minisplit heat pump
I'm a little unclear about how much wattage a minisplit heat pump uses when the compressor is in heating or cooling mode.
I realize that it depends on the model - but do they use 400 - 500 watts, more or less when the compressor is running?
Also, if it has an inverter, does that mean that the DC fan can run at a slow or variable speed on the indoor unit, even when the compressor is not running? If so, what is the purpose of running a fan if the compressor is not on?
We've had a heat pump water heater in our off-grid cabin for a few years and it works fine.
We are now considering adding a 1 ton minisplit heat pump/ac unit. We have a 3,725 watt array, with 10kwh AGM battery bank (usable capacity at 50%) and a Trace SW4024 inverter with a 220 volt transformer and are located in the Ouachita Mountains of western Arkansas.
Any help out there?
Comments
-
Wattage at minimum draw will vary with the unit. I think the lowest I've read is around 330 watts. I live a bit north of you, in central Missouri, and our heat comes with sun. I can just set me window air to come on around 2 and the system will be in float so I won't draw down the system at all, once cooled off, even with my poorly insulated Tin can, the duty cycle is rarely above 50% even on the warmest nights, I just have it set to turn off around 2 am and I'm fine until morning. a similar cycling should work for you, cooling down at high and turning it to lower settings when the sun sets.
Starting multiple threads just make things ugly, hard to follow. I think the Mini split threads are in the Energy Use so I replied here. I would suggest removing the other threads.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Can you measure your load with a Kill-a-Watt or similar meter?
The inverter based mini-split heat pumps are usually pretty off grid system friendly.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thank you.
I'm new to this and didn't intentionally create additional threads, so if there is an administrator who wants to remove a thread or two, that's fine with me. Sorry.
I do have a Kill-a-Watt meter, but it is a 120 volt model and built to plug in to a receptacle, so it may be hard to measure the 220 voltage voltage load.
What I'm still a little unclear of is: In general, how many watts does a 220 volt, 1 ton minisplit draw in the A/C mode when both the outside and inside units are running at max load? And, how many watts does the same minisplit draw when the just variable speed inverter is running the fan? Also, what good is the heat pump when only the fan is running?
As you can tell, I'm still struggling with the basics regarding a minisplit heat pump.
We are currently using a 120 volt 5000 btu GE brand window A/C unit in the summer and have it on a 15 amp plug-in timer.
Overall, it works pretty well but I'd like to study the specs to see if a minisplit in heat pump would cut my propane use during the heating season. We recently increased the battery bank and array size and are hoping that the excess capacity will help run a minisplit in the winter.
-
The FLA rating in the specs for the heat pump you are considering will tell you max amp draw for that system.
-
I have already deleted the duplicate threads (not a problem).
As for measuring larger loads, you can get whole house meters (and some have multiple branch circuit taps) for reasonable amounts of money:
http://theenergydetective.com/
Or you can get clamp current meters--Which help, but do have their own limitations (you cannot measure total energy use, "surge hold" meters are more expensive, etc.).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Checkout this website for examples of various SEER and size models with the specs you're looking for.
http://www.thermospace.com/ductless_split/mini_ductless_split.php
They have 120v and 240v models. All the specs are given for any model selected. These include watts, amps, at high, medium and low speeds. It may be possible that since the 5000 BTU window shaker has been cooling well you might want to consider a 9000 BTU unit.
Most of the units have 3 fan speeds. My opinion is, running the fan without cooling or heating would just be for air circulation.
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
Raj174 said:Checkout this website for examples of various SEER and size models with the specs you're looking for.
However the specs also indicate that it has a LRA (locked rotor amps) of 33 amps and a "compressor RLA" of 4.59 amps.
I don't know what "RLA" is... maybe a typo? Also, I'm not sure from the specs whether that 33 amps is the startup surge that would be seen by your AC source.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
RLA is run load amps. Might ask them about the LRA spec. The site has a chat tab. Maybe the inverter absorbs the surge as it ramps up rpm on the compressor.
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
Thanks for the information. Is my understanding of this correct: The variable speed compressor on the outdoor unit can run at different speeds eliminating frequent startup surges and as a result, consumes less power overall?
-
LRA means "Locked Rotor Amps". (Pretty much the highest possible amperage draw ever)
-
Do yourself a favor and only purchase major manufacturer mini splits. Mitsubishi, Fujitsu,Panasonic, Daikin, Carrier etc.. Parts will be available if you ever need them. Even they discontinue parts after 10-15 yrs.
The off the wall brands not so, they have a poor parts network if any at all.
LRA is locked rotor amps that you will only ever see if the compressor rotor seizes and can no longer spin. This would require a replacement compressor. -
I have just installed and finally operating the fujitsu 9rls3, with an SEER rating of 33. The air conditioning unit runs between 300-500 W but the heat pump can surge to almost 2000W under special demand conditions, although nominally, it also uses about.600 W. With some planning and keeping it in setting for power saving, the use stays below a 1000w on automatic mode.
Sunpower 3 x 435 watt panels, 48 v 215 AH battery bank (Sam's club), Midnite Kid and WBjr, Fujitsu 9RLS3 split duct AC, Outback FX 3048T + transformer 2000W 120/220V, GrapeSolar Fridge.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed