four 6v batteries, 2 CCs, 12v and 24v loads simultaneously
Aeronb
Registered Users Posts: 8 ✭✭
We are looking into setting up a charging station at our R/C airplane club's flying field. Some members have 12v chargers and others have 24v chargers. Will it work? If we had two CCs with each set to charge a pair of batteries, then have the batteries all series together for 24v. I would put two sets of leads out from each pair of batteries so that we would have access to 12v from each. I hope this would help even the discharge from each half of the battery bank. I would never parallel these leads.
Will each of the CCs work independently on their respective battery bank and bring it to a full charge? At some point, due to uneven usage, one half of the bank might be at say; 75% SOC, and the other half could end up at say; 90%. Maybe then someone comes along and puts on a 24v load and brings them down another 5% each. All along the CCs are doing their job to get the batteries back up to full charge. At some point when loading is light one pair comes up to full and some time later the other one does too.
I can't find a reason why this shouldn't work. But I have a feeling that I'm missing something. Any comments and insights are greatly appreciated.
Regards,
Aeron
Will each of the CCs work independently on their respective battery bank and bring it to a full charge? At some point, due to uneven usage, one half of the bank might be at say; 75% SOC, and the other half could end up at say; 90%. Maybe then someone comes along and puts on a 24v load and brings them down another 5% each. All along the CCs are doing their job to get the batteries back up to full charge. At some point when loading is light one pair comes up to full and some time later the other one does too.
I can't find a reason why this shouldn't work. But I have a feeling that I'm missing something. Any comments and insights are greatly appreciated.
Regards,
Aeron
Comments
-
If you have a string of batteries totaling 24V, and you pull power of some in the middle, you are unevenly discharging some of the batteries. A 24V controller will NOT be able to sense this, and some of the batteries will fail prematurely.
Solution,
Best
2 battery banks, 1 at 12V and other at 24V, with 2 chargers
Next best
Split the charging, using 2 ISOLATED chargers, each charging 12V of the bank. You will find out quickly what chargers are NOT isolated, because there will be sparks and smoke
Next best
split the bank apart and charge one 12v section one day, move the charger to the other 12v section next day, and then reconnect to a 24V bank, Lots of connecting and moving around
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mike95490 said:If you have a string of batteries totaling 24V, and you pull power of some in the middle, you are unevenly discharging some of the batteries. A 24V controller will NOT be able to sense this, and some of the batteries will fail prematurely.
Solution,
Best
2 battery banks, 1 at 12V and other at 24V, with 2 chargers
Next best
Split the charging, using 2 ISOLATED chargers, each charging 12V of the bank. You will find out quickly what chargers are NOT isolated, because there will be sparks and smoke
Next best
split the bank apart and charge one 12v section one day, move the charger to the other 12v section next day, and then reconnect to a 24V bank, Lots of connecting and moving around
Thanks for your help. -
There are charge controllers which charge 12 or 24 volt which have a 12 volt power port which you can tap 12volt out of. I'm not sure how well they work or what kind of loads they can supply.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
mike95490 said:If you have a string of batteries totaling 24V, and you pull power of some in the middle, you are unevenly discharging some of the batteries. A 24V controller will NOT be able to sense this, and some of the batteries will fail prematurely.
Solution,
Best
2 battery banks, 1 at 12V and other at 24V, with 2 chargers
Next best
Split the charging, using 2 ISOLATED chargers, each charging 12V of the bank. You will find out quickly what chargers are NOT isolated, because there will be sparks and smoke
Next best
split the bank apart and charge one 12v section one day, move the charger to the other 12v section next day, and then reconnect to a 24V bank, Lots of connecting and moving around
Thanks for your help.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed