Fridge compressor too big or inverter or batteries too small?
softdown
Solar Expert Posts: 3,899 ✭✭✭✭
A friend wanted solar for his recreational cabin. He bought a new 24 volt Cotek PSW 1500 inverter from me after I did a lot of work on his trailer.
Then he got busy:
1000 watts of Renogy panels
4 T105 Trojan 6 volt batteries
Big old fridge made in the 90's
Cotek 1500 pure sine wave inverter
Plus he tied to the grid since that only costs $8000. He wants his solar set up to be capable of running the fridge and lights.
The inverter doesn't have the oomph to power through the compressor surge of the big, old 90's fridge. I suggested that a newer Energy Star fridge should be fine with the 1500 watt inverter. He liked that idea much better than spending well over $1000 for a larger, higher quality inverter.
The batteries are brand new and have 2/0 inter connects so I would guess the cables to inverter are appropriately sized. However...I consider it possible that four T105s *may not* provide optimal oomph for a significant compressor surge. There are 225 Ah/battery. These are 62 pound batteries according to Amazon...not even GC2 sized. Bit surprised by the 225 Ah rating.
Seems that fridges may have significant start up surge. My lights sometimes dim a little bit for a fraction of a second when my fridge kicks on.
Also.....can this hurt the inverter? I think it may hurt the fridge compressor when there is inadequate power. I would guess that he got the old fridge for free though. It is a 90's fridge...at best. He seems comfortable with finding an Energy Star fridge.
Then he got busy:
1000 watts of Renogy panels
4 T105 Trojan 6 volt batteries
Big old fridge made in the 90's
Cotek 1500 pure sine wave inverter
Plus he tied to the grid since that only costs $8000. He wants his solar set up to be capable of running the fridge and lights.
The inverter doesn't have the oomph to power through the compressor surge of the big, old 90's fridge. I suggested that a newer Energy Star fridge should be fine with the 1500 watt inverter. He liked that idea much better than spending well over $1000 for a larger, higher quality inverter.
The batteries are brand new and have 2/0 inter connects so I would guess the cables to inverter are appropriately sized. However...I consider it possible that four T105s *may not* provide optimal oomph for a significant compressor surge. There are 225 Ah/battery. These are 62 pound batteries according to Amazon...not even GC2 sized. Bit surprised by the 225 Ah rating.
Seems that fridges may have significant start up surge. My lights sometimes dim a little bit for a fraction of a second when my fridge kicks on.
Also.....can this hurt the inverter? I think it may hurt the fridge compressor when there is inadequate power. I would guess that he got the old fridge for free though. It is a 90's fridge...at best. He seems comfortable with finding an Energy Star fridge.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
Tagged:
Comments
-
Fully charged GC's should be able to start a fridge. Even though there are only four of them, they can develop a high surge current for several seconds. I would suspect the fridge in this case. As for damage to the inverter I can't say. Mine is one of the old style units with a transformer and is bullet proof compared to cheaper solid state inverters that I've seen fail.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
-
Fully charged GC's should be able to start a fridge. Even though there are only four of them, they can develop a high surge current for several seconds. I would suspect the fridge in this case. As for damage to the inverter I can't say. Mine is one of the old style units with a transformer and is bullet proof compared to cheaper solid state inverters that I've seen fail.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
Anyone think a hard start kit might start the refrigerator. They use them on compressors when the compressor won,t start. I could not get my compressor to start and bought one and installed it. It has a capacitor to store up enough energy to give it a boost to start and runs normal. you can get them from ebay for about $15 or less.
-
solarvic said:Anyone think a hard start kit might start the refrigerator. They use them on compressors when the compressor won,t start. I could not get my compressor to start and bought one and installed it. It has a capacitor to store up enough energy to give it a boost to start and runs normal. you can get them from ebay for about $15 or less.
However...it is foolishness to use a fridge that is not close to being Energy Star rated. The wear and tear on the batteries alone would costs much more than a used Energy Star fridge.
Colorado has a lot of federal employees and quasi-execs. It is very easy to find very good, used fridges for less than $200 at ...say... Habitat stores.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Place a volt meter on the DC input to the AC inverter and see if you get a lot of sag when starting the fridge (or place an 800 Watt hair drier (or up to a 1,500 watt space heater) on your inverter and see what the voltage drop is.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:Place a volt meter on the DC input to the AC inverter and see if you get a lot of sag when starting the fridge (or place an 800 Watt hair drier (or up to a 1,500 watt space heater) on your inverter and see what the voltage drop is.
-Bill
I use an identical inverter for powering a large 14 cubic foot freezer. The fan turns on for a second when the freezer kicks on. No struggle at all...and the freezer is serviced by at least 125' of #12awg wire. Might be closer to 150'.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Long AC wiring from inverter to refrigerator/freezer load can actually be a help. The longer wiring+resistance reduces the high surge current. This is a version of "soft start".
Some folks have simply put a 100' (not heavy duty) extension cord on their refrigerators to fix "hard start" issues.
Obviously, too much resistance is not good either (motor will not start, more energy losses).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Using a long, thin gauge, AC extension cord, has been known to have enough resistance to aid (reduce) the starting surge, yet still pass enough power to properly run the compressor.
(long cord on the AC side, not the low voltage DC wire runs)
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
BB. said:Long AC wiring from inverter to refrigerator/freezer load can actually be a help. The longer wiring+resistance reduces the high surge current. This is a version of "soft start".
Some folks have simply put a 100' (not heavy duty) extension cord on their refrigerators to fix "hard start" issues.
Obviously, too much resistance is not good either (motor will not start, more energy losses).
-BillFirst Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed