charging battery bank with generator
i am in the middle of installing my new solar system and i have a 48v 600 ah agm battery bank and a aims 12000 w inverter charger this is an off grid system i also have a 8750 w predator generator that i would like to hook to the inverter the manual for the inverter says i need a 150% higher capacity gen than my inverter that would be 18000 w gen so my question is i guess will my 8750 gen harm the inverter or just take longer to charge don't want to destroy my new inverter any input would be greatly appreciated thanks in advance
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
Comments
You have pretty big inverter for the size of both generator and battery bank.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
The issue with the inverter is you can pull a lot of current. 12000w at 48v is 250a, potentially more in a surge like motor start. Deep cycle batteries are usually rated at a discharge rate of about C/20, or about 30a in your case. Pulling nearly 10x that, apparent capacity will be reduced considerably. Of course, just because you can pull that kind of current doesn't mean you will, but something to be aware of. I have a lot of inverter for my bank too, but that's mainly to support surges, and for redundancy in case an inverter fails. I keep a close eye on loads.
Off-grid, sometimes it's better to flip a breaker than having guests all running blow dryers and whatever all day, and then find you have to run the generator half the night.
Another thing to keep in mind is with 3 parallel strings of batteries it's important to keep strings balanced so they charge and discharge evenly. Heavy interconnect cable and proper wiring is important. AGMs have advantages, but can be tricky to manage because of the difficulty in measuring state of charge.
It sometimes takes some time to get things working properly in a new system. The key is to monitor closely and ask questions if something doesn't seem right.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
The wiring in them can't handle constant running at full power.
Battery chargers are a constant unforgiving loads to power.
You would need something like my 17.5kw generac, which is like a $3,600 machine, but it powers anything, air compressors, welders, plasma cutter, all the loads other generators fear are no problem for my generac.
Or get a smaller stand alone battery charger that doesn't use more than about 5 or 6kw.
Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
So if you have a 8750 genset, it's what 7Kw cont ? I'd set the charger to only pull 5Kw from the genset, which at 58V charging, would be about 60A DC, when allowing for some reasonable losses and PF.
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
PERFECT FOR HOMES OVER 3500 SQ FT
This Kit Includes the Following Parts:
PICOGLF12KW48V240VS - 12000 watt pure sine inverter charger 120/240vac
PV240POLY - qty 12 - 250 watt solar panel
PV6X240RACK - qty 2 - 6 panel Ground Mount Solar Rack
PICGLFBATS - qty 1 - Battery Temp Sensor
SCC60MPPT - 60 amp MPPT solar charge controller
6FM200H - qty 12- 200 ah deep cycle battery
PVF100FT10AWG - 100 foot PV wire for solar panel (female)
PVM100FT10AWG - 100 foot PV wire for solar panel (male)
PVMC4.A-2F1M - qty 2 - MC4 Branch 2F to M
PVMC4.A-2M1F - qty 2 - MC4 Branch 2M to F
PVEXT15FT10AWG - qty 6 - 15ft PV extension wire
CBL08FT6AWGC- 8 ft 6WG cable to connect SCC to battery bank
CBL08FT1/0 - 8 ft 1/0 AWG cable set (inverter cable)
CBL02FT1/0 - qty 2 - 2 ft 1/0 cable (battery cables)
CBL01FT1/0RED - qty 11 - 1 ft jumper for fuse kit and battery jumpers
ANL300KIT - 300 amp inline fuse kit
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
Just seems to me at least, that the system purchased couldn't power much other than the inverter. Was this intended as a standby system, rather than an off grid system? the reason asked is because it is in the off grid section.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
You might want to consider a smaller inverter to handle small loads, and just use the big one for big loads. Knowing more about your loads would help..
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
1/0 can take 150 amps max at 70°C. I hope that it's only a typo.
A+
Erik
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
http://www.smartgauge.co.uk/batt_con.html
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery
Realistically, in my opinion, they should have promoted the kit as a 3Kw off grid system, but that doesn't sound quite as impressive, or at least a 12 Kw ( with 18Kw generator support ) Note how all of the kits they sell, from 2-12Kw, have the same array/ controller, just a larger inverter, a 3Kw 48v inverter from Cotek for example, I have the manual in front of me, uses 40w in no load and 9w in power save mode, as apposed to 200 & 40 for the Aims 12 000w.
The large inverter is a killer, it's self consumption is too high unless you use that much energy, and if you do, the ballance of system is too small to support it, without a generator. Truth in advertising comes to mind.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
However your clamp on ammeter (current in parallel batteries) and volt meter (series balance) shows is most balanced. Start with the recommended layouts and adjust as needed.
I am available for custom hardware/firmware development
To conserve pressure tank capacity, I supply toilets and other water uses not needing much pressure directly from gravity tank. The pressure tanks (2x30gal) easily supply overnight needs for me, so that pump stays off and I can use a really small inverter at night. You'd need a big enough inverter for reefers though, probably in the range of 1500w with decent surge capability.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
- 12000 watt pure sine inverter charger 120/240vac
- 12 - 250 watt solar panel
- 2 - 6 panel Ground Mount Solar Rack - 60 amp MPPT solar charge controller
- 12- 200 ah deep cycle battery