Conext xw 4548 with -48v battery bank
11JAGAN
11JAGAN Solar Expert Posts: 34 ✭✭
The requirement is for remote telecom application
current scenario
There will be two generator (complete off grid) each run twelve hours a day to take care of 3500w load (combination of 230Vac and -48Vdc load)
Attachment not found.
if i stop the generator the the ipms battery bank will take care of -48 Vdc load
but the AC load will be off
i am searching a solution for it
Can i use conext XW 4548 with a positive grounded battery bank?
if so how can i do that?
or any other inverter can function at -48Vdc
Thanks in advance
    Re: Conext xw 4548 with -48v battery bank
    I don't know about + gnd battery bank, but why can't the 4548 inverter/charger, actually invert and provide the 3500w AC too ?
    And I'd throw in at least one more generator, because you are going to be running those 2 into the dirt really quick. The $300 big box store generators have a 500 hour design life, you should be looking at a small water cooled diesel, I think Yamar engines are used in them. Kubota makes one (7Kw) too.
  • 11JAGAN
    The isolated power modules(IPMS) is a charger with a battery bank (which is positive grounded).
    i don't want additional battery bank ,since the battery bank inside ipms is sufficient for me.
    i just want an inverter which should operate at -48v dc
  • Blackcherry04
    Try this and see if it suits you. Ck with Schneider customer service if in doubt about a XW.
    http://legacy.outbackpower.com/pdf/tech_notes/Positive_Grounding_of_OutBack_Devices_Rev2.pdf
  • 11JAGAN
    Can i do like thisAttachment not found.
    BB. Super Moderators, Administrators Posts: 33,448 admin
    Just be careful with any I/O (communications, RS 232, RS 422, i/o ports). They will usually be referenced to the negative battery bus voltage (i.e., that will be "signal ground"). If you connect to external/other equipment--The shifted "positive" ground can blow wiring between devices with mix positive/negative grounds.
    Some interfaces, like 10/100/1,000 BaseT Internet, are (usually) transformer isolated interfaces and a good way to communicate between positive and negative ground referenced devices.
  • 11JAGAN
    i am not going to use any communication device in this
    any other issues
    11JAGAN wrote: »
    any other issues
    How do you program it? The Combox or SystemControlPanel run off the Xanbus. I don't know if it is isolated or not.
