Repeated Low voltage on my Conext XW pro

memonty
memonty Registered Users, Users Awaiting Email Confirmation Posts: 4
Recently Conext XW Pro started to give me daily low voltage warning. 
I’m grid tied and when there is no power and the battery is depleted it shuts down and needs a charger to reboot it. 
The 3 charging indicators on the front of the panel no longer lights up
My solar provider doesn’t seem to know how to fix this issue. 
Please tell me what to do. I’m getting really frustrated and desperate. I’m connected to the Insight Mobile App
would truly appreciate any help I can get to rectify this issue. Thanks 

Comments

  • SumPower
    SumPower Registered Users Posts: 144 ✭✭✭
    edited June 6 #2
    Many here would like to help. But more information about your system is needed.

    Battery type and amp hour capacity? LFP Batteries, AGM or Flooded lead acid.

    Kw of solar panels?

    Charge controller?
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 7,129 ✭✭✭✭✭✭
    edited June 7 #3
    Add my email below to Insight and I will take a look.  Your post sounds like your battery is dead.  Which 3 charge indicators are you writing about?  A screen below, which 3 ?



    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • memonty
    memonty Registered Users, Users Awaiting Email Confirmation Posts: 4
    Hi Dave
    My provider just gave me the info you requested above. 
    Please see below
    Battery type and amp hour capacity? - LFP Battery 10.24 Fortress 

    Kw of solar panels? - don't remember but I think you have 10 panels @ 590W (or 650W). So total power is 5.9kW

    Charge controller? - Schneider MPPT60
  • memonty
    memonty Registered Users, Users Awaiting Email Confirmation Posts: 4
    edited June 18 #5
    Sorry but I’m not seeing your email. 
    Would love if you could login and take a look. 
    The lights I’m referring to are the charging lights above the 3 battery icons on the front of the Inverter in the green section. 
    When my provider unplugs the charger controller from the inverter the charging lights comes on but when it’s replugged the lights go off. 
  • BB.
    BB. Super Moderators, Administrators Posts: 33,745 admin
    If you are on a mobile phone, you probably do not see Signatures in the forum software... Anyway:

    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • heavy_humster
    heavy_humster Registered Users, Users Awaiting Email Confirmation Posts: 2
    This is a classic Xanbus charge coordination issue.

    When the MPPT60 is connected to the XW Pro via Xanbus, the inverter takes over as the charge master. It tells the MPPT60 what charge stage to run (bulk/absorb/float) and the MPPT defers to it. If the XW Pro charger is configured incorrectly or its charge current is set to 0, it will suppress the MPPT60 charging entirely.

    When you physically unplug the MPPT from the Xanbus bus, it loses the master command and falls back to its own standalone charge settings - which is why charging lights come on.

    Things to check:
    1. In SCP or Conext Connect, go to XW Pro > Charger settings. Make sure AC Charger max charge current is not set to 0, and that the charge stage voltages match your battery specs.
    2. Go to MPPT60 settings and verify it sees the battery bank type correctly (LFP based on your setup?).
    3. If you have a BMS connected via Xanbus, check if it is sending a charge inhibit signal - some LFP BMS units do this when cells are unbalanced.

    The symptom you are describing (charges only when MPPT is disconnected from Xanbus) almost always points to the XW Pro charge master overriding the MPPT with a 0A command or a charge inhibit from BMS comms.
  • memonty
    memonty Registered Users, Users Awaiting Email Confirmation Posts: 4
    Hi Bill
    Thanks for responding to my post.
    I would really appreciate if you could login to my insight app but unfortunately I don’t know how to add your email to the app. Can you walk me through how to do this?  
    Much appreciated and thanks.  
  • BB.
    BB. Super Moderators, Administrators Posts: 33,745 admin
    Memonty,

    Dave will have to walk you through your system setup... I do not have the knowledge.

    Take care,
    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 7,129 ✭✭✭✭✭✭
    I did contact her from the road Bill !  Hope you are doing well this summer! Come on up?  Best!  --Dave
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • BB.
    BB. Super Moderators, Administrators Posts: 33,745 admin
    Great Dave!

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 7,129 ✭✭✭✭✭✭
    Tried to help,  sent a procedure. Did not hear back. Even resent in case it went to SPAM.
    Maybe they went to LA to see the US win the Soccer game tonight😉 
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • Dave Angelini
    Dave Angelini Solar Expert Posts: 7,129 ✭✭✭✭✭✭
    I did take a look!   Appears you are using more energy than you are making.    Please get back!  Best!  --Dave






    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net