (but only used 13.8A at full load). So I wired that circuit in directly off the generator. Tried to start the saw and it stalls out the generator.
So I call the manufacture of the saw and they tell me that the electrical requirements that they advertise only apply to on grid (no mention of this anywhere in the owners manual). They tell me that they think there is a work around, but would not tell me what it is. They also let me know that I can't return the saw. Next I call the store I purchased it from and they to tell me I can't return the saw and they give me no help in how to set it up so that it will work.
So I am on my own. After many hours talking to folks and internet research, I find that maybe a soft starter or a VFD will be the solution. I see that Schneider electric sells many options. So I call Schneider electric and the square D tech line and am told that they think this product would work but were not able to help me choose which one to order (they did offer to help me if I have installation questions though.. ). Anyways, does anyone here have expertise with these products? If so, am I on the right path? If so, which of these products soft starter or VFD will work best with my application, and how do I choose which size of the product to purchase?
Thanks in advance,
Mike Burcusa
Comments
-
Welcome to the forum
The motor inrush can be as high as 10× the run current, this inrush will cause the generator to try match the demand but the diesel engine cannot react fast enough to support the inrush and start up current causing it to stall. So you are correct a soft start will reduce these currents, ramping up which in turn allows the generator to provide the demand graduaiiy. The generator should be able to support the load under normal run conditions once over the "hump", the soft start should be sized appropriately to the horse power of the motor, being rated above the motor name plate rated HP to lessen the demands on the electronic components, for example a 3hp motor should use a soft start with a 5hp rating for example, or with a current rating higher then the motor full load amp rating. Any offerings from reputable manufacturers, Schneider/Square D, Eaton, Siemens, Danfoss, Hitachi, ABB etcetera are good choices, VFD's tend to be more expensive and generally used on 3 phase equipment with more complex control options such as reverse and input capabilities, none of which are needed on a saw.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
On mobile site, so can't see if you have system details in a sig line, but any chance you could run the saw off battery/inverter and use the genny to recharge?
Battery/inverter can generally handle surges better than generators, and some inverters have a generator support feature in which they can augment generator with battery rather than simply passing generator current through.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
burcusa said:Anyways, does anyone here have expertise with these products? If so, am I on the right path?
If the saw does not spin use a smaller value resistor.
If the saw still trips the generator use a larger value resistor.
-
Hard to find a VF drive for single phase motors. Far better off with 3 phase motor but expect its a custom motor for the table saw. The odd part is you can feed a 3 phase VF drive with single phase (if the correct option is ordered.).
That starting resistor sounds intriguing and a lot cheaper.
-
I agree with trying a resistor. Maybe one like this. The load is much greater than 300W, but it's brief.
https://www.ebay.com/itm/1-ohm-300-Watts-High-Power-Ceramic-Tube-Resistor-300W
I am available for custom hardware/firmware development
-
Thanks everyone for the helpful comments. I am really interested in the resistor option. Will this work with the magnetic starter on the saw? Or will I need remove the starter and put a much simpler switch in?
Then just to be clear, do I write the resistor and closed push button in before the switch?
Thanks again!
Mike -
burcusa said:Thanks everyone for the helpful comments. I am really interested in the resistor option. Will this work with the magnetic starter on the saw? Or will I need remove the starter and put a much simpler switch in?
Then just to be clear, do I write the resistor and closed push button in before the switch?
Thanks again!
Mike
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed