Xw6048 with grid breaker turned off
fca1
Solar Expert Posts: 124 ✭✭
Hi just a question when I turn off the breaker that feeds the xw ac1
It shows this in ac voltage ....it's Strange
48.9v ?? Attachment not found.
Re: Xw6048 with grid breaker turned off
Check the neutral and earth ground at the Inverter and see if you get that on a dvm. -
Shows 0V on mine.
Did you try to measure what it really is at AC1 terminals? -
Re: Xw6048 with grid breaker turned offShows 0V on mine.
So reading it with multimeter
It matches the reading of the xw6048
50v and DMM 49v
With ac grid breaker on I got 3v between neutral and earth ..
With ac grid breaker off I got 100v between neutral and earth..
I don't have batteries negative conected to earth..
At least intentionally only if xw do it by itself -
Apparently, your neutral is not connected to the ground, or it couldn't be 100V in there.
But also, I guess the XW neutral is not connected to the grid neutral.
- 218 Forum & Website
- 185 Solar Information links & sources, event announcements
- 647 Solar Water Pumping
- 813 Wind Power Generation
- 599 Discussion Forums/Café
- 73 Construction
