voltage dump?
System
Posts: 2,511 admin
Comments
-
Re: voltage dump?
Technically a "dump load" is used for generating devices that cannot be safely turned off and you need a place for the energy to go so that you don't overcharge the battery.
The most common device (that I can think of) that needs a dump load is a wind turbine. If, you "stop charging" by opening a switch, the turbine will over-speed and self destruct. Here is a youtube video of a LARGE wind turbine whose blades failed when its brakes failed during a wind storm.
So, your charge controller turns cycles on a "dump load" so that there continues to be a load on the wind turbine and the speed stays within specs. (wind turbines should also have one or two additional methods to prevent over-speed for safety).
The other discussion on this board about "dump loads" is to use them as "opportunity loads"... For an example, your Solar PV panels (which do not need a dump load) have fully charged your battery bank... Now you can turn on an electric heater (for hot water) or turn on a well pump to fill the cistern with the "extra" power available.
In general, using a dump controller to charge a battery is probably not a good as a regular 3+ stage charge controller (most dump loads are either on or off--no "float" setting).
Of course, this is all based on a guess that this is an off-grid system, using solar PV (Photo Voltaic) panels and some sort of modern PWM or MPPT type solar charge controller...
If you have a solar panel just connected to a battery bank--then you will need some sort of charge limiter to prevent your batteries from being damaged/over charged/boiling away your electrolyte.
If you have a "Grid Tied" system (typical solar power system for a home with utility power)--then there is no place to install a dump controller+load.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: voltage dump?
You've no doubt spent quite a bit on your PV system and it's a shame to waste a portion of the energy it produces. I'm going to use excess energy to maintain the charge on a spare battery bank. My main battery bank powers loads on a daily basis and is often depleted by morning, while my spare battery bank will be available to power loads in the event of a grid power failure. -
Re: voltage dump?I have a PV system. IN general do I need a voltage dump (power dump?)?
NO, but you will need a Charge Controller. PV's do not need a "dump load" Wind and Hydro need dump loads to keep turbine speeds down, when batteries are fully charged.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: voltage dump?
Thanks for the responses. I was thinking that was the case as far as wind/hydro.
That brings up the next question. I do have a PWM CC. Can I put in a dump load device or use my CC that it will "turn on" after the batteries are full? It seems like a waste to lose that "excess" energy? As SolarJohn mentioned he can charge a different battery bank. How is that "wired" in? Thanks. -
Re: voltage dump?You've no doubt spent quite a bit on your PV system and it's a shame to waste a portion of the energy it produces. I'm going to use excess energy to maintain the charge on a spare battery bank. My main battery bank powers loads on a daily basis and is often depleted by morning, while my spare battery bank will be available to power loads in the event of a grid power failure.
I would think tha tif you are depleating your batterie bank qvernight, then it is not big enough. Why are you using a seperate bank? By having the two banks sepatate you are shortenning the operational life of both banks. -
Re: voltage dump?That brings up the next question. I do have a PWM CC. Can I put in a dump load device or use my CC that it will "turn on" after the batteries are full? It seems like a waste to lose that "excess" energy? As SolarJohn mentioned he can charge a different battery bank. How is that "wired" in? Thanks.
Most CC's do not have this function. SolarJohn and I have an additional controller that when the battery reaches a voltage level the controller turns on other loads. SolarJohn is using the Morningstar relay drive controller and I am using a industrial PLC. -
Re: voltage dump?
Quote: I would think tha tif you are depleating your batterie bank qvernight, then it is not big enough. Why are you using a seperate bank? By having the two banks sepatate you are shortenning the operational life of both banks.
I could certainly use a bigger battery bank, but I'm not shortenning the life of both banks.
I've programmed the system to stop using power from the main battery bank when the SOC drops to about 80%. I could have used a lighter load, but then I would be under-using my system. I want to use as much free energy from the sun as I can, without stressing my battery bank.
My spare battery bank consists of older batteries, and they're not the same type as my newer battery bank. Connecting them together would not be a good idea. However, by maintaining my spare bank at full charge, I always have stored energy to use in the event of a grid power failure.
I use a Morningstar Relay Driver, controlling a relay, to divert energy from the charge controller to the spare battery bank. The first priority is to recharge the main battery bank, but when that bank is nearly fully charged, excess energy from the PV array is used to charge the spare battery bank. The relays are controlled by a Morningstar Relay Driver, which allows me to establish voltage setpoints, and therefore charging priorities.
To summarize: Charging my main battery bank is top priority, and I use as much energy from that bank as I can (without stressing the battery bank too much), in order to get the most from my small system. The spare battery bank is maintained at full charge, but seldom used to power loads. It is my emergency power supply. -
Re: voltage dump?
John,
Just out of curiosity, what criteria do you use to determine 80% soc? Voltage? if so how does that compensate for load? Total amp/hour draw from a meter like a Trimetric? Specific gravity? I don't know anyway to measure sg and translate it to do any switching.
Tony -
Re: voltage dump?John,
Just out of curiosity, what criteria do you use to determine 80% soc? Voltage? if so how does that compensate for load? Total amp/hour draw from a meter like a Trimetric? Specific gravity? I don't know anyway to measure sg and translate it to do any switching.
Tony
Battery voltage, under a significant load, according to information from the battery manufacturer. I depend on a compressor kicking in, and the resultant voltage drop as my trigger to remove the load. I also compensate for momentary motor-starting voltage sags by programming in a high-to-low transition delay of 10 seconds. This system is not terribly accurate of course, but I've monitored it and am satisfied that it's fairly close. Once the load is removed, no-load battery voltage gradually increases to 12.5 volts or more. This seems to indicate that I've not gone lower than 80% SOC. I could probably use a little more energy from them each night without stressing them too much.
I wrote more about it here: http://solarjohn.blogspot.com/2007/03/measuring-battery-state-of-charge.html and in more recent blog posts.
John -
Re: voltage dump?
I have not ever used one of these battery monitors (grid tied system on my home)--but I like the Specs. for the new Xantrex battery monitors which have a programmable output--that can be set to turn on/off at specific State of Charge levels. Use the output for an alarm/load control (highly recommended for helping to prevent killing of batteries on automatic/spouse/employee/somebody who does not pay for batteries/etc. operated installations).
The high-end Xantrex BM also appears to have battery temperature compensation--highly useful for those installations with wide temperature swings.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: voltage dump?Battery voltage, under a significant load, according to information from the battery manufacturer. I depend on a compressor kicking in, and the resultant voltage drop as my trigger to remove the load. I also compensate for momentary motor-starting voltage sags by programming in a high-to-low transition delay of 10 seconds. This system is not terribly accurate of course, but I've monitored it and am satisfied that it's fairly close. Once the load is removed, no-load battery voltage gradually increases to 12.5 volts or more. This seems to indicate that I've not gone lower than 80% SOC. I could probably use a little more energy from them each night without stressing them too much.
I wrote more about it here: http://solarjohn.blogspot.com/2007/03/measuring-battery-state-of-charge.html and in more recent blog posts.
John
John,
You have nicely quantified my own intuition. While perhaps not 100% accurate in all cases, it certainly gives a pretty good general idea of condition. As Bill suggests, the Xantrex meter can trigger a lvd, and I think the new Bogart series will do so as well. In my case, my nightly draws are so small, I seldom see voltages, even under load below ~12.5. As I said, I use the Bogart Tri-metric %meter, coupled with the amp/hours from full to guide me in much the same way.
Tony
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed