Placing a fuse on every solar battery?

softdown
Solar Expert Posts: 3,937 ✭✭✭✭
I’ve seen this recommended a few times. Anybody doing it?
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
Comments
-
Every source of power needs an Over Current Protective Device installed to protect the conductors from geting to hot to cause a fire. And to protect people from getting injured or shocked.Every battery string I have has a breaker.
-
Don’t recall seeing systems with a fuse on each batteryFirst Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
At the very least, the usual requirement is one Over Current Protective Device per "string" of batteries.
If you have one series string, 1 fuse.
If you have two series strings, 2 fuses.
etc.
Actual practice can have two fuses per "floating" (no ground bonding)string, one at + output, and a second on the - output. This is done to provide more robust fault coverage (I.e, a multiple shorts in a "floating" power system).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Yes, having a fuse on every string is accepted practice.Since lithium fires are toxic it seems like more fuses on lithium batteries is prudent.First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
-
If your battery bank is (for example) negative grounded (frame, house green wire/ground rod/etc.), one fuse per series battery + bus connection is sufficient.If you have multiple 3.7 volt cells in parallel, then the set connected in series for 12/24/48 VDC etc., should each cell have its own fuse... One could argue that, but I have never seen that done (lots more fuses). That would help protect against a single cell going shorted...But again, I have not seen that done, and I would suggest that the expense, complexity of extra wiring, etc. would make small AH Cell Lithium batteries an unsupportable configuration.If you are concerned about fire and byproducts (a real concern)--Install in separate shed/root cellar/or similar. Not a bad idea anyway (Battery "shed" separate from home/critical buildings).Also, in reality, fuses/breakers are to protect your wiring from starting a fire, not to protect attached "devices".Installing (or purchasing batteries with BMS) a battery management system for your Lithium bank is probably the best solution.Lots of protection, over/under voltage cells, over current charging/discharging current, much more precise and accurate over current protection vs fuses/breakers, over/under temperature of cells, shutdown of bank if any parameters are exceeded, etc.Bill "not a battery system engineer" B.Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 652 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 612 Discussion Forums/Café
- 305 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed