Can failed wind turbine load bank damage solar controllers
EFX4N6
Registered Users Posts: 1 ✭
Am investigating failure of large solar/wind off grid system. Found that cooling fans on load bank failed and overheated bank. Also found arc tracking type damage to electronics on solar controllers, consistent with lightning surge. Could this be caused by a failure of the wind turbine load bank?
Comments
-
It has been a decade or two since I did printed circuit board design... But, if I recall correctly, very roughly, the flash over voltage is roughly 50 volts per 0.001 inch across a clean circuit board and around 500 volts per 0.001" through the board (no voids).
Otherwise, carbon tracks can form from dirt/salt/etc. on the surface of the board. Inside the board (and possibly on the surface) copper whiskers can grow and cause shorts.
How high of voltage did your battery bank voltage go? Very roughly, it is possible for a wind turbine to output several times its rated load voltage if driven at rated RPM... For example, in the olden days, one could buy a kit that would allow a car alternator to output around 120 VDC on a 12 volt alternator.
For a DC battery bank--Say 48 volts--A "working" bank can run as high as 62 VDC or so and Xantrex/Schneider has an error log entry if the battery bank exceeds 72 VDC (has happened on at least one member's system here).
My guess, for a 48 VDC battery bank, if you see over 72 VDC for any length of time--That is an "out of control" charging event and runs the risk of battery bank and connected electronics/devices damage.
To get arc tracks on a clean board, I would suspect that your system would have to see 5x or more on a (well design) 48 VDC system (charge controller).
Battery banks seem to be relatively rugged against surge current from lightning. The lead acid battery has both (relatively large) capacitance (between + and - connections). And a typical design would have the Negative Terminal tied to earth ground (metal water pipe in ground, ground rods, ground plates). Plus, lead acid batteries will take "excess voltage and current" and gas (hydrogen and oxygen generation)--So lead acid batteries do have a method to "manage" excess energy to a degree (other battery chemistries like many Lithium Ion types do not).
Our retired forum founder has said, from his experience, that lightning strikes were far more likely to take out the AC output of an AC inverter than the DC input.
I would suspect that the carbon tracks are more likely from dirt/dust/humidity accumulation (always the issue between forced air cooling with little dust control vs the more expensive sealed unit design) or the possible "real bug" that got in the controller and shorted out some leads with their body?????
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
@BB said, I would suspect that the carbon tracks are more likely from dirt/dust/humidity accumulation (always the issue between forced air cooling with little dust control vs the more expensive sealed unit design) or the possible "real bug" that got in the controller and shorted out some leads with their body?????
This is the result of a small gecko which crawled into my inverter and got cremated.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
EFX4N6 said:Am investigating failure of large solar/wind off grid system. Found that cooling fans on load bank failed and overheated bank. Also found arc tracking type damage to electronics on solar controllers, consistent with lightning surge. Could this be caused by a failure of the wind turbine load bank?
With a proper turbine being up high, it's a lightning magnet, and that would make everything fail.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
The problem with a good wind turbine is its also a good lightning rod.
If it looks like lightning damage it probably is?Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 885 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 606 Discussion Forums/Café
- 300 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed