Prostar MPPT Display Blank
nickdearing88
Registered Users Posts: 100 ✭✭✭
I went to check on my system this evening and noticed my CC's display was blank. The backlight comes on upon a key press, the SOC indicator lights are one, and the system appears to be functioning normally, but no characters on the display. Battery voltage was 25.9, Array voltage was 59.1. I can't imagine what happened.
The CC display was working normally when I was outside this morning.
I figure I'll disconnect/reconnect the solar and battery inputs to reboot and see what happens but wondered if anyone has ideas.
Edit: Is there a secret key sequence to reboot the controller without being able to see the menu items?
The CC display was working normally when I was outside this morning.
I figure I'll disconnect/reconnect the solar and battery inputs to reboot and see what happens but wondered if anyone has ideas.
Edit: Is there a secret key sequence to reboot the controller without being able to see the menu items?
Current system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter
Comments
-
If performing a manual reboot disconnect solar first then battery, reconnect battery first then solar, you probably know this but just a reminder.FWIW1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:If performing a manual reboot disconnect solar first then battery, reconnect battery first then solar, you probably know this but just a reminder.FWIW
The controller is also powering loads correctly, I tested my DC lights and small fan. Very strange.Current system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter -
Tech support is a good option, Morningstar generally is pretty good with assistance.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Joe from Morningstar emailed me back this afternoon and suggested I remove power from the controller and reboot. I did so and the display is now back to normal.
Now I don't have to worry about sending it in for a replacement....hopefully. The unit recorded no faults in the log from yesterday or today.Current system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter -
You might want to check if you have the latest Firmware on the Settings display screen.
v14 is currently available on the support site on the Software Tab here.
http://support.morningstarcorp.com/search/?searchterm=prostar+MPPT+Firmware
v10.0 fixed meter screen blank outs and contrast issue
Here is a link to the UMC-1 USB to Meterbus adapter which provides a PC connection to the PS-MPPT.
https://www.morningstarcorp.com/products/usb-meterbus-adapter/
This video shows how to update the firmware.
https://www.youtube.com/embed/luKLEnRjxkk
You may also want to adjust the display settings.
Also for future reference the "Reset Control" Command will reboot the controller.
From any of the Main Status Screens:
1X) Down arrow to Commands Menu
1X) Right arrow to Command Menu Select
5X) Down arrow Reset Control
2X) Right arrow to Reset and Confirm Reset
-MStar Applications EE -
MStar1 said:You might want to check if you have the latest Firmware on the Settings display screen.
v14 is currently available on the support site on the Software Tab here.
http://support.morningstarcorp.com/search/?searchterm=prostar+MPPT+Firmware
v10.0 fixed meter screen blank outs and contrast issue
Here is a link to the UMC-1 USB to Meterbus adapter which provides a PC connection to the PS-MPPT.
https://www.morningstarcorp.com/products/usb-meterbus-adapter/
This video shows how to update the firmware.
https://www.youtube.com/embed/luKLEnRjxkk
You may also want to adjust the display settings.
Also for future reference the "Reset Control" Command will reboot the controller.
From any of the Main Status Screens:
1X) Down arrow to Commands Menu
1X) Right arrow to Command Menu Select
5X) Down arrow Reset Control
2X) Right arrow to Reset and Confirm Reset
I would like to purchase the EMC-1 to gain the webserver ability, can it also be used to update the firmware? I hate to just by the USB adapter to only update the firmware. I can do all necessary configuration I require using the built-in meter/display.
Thanks for the command sequence to reboot without the display working; that's what I was looking for.Current system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter -
We are developing the ability to perform remote firmware updates with the Prostar and other products with the EMC-1. However, that feature is not yet available and I an not sure when it will be available.
The EMC-1 provides a LiveView HTML display which you can access on the LAN or the web with port forwarding. We should be posting the EMC-1 Firmware update on the website by the end of the year which will have the web service which requires only a password protected login rather than port forwarding.
-MStar Applications EE
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed