Using a T-fuse without the fuse block?

I read that you should locate inverter fuses close to the battery.
For my small off grid system, (more like an emergency backup), I was looking at the T-fuse for the inverter and is there any reason I can't mount one end directly to the battery post of my Vmax SLA battery without using the fuse block? As big as the T-fuse is, it fits quite nicely using a few washers to lift it up a bit to clear the battery case. From there I just need a short cable run to my battery disconnect switch, then on to the inverter. (I could actually attach the other end of the T-fuse directly to the switch without a cable. I only need to widen the fuse hole a bit.)
So since it's not a flooded lead acid battery, what is the downside of doing this since there are no corrosive/explosive fumes to deal with? (Yeah, I know, SLA's are not fully sealed, but they will not be in an enclosed container.)
Comments
With batteries commonly used in off grid systems, the energy levels are nothing short of fearsome. Heck the typical 2v, 1200ah that I deal with, can go to 9,000 amps on a dead short. No, I'm not exaggerating! Watching the short circuit tests is pretty awesome actually.
Did I mention that I really like fuses?
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
http//www.samlexamerica.com/products/ProductDetail.aspx?pid=8
mounts directly on the positive battery post, and the cable connects to the other post on the fuse holder. Any reason not to do this?
Steve
Back to OP:
As for me....I bought a bunch of fuse blocks and a whole lot more fuses. Of course the fuse blocks are nice to have. Having fused power lines put one ahead of many, many solar installs....whether a fuse block is used or not.
This isn't a car that is going to vibrate over 100,000 miles of road. Whether one needs to take a number of large safety precautions may depend on whether children and guests have access to the battery bank.
https://www.amazon.com/Samlex-Solar-DC-FA-300-Fuse-Assembly/dp/B005ELATP6
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
Unlikely disturbing would increase the rating, but rather decrease it. Use copper washers (harbor freight has a good cheap kit of many sizes) and SS bolt with lube ( I like the McMaster Carr copper flake conductive lube ) should give you a good connection, Steel or SS is not very conductive and will heat up under large loads.
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
You know, I saw those terminal block fuses but since I kept seeing everyone using T-fuses for inverters I thought I should go with those.
What I didn't like is having to buy/use those T-fuse holder blocks which take up a lot of space and need an extra cable run.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P