PV and combiner switch

what about this. I have a new heavy duty marine battery selector switch.these are the big red switches with batt. 1,batt.2,all, and off. wouldnt this work well between the PV and the charge controller as both a combiner and disconnect? these are rated 48volts up to 350 amps.
whatdayathink?

Comments

  • System2
    System2 Posts: 6,290 admin
    Re: PV and combiner switch

    First thoughts, without actually seeing the switch, or your project, proposed or already installled - - -
    1) You would still need fuses.
    2) If you have insurance, how would a non-listed switch affect it in the event of a claim?
  • niel
    niel Solar Expert Posts: 10,300 ✭✭✭✭
    Re: PV and combiner switch

    as a disconnect it would work, but it may be overkill in some circumstances. as a combiner it can accomodate 2 strings up to its voltage rating and i'm sure they won't be anywhere near the current rating of that switch. fuses, as was stated, will still be needed.