is there anyone who can help me with my batteries
felix
felix Registered Users Posts: 12 ✭✭
setup for the kid 6 pcs. 24 v
absord V
float V
with more
  • Photowhit
    So you will have 3 strings of 2 batteries.
    Since you have a 24 volt system, you can double the charging voltage they give you (of 14.4 - 14.7 volts) to 28.8 - 29.4 volts and float (of 13.6 - 13.8 volts) to 27.2 - 28.6.
    With a single kid you don't need to worry about the max input amperage of 25 amps, since you have 3 strings and could take as much as 75 amps.
    I hope you purchased these as a back up or UPS, as they appear to be designed for float use rather than daily cycling, though I may be reading that incorrectly since they take such a high charge rate. My old and feeble mind...
  • felix
    edited July 2016 #3
    if I buy two batteries more , what is the best way to connect them
  • vtmaps
    Don't do it.  You already have three strings.  Four strings is too many (actually, three strings is too many IMO).  --vtMaps
    While I agree with vtMaps that is a lot of batteries in parallel--Assuming you have to do this, then here is a description of how to parallel batteries:
    http://smartgauge.co.uk/batt_con.html
    What is not talked about in that link is, depending on the size of battery and diameter of the copper wire, you should probably have a fuse/breaker per parallel string of batteries (4 parallel strings, 4 breakers or fuses). It is possible for a shorted string to be fed power by the other 3 strings and overheat the batteries/wiring.
  • felix
    why is that too many
  • jonr
    edited July 2016 #7
    > What is not talked about in that link ...
    Also not talked about is the fact that batteries vary in internal resistance.  So their claims of "perfect balancing" are bogus (although with measurements and uneven cable lengths, one could get closer).  Method 3 is draw incorrectly in terms of cable lengths.  Drawings of 4 in parallel and reference to 8 is misleading.
    Common battery to battery variations can be the equivalent of 6+ feet of cable length.  Someone should create a reference page done right.
  • felix
    edited July 2016 #8
  • jonr
    If you put some load on your bank and use an ammeter to test each red link, what values do you get?
  • felix
    I'll try tomorrow is not home