Charging problem with xw6048

Hi Everyone,
I have a problem with one of the new xantrex xw 6048 hybrid inverter /charger.
The problem is the XW inverter /charger AC 1 Led is not glowing and charging the batteries when the grid supply is available( it is functioning with battery in inverter mode
I don’t know why?
Attachment not found.
It’s charging the battery only when the voltage is higher than 205 or else it’s functioning with batteries in inverting mode.
Please help me to sortout this issue ASAP
I have a problem with one of the new xantrex xw 6048 hybrid inverter /charger.
The problem is the XW inverter /charger AC 1 Led is not glowing and charging the batteries when the grid supply is available( it is functioning with battery in inverter mode
I don’t know why?
- When The grid voltage is below 205 Vac.(please find the attached image) it’s functioning in inverter mode- AC1 Led is off , Inverter Led is on and charging is off. In the specification it is mentioned the AC range (165-280vac)
Attachment not found.
- When the grid voltage is above 205 Vac it’s charging the battery-AC1 Led is on ,charging led is on and inverting led is off.
It’s charging the battery only when the voltage is higher than 205 or else it’s functioning with batteries in inverting mode.
Please help me to sortout this issue ASAP
Comments
htps://offgridsolar1.com/
E-mail [email protected]
Many inverters simply pass the AC voltage through to the loads when all is well... For US, roughly from 210 to 264 VAC is "good voltage" for a 240 VAC circuit.
We also have 208 VAC circuits (one leg of a 3 phase power system), so the low voltage would be around 182 VAC... It is possible the inverter is trying to "protect your loads" (and itself/house wiring) because it thinks there is a "brownout" going on.
If you can change the acceptable AC input voltage range to a lower nominal value, that may change its behaviour.
-Bill
-Bill
htps://offgridsolar1.com/
E-mail [email protected]
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Set table range is 156 - 230 for low and 250 - 280 for high range
AC2 default is 160 low, 276 high. Same settable range.
Frequency default is 55 hz low and 65 hz high. Settable low is 44-59 hz. Settable Hi is 61-70.
What is feeding AC2? That is normally used for Generator/Hydro etc.
My grid is normally around 245 VAC
True AC1 is tighter but he is plugged into AC2 in his picture and he never came back with any reasonable answers. I am guessing he does not have an SCP or combox and so he is busy trying to find one.
htps://offgridsolar1.com/
E-mail [email protected]
Still really wondering what source was giving that low of voltage and what the frequency was? Can't see which source is ON in the shot with the meter. All of the others are Gen or AC2. Also needs to check L-N-L voltages. If I remember correctly need L1-N for voltage sense? For North American Inverter.
Just have to wait for him to come back with some information.
The problem is been fixed using the XW SCP T