Off Grid Generac
c1302c5
c1302c5 Registered Users, Users Awaiting Email Confirmation Posts: 1
I have an off grid cabin with a Generac 7kw Model 43893 trying to power the cabin. I don’t have the inside transfer switch. The generator will start but not supply power to the panel. I’m thinking there should be a jumper I should be able to use to get the generator to supply power? I have a solar panel connected to the generator battery to keep it charged, which appears to be working fine. Any tips, tricks or suggestions would be appreciated.
  • cleancurrent002
    cleancurrent002 Registered Users Posts: 14 ✭✭
    Yeah, without the transfer switch, the generator might not be feeding power. Some models need a jumper to bypass that setup. Check your manual or wiring diagram and make sure the breaker on the generator isn’t off. You’re on the right track, bro!
  • mihail499xAaz
    mihail499xAaz Registered Users Posts: 5 ✭✭
    That model is not meant to backfeed a panel directly. There is no jumper you can add. It needs a proper transfer switch or an inverter setup to connect safely.
    If it starts but does not power the panel, it is doing exactly what it should. Backfeeding without a transfer switch is dangerous and illegal. Your options are to install a manual transfer switch, use a generator inlet with interlock, or run loads directly from the generator outlets. For off grid cabins, many people pair the generator with an inverter charger that feeds the panel correctly.
    Do not try to hack around this. Get the right switching hardware.