Fm80 - T100
System
Posts: 2,511 admin
Hello,
I am interested in one of the charge controllers:
Outback Flexmax 80
Apollo T100
I have seen, that the amps, volts and price is higher of the T100.
What other differences are between them?
How is the quality of them?
The panels will have about 1500WP and are about 50m far away of the charge controller.
The volts should be as high as possible to save wire costs.
Batteries, Inverter and Charger from the generator have all 24V.
Thanks
BRJ
I am interested in one of the charge controllers:
Outback Flexmax 80
Apollo T100
I have seen, that the amps, volts and price is higher of the T100.
What other differences are between them?
How is the quality of them?
The panels will have about 1500WP and are about 50m far away of the charge controller.
The volts should be as high as possible to save wire costs.
Batteries, Inverter and Charger from the generator have all 24V.
Thanks
BRJ
Comments
-
Re: Fm80 - T100
BRJ,
The T-100 and FM80 are both large and feature-rich MPPTR charge controllers, and they both come with five year warranties.
The T-100 can handle PV arrays with higher power- and voltage specs than can the FM80, and it includes a built-in battery status monitor. However, it’s also more expensive than the FM80.
The main technical advantage of the T100 for your application might be the higher input voltage specification, as this might allow you to configure your array for a higher voltage. This could be helpful for your array located 50 meters from the battery bank.
However, you’ll have to compare temperature-corrected array specs for different configurations along with wire size and cost to determine the optimal solution.
Note, however, that this is not a free benefit. All else being equal, a higher array voltage means that the controller will operate at lower efficiency. Additionally, there are no readily available DC circuit breakers available for >150 VDC systems, so you’d need to use fuses for over-current protection of the array string(s).
I would suggest that either controller is larger than you need for your planned system with 1,500 W and a 24 V battery bank. Instead, you may wish to consider an OutBack MX60, a Xantrex XW60, or the just announced OutBack FM60. The latter model is a replacement for the MX60 and is a 60 Amp version of the FM80.
HTH,
Jim Goodnight
“crewzer”
OutBack Power Systems -
Re: Fm80 - T100
Dear Jim,
I will perhaps use one of the following modules:
http://www.schottsolar.com/uploads/media/SCHOTT_ASI_78-81-86_en.pdf
At moment it is not easy to get modules in Germany.
With the FM80 I can make 6 modules serial in one string.
Nominal voltage is about 100volts.
Open circuit voltage will be about 136V.
3 strings makes about 1450W nominal power.
Is the initial power of 1800W not to high for the MX60?
I think a cable with 25mm² is for 50m necessary.
What is your opinion?
With FM80 it is possible to make later 4 strings.
I found prices for MX60 about 490 USD and for FM80 about 570 USD in USA.
In Germany they cost 980 USD and 1100 USD.
Why do they cost here so much more?
What should be all in the combiner for this system?
circuit breaker
overvoltage protection (lightning)?
grounding lug
Is the circuit breaker enough for lightning?
The difference between MX60 and FM 80 are voltage and amps.
Anything else?
Thanks
BRJ -
Re: Fm80 - T100
BRJ,
I'm on travel today and I have family activities this weekend. I'll respond to your questions on Monday.
Regards,
Jim Goodnight
"crewzer"
Eastern Regional Sales Manager
OutBack Power Systems -
Re: Fm80 - T100
BRJ,I will perhaps use one of the following modules:
http://www.schottsolar.com/uploads/m...8-81-86_en.pdf
At moment it is not easy to get modules in Germany. With the FM80 I can make 6 modules serial in one string. Nominal voltage is about 100volts. Open circuit voltage will be about 136V.
At -10 C, the temperature corrected voltage specs would be ~113 V and ~154 V. The latter value is higher than the FM80’s limits (145 V operational and 150 V absolute maximum), so the six modules in a series string is not a good idea. I’d recommend a maximum of five modules per series string.3 strings makes about 1450W nominal power. Is the initial power of 1800W not to high for the MX60?I think a cable with 25mm² is for 50m necessary. What is your opinion?
Reference: FM80 and FM60 User Manual ( http://www.outbackpower.com/pdfs/manuals/flexmax.pdf )With FM80 it is possible to make later 4 strings.I found prices for MX60 about 490 USD and for FM80 about 570 USD in USA. In Germany they cost 980 USD and 1100 USD. Why do they cost here so much more?What should be all in the combiner for this system? circuit breaker… overvoltage protection (lightning)? grounding lug
http://www.outbackpower.com/products/integration_hardware/system_components/
OutBack’s combiner boxes (and controller and inverters) include grounding lugs. System grounding should be carried out according to local electrical standards.Is the circuit breaker enough for lightning?The difference between MX60 and FM 80 are voltage and amps. Anything else?
MPPT algorithm: periodic sweep vs. continuous tracking
Output current: 60 A vs 80 A
Ambient temperature: 25 C vs 40 C for full power
Operational Input Voltage: ~141 V vs. 145 V
Remote Programming: no vs. yes (via Mate)
Data Logging: 64 days vs. 128 days
Note that MX60 production has been discontinued. It has been replaced with the FlexMax 60, which is the same physical size as the legacy MX60, and is still rated at 60 A output, but otherwise offers all of the features of the FM80. See here for more information: http://www.outbackpower.com/products/charge_controllers/flexmax/
I hope this additional information is helpful to you.
Regards,
Jim Goodnight
“crewzer”
Eastern Regional Sales Manager
OutBack Power Systems -
Re: Fm80 - T100
Dear Jim,
thank you for your answer..
I have ordered the Flexmax.
Perhaps I will use the Kaneka K60 modules.
Thin film modules produce on the beginning more Wp as later.
How many Kaneka K60 modules can max. run on the FM80?
Best regards
BRJ -
Re: Fm80 - T100
from what jim had written to you, "The FM80 is rated for arrays of up to 2,500 W STC with 24 V battery systems." this will be lower for 12 battery systems and higher for battery systems that are higher and runs fairly linear meaning x2 battery voltage = x2 wattage capability.
Maximum Solar Array: 12 VDC systems 1250 Watts / 24 VDC systems 2500 Watts / 48 VDC systems 5000 Watts / 60 VDC Systems 7500 Watts. -
Re: Fm80 - T100Batteries, Inverter and Charger from the generator have all 24V.
Perhaps I will use the Kaneka K60 modules… Thin film modules produce on the beginning more Wp as later…. How many Kaneka K60 modules can max. run on the FM80?
As indicated, the FM80 is rated to handle a PV array rated at between 2,000 W STC and 2,500 W STC when used with 24 V (nominal) battery systems. The maximum rating depends on local electrical codes and standards.
Here’s a link to the latest spec sheet: http://www.outbackpower.com/products/charge_controllers/flexmax/
You could connect between 33 (1,980 W STC) and 41 Kaneka K60 modules (2,460 W STC) to a single FM80, depending on the local electrical code and standards. However, it would be a potentially messy installation.
Ref: http://www.havelland-wind.de/images/files/1208514687-2.pdf
The K60’s unusually high Voc (92.0 V) limits the array configuration to no more than one PV module in series for connection to the FM80. Accordingly, all K60 modules for your array would have to be connected in parallel.
The K60’s 67.0 Vmp also means that the modules generally can’t be used to charge 48 V (nominal) batteries, as the module voltage will drop as they heat up. This would be a problem should you want to increase your system size and/or convert to a 48 VDC inverter
Accordingly, I would not recommend the Kanera K60 module for your system.
HTH,
Jim / crewzer
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed