CC and remote Voltmeters different?

morpho
morpho Solar Expert Posts: 179 ✭✭✭
My magnum remote gives me a full volt difference (higher) than my midnite classic CC’S give me. My handheld voltmeter confirms the CC readings. What gives? 

Thanks. 
11.5 kw array  -  3 - midnite solar classic 200's   -  Magnum MS-PAE Inverter  -  Magnum ME-RC50 remote  -  ME-BMK batt-monitor  -  2 simpliphi lithium (48v) - Yamaha ef3000ise - 1 confused look on face

Comments

  • JRHill
    JRHill Registered Users Posts: 373 ✭✭✭✭
    I looked into having my Fluke 77 calibrated so I have a standard. I might as well buy a new equivalent at Platt for the costs quoted. I wasn't surprised because it is probably a function of those uses where there has to be a calibration sticker and those are expensive.

    To me, here is what gives: if your handheld confirms the CC then maybe that is enough of an average. If other stuff is off you really need to look at wiring, its hygiene and retorque. If all is good then you might recalibrate voltages at the device, if you can **.... A full volt at 48vdc is a bunch especially with the flat curve of SimpliPhi blocks. My inverter, CC, batteries, shunts all operate within 0.2 +/- when I last checked. On Outback stuff the recal adjustments at the device are in steps of 0.4v which kind of sucks. Best practice is to take readings under load.
    .
    ** A mixed system can be a curiosity.
    Off Grid. Two systems: 1) 2925w panels, OB VFXR3648, FM80, FNDC, Victron BMV-712, Mate3s, 240 xformer, four SimpliPHI 3.8; 2) 780w, Morningstar 30a, Grundfos switch, controller and AC/DC pump, 8 T105. Honda EU7000is w/AGS. Champion 3100. HF 4550, Miller Bobcat.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,637 admin
    In general, make sure your batteries are "charged/full" for DVMs... Seen some strange behaviors with weak batteries (consistent, but wrong, readings--If I recall correctly, saw "added voltages" such as 4x 12 volt batteries in series did not add up individual battery voltages (I.e. 12 volts * 4 added up to something other than 48 volts, etc.).

    You can find precision voltage sources at Amazon/etc...

    Some of the higher end charge controllers have a programmable offset to "re-calibrate".

    Is the remote getting its battery voltage via its own battery wiring, or is it communicating with the charge controller?

    If there each has their own "sense" leads/connections... There is always the possibility of there is current flowing, that the voltage readings would be different because of voltage drop across wiring/connections. I.e., the voltage measured at the charge controller would be different vs battery bus (if there is "relatively" high current flow).

    -Bill

    https://en.wikipedia.org/wiki/Segal's_law

    The saying was coined by the San Diego Union on September 20, 1930: "Confusion.—Retail jewelers assert that every man should carry two watches. But a man with one watch knows what time it is, and a man with two watches could never be sure." Later this was — mistakenly — attributed to Lee Segall of KIXL, then to be misquoted again by Arthur Bloch as "Segal's Law".[2]
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,917 ✭✭✭✭✭✭
    Magnum is out of business also...

    Get 3 watches !  That is how they measure fuel metering on rockets.  An algorithm also goes into play for the 3 sensors.
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • BB.
    BB. Super Moderators, Administrators Posts: 33,637 admin
    As Dave says... Critical systems should have multiple sensors for critical systems... Typically 3 at least. Otherwise, for systems that are not critical, then a "sensor failure" should not cause catastrophic failures.

    A recent example is the Boeing 737 Max that used angle of attack sensors to "manual override" pilot controls (push nose down if plan is close to stalling)--The major issues was the failure of one sensor (showing high angle of attack near stall conditions) would trigger the MCAS (override computer) to push the nose down even if the second sensor indicated normal flight conditions. And the pilots could not apply enough control pressure to "over power" the safety system (2 planes crashed).

    The MCAS was created because less than engineering solutions to create a more fuel efficient version of the plan required larger diameter engines--Force the new engines to be mounted higher and further forward--Which can tend to push the nose up and create stall conditions. And any mention of the MCAS and how to override was removed from manuals. And as I recall, there was an optional "red MCAS failure light" (extra cost option for the aircraft).... All's of this was so pilots could fly old and new version of 737's without additional training (save crew training costs). (As I recall, the pilot could pull the circuit breaker for the MCAS and turn off the servo/controller override and allow pilots to regain control/cancel MCAS override of controls).

    https://www.icheme.org/media/19013/lpb287_pg24.pdf

    And, of course, Boeing never tested a sensor failure of what was know to be (relatively) failure prone AOA sensors (bird strikes, icing, maintenance issues, etc.).

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,917 ✭✭✭✭✭✭
    Ahh the Boeing Corp.  They are a big warning to other Engineering based companies for woke ideology
     (DEI) off the deep end.  Thanks Bill for reminding me of that one. Friday !  I am buying in the Lounge at 5pm 😎
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • Graham Parkinson
    Graham Parkinson Registered Users Posts: 175 ✭✭✭
    You can buy voltage reference chips to use to calibrate your multimeter

    https://uk.rs-online.com/web/content/discovery/ideas-and-advice/voltage-references-guide

    Offgrid in cloudy PNW

    Full Schneider system with 18 REC 420W panels, 100A-600V controller, XWPro, Insight Home, six Discover AES Rackmount 5kW batteries, Slimline enclosure, Lynk II, AGS, H650,  H2200, H3000 (On Victron AutoTrans with Gen Line 2 wire AGS on AC1), Kubota 4500, Onan 7500 (on second AGS and AC2).