An "alternative coupling"?
MarkC
Solar Expert Posts: 212 ✭✭✭
Is it possible to "couple" (typically) grid tied and off-grid equipment at the DC PV panel connection(s)? Is there equipment that would allow simultaneous/parallel connectivity of both a typical off-grid charge controller AND an on-grid inverter to the same set of panels. This is not a theoretical musing as it is being done in the electric vehicle arena to provide V2G functionality - for bi-directional energy transfer to/from large EV batteries from solar and back to grid.
3850 watts - 14 - 275SW SolarWorld Panels, 4000 TL-US SMA Sunny Boy Grid tied inverter. 2760 Watts - 8 - 345XL Solar World Panels, 3000 TL-US SMA Sunny Boy GT inverter. 3000 watts SMA/SPS power. PV "switchable" to MidNite Classic 250ks based charging of Golf cart + spare battery array of 8 - 155 AH 12V Trojans with an APC SMT3000 - 48 volt DC=>120 Volt AC inverter for emergency off-grid. Also, "PriUPS" backup generator with APC SURT6000/SURT003 => 192 volt DC/240 volt split phase AC inverter.
Comments
-
Some (but perhaps not typical) controllers have ways to disable the MPPT tracking feature that may cause interference between controllers.
I am available for custom hardware/firmware development
-
It may be possible to run both a grid inverter and a CC in parallel at the same time but,
Many brands would not like it and you would have to test it.
The lower DC input might not share power with the higher DC input of the other. It could be erratic.
Equipment damage and certainly not approved by Fire and Homeowners insurance.
Why can't you switch it? One on, the other off?
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Dave Angelini said:It may be possible to run both a grid inverter and a CC in parallel at the same time but,
Many brands would not like it and you would have to test it.
The lower DC input might not share power with the higher DC input of the other. It could be erratic.
Equipment damage and certainly not approved by Fire and Homeowners insurance.
Why can't you switch it? One on, the other off?
3850 watts - 14 - 275SW SolarWorld Panels, 4000 TL-US SMA Sunny Boy Grid tied inverter. 2760 Watts - 8 - 345XL Solar World Panels, 3000 TL-US SMA Sunny Boy GT inverter. 3000 watts SMA/SPS power. PV "switchable" to MidNite Classic 250ks based charging of Golf cart + spare battery array of 8 - 155 AH 12V Trojans with an APC SMT3000 - 48 volt DC=>120 Volt AC inverter for emergency off-grid. Also, "PriUPS" backup generator with APC SURT6000/SURT003 => 192 volt DC/240 volt split phase AC inverter. -
You could connect the panels only to a grid-tie inverter and then run a 240VAC battery charger. If net metering rates aren't attractive, then switch on the charger only when the sun is shining.
I am available for custom hardware/firmware development
-
@MarkC Do you have grid available? I've been thinking along similar lines and think I have a solution, but it would need the grid, so without rambling on thought I would ask a simple question first.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:@MarkC Do you have grid available? I've been thinking along similar lines and think I have a solution, but it would need the grid, so without rambling on thought I would ask a simple question first.
Can you explain your solution?3850 watts - 14 - 275SW SolarWorld Panels, 4000 TL-US SMA Sunny Boy Grid tied inverter. 2760 Watts - 8 - 345XL Solar World Panels, 3000 TL-US SMA Sunny Boy GT inverter. 3000 watts SMA/SPS power. PV "switchable" to MidNite Classic 250ks based charging of Golf cart + spare battery array of 8 - 155 AH 12V Trojans with an APC SMT3000 - 48 volt DC=>120 Volt AC inverter for emergency off-grid. Also, "PriUPS" backup generator with APC SURT6000/SURT003 => 192 volt DC/240 volt split phase AC inverter. -
Somehow, you want the Classic to come up with a Vmp that is slightly lower than the one that the SMA finds. If you can do that, it will get priority.
Maybe by setting the MPPShdw.CycTms/Cycle time on the Sunny Boy to a value much higher than the Classic.I am available for custom hardware/firmware development
-
My idea is somewhat different to sharing the DC output from the panels which would more than likely cause conflict between the GT inverters and the CC. How about using using an inverter charger which has grid support, the grid/GT would charge the backup battery and pass through current charges the Leaf, when both are fully charged, the only load would be what is required for float on the backup battery. Since it would be taking from the grid, which you are feeding into, the net result would be what you are seeking, this however would mean a new piece of equipment, which perhaps is not what you had in mind. My situation is sort of the reverse of yours, I have the inverter charger and want to push excess production into the grid but it's not hybrid, so was thinking of ways to accomplish that.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:My idea is somewhat different to sharing the DC output from the panels which would more than likely cause conflict between the GT inverters and the CC. How about using using an inverter charger which has grid support, the grid/GT would charge the backup battery and pass through current charges the Leaf, when both are fully charged, the only load would be what is required for float on the backup battery. Since it would be taking from the grid, which you are feeding into, the net result would be what you are seeking, this however would mean a new piece of equipment, which perhaps is not what you had in mind. My situation is sort of the reverse of yours, I have the inverter charger and want to push excess production into the grid but it's not hybrid, so was thinking of ways to accomplish that.
http://midniteftp.com/forum/index.php?topic=2511.0
The author - Will is quite knowledgeable about communicating with the Midnite equipment - maybe something similar with your inverter/charger is available.
In my situation, the "PV coupling" is the first step in essentially bi-directional energy to/from the Leaf - and is one of the choices - but would seem to be a very efficient choice. Since I don't have a "hybrid" set up, I don't believe I can do what you are suggesting?3850 watts - 14 - 275SW SolarWorld Panels, 4000 TL-US SMA Sunny Boy Grid tied inverter. 2760 Watts - 8 - 345XL Solar World Panels, 3000 TL-US SMA Sunny Boy GT inverter. 3000 watts SMA/SPS power. PV "switchable" to MidNite Classic 250ks based charging of Golf cart + spare battery array of 8 - 155 AH 12V Trojans with an APC SMT3000 - 48 volt DC=>120 Volt AC inverter for emergency off-grid. Also, "PriUPS" backup generator with APC SURT6000/SURT003 => 192 volt DC/240 volt split phase AC inverter. -
jonr said:Somehow, you want the Classic to come up with a Vmp that is slightly lower than the one that the SMA finds. If you can do that, it will get priority.
Maybe by setting the MPPShdw.CycTms/Cycle time on the Sunny Boy to a value much higher than the Classic.
I do wonder about the basic electrical characteristics of the two pieces of equipment (potential variations in resistance that each equipment dynamically exhibit to the the PV panels under actual energy production - and will that be unstable or even destructive?). If either the CC or GT inverter could "backfeed" seems that could be problematic - or maybe useful, depending upon the functionality needed!3850 watts - 14 - 275SW SolarWorld Panels, 4000 TL-US SMA Sunny Boy Grid tied inverter. 2760 Watts - 8 - 345XL Solar World Panels, 3000 TL-US SMA Sunny Boy GT inverter. 3000 watts SMA/SPS power. PV "switchable" to MidNite Classic 250ks based charging of Golf cart + spare battery array of 8 - 155 AH 12V Trojans with an APC SMT3000 - 48 volt DC=>120 Volt AC inverter for emergency off-grid. Also, "PriUPS" backup generator with APC SURT6000/SURT003 => 192 volt DC/240 volt split phase AC inverter. -
The "destructive part" is where I would really think the whole idea needs to be thought out and is it really worth the risk?
I did an insurance claim for a system that had pictures taken during a pre-inspection of the house/garage. The after the fire pictures show quite a bit of extra solar equipment that was not really installed correctly. They did settle but I doubt these folks will ever have home insurance again. If you are doing the work as an owner builder you still need a permit if you have a claim.
If you hired someone,Qualified personnel havetraining, knowledge, and experience in:• Installing electrical equipment• Applying all applicable installation codes• Analyzing and reducing the hazards involved in performing electrical work
Pessimists usually have more data, unfortunately."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
MarkC said:Is it possible to "couple" (typically) grid tied and off-grid equipment at the DC PV panel connection(s)? Is there equipment that would allow simultaneous/parallel connectivity of both a typical off-grid charge controller AND an on-grid inverter to the same set of panels. This is not a theoretical musing as it is being done in the electric vehicle arena to provide V2G functionality - for bi-directional energy transfer to/from large EV batteries from solar and back to grid.
BTW that's not how V2G works.
-
Dave Angelini said:The "destructive part" is where I would really think the whole idea needs to be thought out and is it really worth the risk?
I agree, no it is not worth the risk unless the equipment manufacturers explain why (or why not) it can be done - or someone has come up with an innovative (and safe/tested) way to do it (however, seems that is how we have made much of our progress). What got me interested is that an innovative manufacturer is actually doing it (V2G) with their equipment - as described. But I don't have their equipment.3850 watts - 14 - 275SW SolarWorld Panels, 4000 TL-US SMA Sunny Boy Grid tied inverter. 2760 Watts - 8 - 345XL Solar World Panels, 3000 TL-US SMA Sunny Boy GT inverter. 3000 watts SMA/SPS power. PV "switchable" to MidNite Classic 250ks based charging of Golf cart + spare battery array of 8 - 155 AH 12V Trojans with an APC SMT3000 - 48 volt DC=>120 Volt AC inverter for emergency off-grid. Also, "PriUPS" backup generator with APC SURT6000/SURT003 => 192 volt DC/240 volt split phase AC inverter. -
When I can buy something like this from my supplier or the store here is "when". Most all quality electronics has an intended use statement in the beginning of a decent manual. Insurance companies are not happy when there is deviation.
I probably will lose my homeowners policy because of the ridiculous amount of money they want where I live. It is a gut check to self-insure but in many ways it is better as it forces you to address every issue. We go through this insured and not insured. The last time they used Google earth to check the slope of the mountain/hill. Now they don't even do that, they just look at a zip code. Even the Military USAA policy that I had will no longer insure this zip code.
Good Luck on whatever you decide!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
The Classic has many settings to change MPPT behavior.
Any PV->battery or PV->grid device that backfeeds anything towards the PV array doesn't make sense to me - does anyone know of such behavior?I am available for custom hardware/firmware development
-
Insurance companies are in the business of collecting and investing premiums. They are not in the business of paying claims beyond a level that induces people to keep paying premiums.
They know odds better than you or I do, and over a large enough sample, insurance is always a losing bet - no different than a casino.
It is a gut check to self insure, especially for risks that are potentially life altering. On the other hand, a lot of folks are functionally self insuring, but don't know it. My father died some months ago in a house I own. It had to be insured as a rental as it wasn't owner occupied, and rates were accordingly higher. After he died, it took some time to clear stuff out and get the place ready to be sold. I took the usual steps of shutting off water, collecting mail, etc while vacant. It sold recently, so I contacted the agent about the date to end coverage. Apparently there can be issues where a delay in transfer of title can leave the property still at vendors risk after closing, so on the lawyer's advice I asked about extending coverage for a week or two after close. The answer was that; they would not cover after close, because the property would be vacant until close, an extra fee would apply for the period to close, and the property was effectively uninsured from date of death to the date the extra fee was paid. They would not, however, rebate premiums for the uninsured period. I was functionally self-insured for ~6mos and didn't know it. In hindsight, I should have been truly self-insured (and not paying premiums) instead.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Condolences about your father. Insurance has so much unintelligible fine print that I'm surprised that they ever have to pay a claim.
I am available for custom hardware/firmware development
-
They have to pay some claims, or nobody would pay premiums.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Insurance is just like any other contract, you have to read it all or have your attorney read it and advise you of the terms before you sign up.
-
Estragon said:Insurance companies are in the business of collecting and investing premiums. They are not in the business of paying claims beyond a level that induces people to keep paying premiums.
They know odds better than you or I do, and over a large enough sample, insurance is always a losing bet - no different than a casino.
They insured us until they just decided not to. We went 3 years without and then got a decent offer. The houses they do insure have none of what many of my offgrid clients do. It is a stupid business model and has been going on for a very long time."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
I can relate to that. They threatened to discontinue coverage a few years ago on the house because a porch door didn't close properly! The main door to the house was fine, so it's not like the place was insecure.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Yes that is unreasonable. Another one for you, on the other side of my hill there is a house without any of the safety gear, no one is living there, and they pay almost nothing for insurance because it is a vacation home on their main policy. Tall dead grass growing right up to the porch."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Bah! I guess it's easier to have someone drive around in a city finding a porch door open a crack than to find an obvious total loss waiting to happen in a more remote area.
Maybe the underwriter has a brush clearing clause buried deep in the legalese.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Not to derail the thread but one more....
I could not insure my home when I first purchased. Reason: the railings on either side of my back steps were made of different materials - one white vinyl and the other unpainted wood. I painted the wood railing white and called them back to take pictures, then the policy started.
Crazy.Current system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter -
It's all about the demographic and the odds. When I was a young man, I paid a huge amount for auto insurance, I now have 5 cars worth more than my house was at the time and I pay a lot less. Go figure.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed