Re: Shunt based battery monitor wiring issue
There should be only a single negative connection from the battery to the shunt all others go to the other side of the shunt to prevent alternative paths for current to flow, learning through mistake…1 · -
Re: Weird Battery Bank graph, maybe one of the experts can decipher for me
The mp4 connectors are what are typically used to interconnect the panels, I bought some panels which had bad connectors, one melted, one was cracked, pic above, was almost invisible and only discove…1 · -
Re: Weird Battery Bank graph, maybe one of the experts can decipher for me
Looks to me like the grid is charging almost every hour once the voltage drops to around 53.4V, which rapidly recovers to 58V. Dose this reflect in your settings?, you might want to program a charge …1 · -
Re: Help connecting inverter to sub panel with ATS
You are welcome, but please read the text, being sure to follow directions, as an electrican I can say that there is nothing worse than being caught by supprise by installations that do not confirm t…1 · -
Re: Help connecting inverter to sub panel with ATS
This is the way I would wire the ATS, the inverter becomes the prime source (public power), should the inverter shut down for any reason the ATS will transfer to grid power, which would technically b…1 ·