Looking for some assistance with batteries discharging at different rates.  I have a SolArk 15-LV and two eVault 360ah batteries and the batteries are discharging at different rates.

Comments

  • JRHill
    JRHill Registered Users Posts: 464 ✭✭✭✭
    edited August 30 #2
    Please explain further. Are these in use on the same system? Are they on different charge controllers? How are they wired if on the same system?
    Off Grid. Two systems: 1) 2925w panels, OB VFXR3648, FM80, FNDC, Victron BMV-712, Mate3s, 240 xformer, four SimpliPHI 3.8; 2) 780w, Morningstar 30a, Grundfos switch, controller and AC/DC pump, 8 T105. Honda EU7000is w/AGS. Champion 3100. HF 4550, Miller Bobcat.
  • JRHill
    JRHill Registered Users Posts: 464 ✭✭✭✭
    When I changed over to LFP04 batteries the installation requirements made it quite clear that a connecting bus was preferred but if individually wired that each block have EXACTLY the same cabling AND length regardless of position.
    Off Grid. Two systems: 1) 2925w panels, OB VFXR3648, FM80, FNDC, Victron BMV-712, Mate3s, 240 xformer, four SimpliPHI 3.8; 2) 780w, Morningstar 30a, Grundfos switch, controller and AC/DC pump, 8 T105. Honda EU7000is w/AGS. Champion 3100. HF 4550, Miller Bobcat.
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 7,052 ✭✭✭✭✭✭
    Also bad balance from the BMS of each battery not being networked as a system. Defective battery is up there also.
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • Dave Angelini
    Dave Angelini Solar Expert Posts: 7,052 ✭✭✭✭✭✭
    Set-points? It seems there are so many ways to mess this up. Why do we do it😉