Auto Transformer question?
verdigo
Solar Expert Posts: 428 ✭✭
Looking at split leg balancing are all these units the same as long as they are 240v to 120v at 60hz? Lots of these units on ebay but the descriptions don't specifically state they can be used for leg balancing. This is such a unit http://www.ebay.com/itm/Auto-transformer-4kVa-120-vac-lv-240-vac-hv-express-/390603719078?pt=BI_Circuit_Breakers_Transformers&hash=item5af1cbc1a6
Dennis
Dennis
Re: Auto Transformer question?
Never mind. Just got schooled by wiki. Just looking for a cheaper version of the PSX-240. -
Re: Auto Transformer question?Looking at split leg balancing are all these units the same as long as they are 240v to 120v at 60hz? Lots of these units on ebay but the descriptions don't specifically state they can be used for leg balancing. This is such a unit http://www.ebay.com/itm/Auto-transformer-4kVa-120-vac-lv-240-vac-hv-express-/390603719078?pt=BI_Circuit_Breakers_Transformers&hash=item5af1cbc1a6
Dennis
Would be good for a 50Hz system, might run OK for 60HzPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Only $90 plus $125 shipping. OK.SMA SB 3000, old BP panels. -
If it's a 50 Hz transformer it should work fine on 60 Hz.
However a 60 Hz transformer would probably not work well on 50Hz, it would tend to draw excess power and overheat due to insufficient impedance for 50 Hz operation at it's rated voltage. -
Found a PSX-240 for $400.00, and free shipping so I just bought it. -
I looked at that one, but decided to go ahead and spend the extra money for the PSX-240 when they had the earth day sale and it works great for running the 220 VAC heat pump. Thanks NAWS!!!12K asst panels charging through Midnite Classic 150's, powering Exeltechs and Outback VFX-3648 inverter at 12 and 48 volts. 2080 AH @ 48 VDC of Panasonic Stationary batteries (2 strings of 1040 AH each) purchased for slightly over scrap, installed August 2013. Outback PSX-240X for 220 volt duties. No genny usage since 2014. -
Got my PSX-240 from the UPS guy today. This thing is a lot bigger than in the pictures. -
Re: Auto Transformer question?Got my PSX-240 from the UPS guy today. This thing is a lot bigger than in the pictures.
They're a lot heavier than it shows in the pictures too. LOL!
For split-phase leg balancing simply wire the neutral to the neutral bus in it, and run L1 from your service panel or inverter to one side of the breaker and L2 to the other side of the breaker. And, of course, ground it. It's that simple. If you wire it on the inverter output, or the inverter's distribution panel like I have mine, it will leg balance your generator too.
Chris -
If I am in need of an auto transformer to get 240 volt output from my 120 volt Inverter, and don't want to spend $300 to $500 on an Outback or Xantrex/Trace unit, what criteria should I be looking at? For example, what should I search for on eBay or what specifications are critical if I look on surplus electronics sites? Thanks!!
Jim in Western Wisconsin -
What load is planned for it WisJom? And what do you have for an inverter?If I am in need of an auto transformer to get 240 volt output from my 120 volt Inverter, and don't want to spend $300 to $500 on an Outback or Xantrex/Trace unit, what criteria should I be looking at? For example, what should I search for on eBay or what specifications are critical if I look on surplus electronics sites? Thanks!!
That info will help. -
I have a Trace SW4024, and the load would be under 4kw, probably under 3kw. If it made a big difference in cost, it would be relatively easy to limit the load to under 2kw.
Thanks! -
Don't forget that the windings of the autotransformer only need to be sized to handle the power of the 240 volt load itself. Any additional 120V load you add connected directly to the inverter output does not put any load at all on the autotransformer. And the thermal mass of the transformer is large enough that, except for voltage drop considerations, you do not really have to worry about sizing it for surge current, even on the 240V load.waynefromnscanada wrote: »What load is planned for it WisJom? And what do you have for an inverter?
If you are also using it for leg balancing of a 240V generator, or to provide for 120 volt loads on the synthetic phase, then you have a more complicated calculation to do.SMA SB 3000, old BP panels. -
Re: Auto Transformer question?If I am in need of an auto transformer to get 240 volt output from my 120 volt Inverter, and don't want to spend $300 to $500 on an Outback or Xantrex/Trace unit, what criteria should I be looking at? For example, what should I search for on eBay or what specifications are critical if I look on surplus electronics sites? Thanks!!
The thing with autotransformers is that they're not all created equal. The chances of the cheap ones being wound correctly so the synthetic leg is perfectly 180° out of phase with the input leg is not good, and that can cause problems with 240V stuff, and even with stepping down a 240V generator to 120V for input to a 120V inverter.
Outback offers the same transformer that's inside the PSX-240 as just the bare transformer (designed to mount in their conduit box). You have to supply your own box for it. It's called the FW-X240 and it's quite a bit cheaper than the PSX-240
http://www.solar-electric.com/x-240.html
Buy an Outback one and you know what you're getting, and that it won't damage your stuff.
Chris -
cheaper, No Kidding! $200 just or the box and some wire etc...
Re: Auto Transformer question?westbranch wrote: »cheaper, No Kidding! $200 just or the box and some wire etc...
You also get a cooling fan, a temp sensor I presume and a circuit to regulate it and circuit breakers. -
You can also look for isolation transformer. The most flexible is one that has two primary and two secondary windings so you have the options of 120v to 240v either way with or without isolation or autotransformer connection.
One important difference between an autotransformer and isolation transformer is an isolation transformer wired as a autotransformer can deliver twice the VA rating. I have some 2 KVA rated Thordarson 23V615. Wired as autotransformer they can run 4 KVA.
OutBack FWX-240, 3 kVA 120/240 Auto Transformer weighs about 25 lbs.
Xantrex T240 Autotransformer 4kVA Auto transformer weighs 39 lbs - 7 to 9 lbs of the metal cabinet.
Thordarson 23V615 2kVA isolation transformer weighs 52.5 lbs.
Generally, more 'iron' (weight) is better. It depends on losses across load range. Again generally, lower lbs./VA means more losses at either lower load or higher load end of VA range. (Outback sells an X-fan option kit) A low weight per kVA is usually wound with fewer turns per volt (to prevent core saturation) resulting in poorer power factor and more losses at low end loads. Leakage inductance is also a factor, generally worse on low weight per kVA. Allowing higher leakage inductance allows higher KVA loading without saturating an undersized core, with down side of more losses and more voltage fluxuations versus load level.
Another thing, being it either isolation or autotransformer, they almost always wind their secondaries with about 1.02 to 1.05 times their primary winding turns per volt ratio. This is to make up some of the losses through the transformer, preventing lower then target voltage on secondary. This has ramifications if you are using them to balance 120 v loads with an autotransformer. -
Man I really hate to bump such an old thread ... Here goes don't smack me!
My next project is going to take my Pool Pump Offgrid. I have a nice Pentair Intelliflo VS - I can set the RPMS, priming speed/length etc. Its pretty cool. Well now
I am going to take two 327w panels in series to a midnight classic 150 to a bank of 12v 540 ahrs to a xantrex pure sine 1800 to a step up transformer. Nothing else will be on this circuit.
I guess I am going to go for the Outback PSX-240 Auto transformer 120/240VAC big price tag
I've seen some step up transformers on ebay in the $60-150 range that Im afraid to try but looks like they will work. I dont want to gamble my expensive pool pump.
Anyone else have any experience lately with this? Am I going about it all wrong? I dont want to spend on a inverter that does 240 60hz or buy stackables - im broke after installing my last system. -
Re: Auto Transformer question?I am going to take two 327w panels in series to a midnight classic 150 to a bank of 12v 540 ahrs to a xantrex pure sine 1800 to a step up transformer. Nothing else will be on this circuit.
Rethink. How about putting those batteries in a 24 volt configuration? You can use thinner cables and have fewer parallel batteries (more stable).
Your classic will be more efficient down converting the Vmp to 24 volts than to 12 volts, and if you haven't bought it yet, you could get by with a smaller (cheaper) controller such as the Midnite Kid.
Look at the Victron Phoenix inverters... some of them make 230 volt AC at 60 hz. They are efficient and have very low tare losses. You would not need the autotransformer which also consumes a few watts.
The other option is to just find a DC motor in the right voltage and HP range and add a direct DC drive pump system run off the solar in parallel to the Inteliflo. I am doing some research on this now. This would eliminate the need for a battery setup but may require a voltage booster.
One reason is the utility is making it impossible to get a new interconnect agreement with the same terms as my old agreement.
BTW here is a company that does solar pool pumps in Florida:
http://www.floridasolarpump.com/ -
The Victron Inverters are interesting - looking at the data sheet here: http://www.victronenergy.com/upload/documents/Datasheet-Phoenix-Inverter-180VA-1200VA-EN.pdf
I see there is only one model with a dip switch to set the hz. And that model is lower in w's 48/350
The reason I am going down this road with my idea is I already have all the equipment I listed. I'm not against getting another inverter if its in the $600-800 range.
The pool pump I have is controlled by a Jandy Aqualink pool system - (iphone app controlled, etc) so its already paired with the motor. It has a control box with big relays feeding to components of it, so I could easily feed in my own 230v source to the relay.Rethink. How about putting those batteries in a 24 volt configuration? You can use thinner cables and have fewer parallel batteries (more stable).
--vtMaps
- 234 Forum & Website