Re: Trace SW4024 circuit diagrams
Usually with stuck relay you get an error of "AC_out connected to AC_in". Newer FW actually has a welded relay error message. Flashing green means AC_in voltage detected but inverter is not…1 · -
Re: Low current levels from solar panels under clear skies?!?
On a cheap PWM controller reversing battery connections might damage it. You can also get pass through to panels when polarity reversed because the series MOSFET switch body diode will conduct puttin…2 · -
Re: Low current levels from solar panels under clear skies?!?
Some of the Renogy '12v' mono panels only have 30 or 32 series connected cells. Should avoid panels less then 36 series connected cells. They are okay for PWM controllers but don't have enough overhe…1 · -
Re: DC Breaker tripping
MicroAir EasyStart has a compressor start delay. When outside unit contactor engages only the outside unit's fan initially comes on. About three to four seconds later the EasyStart begins its compres…1 · -
Re: Duracell branded 6v info
The reason no one at Duracell knew anything about them is the batteries are just their branding label put on battery sourced from other vendor. Only a limited list of lead acid battery manufacturers …1 ·