GoodWe hybrid inverter GW20K-ET
chrisgraham
Registered Users, Users Awaiting Email Confirmation Posts: 7 ✭✭
Hello everyone
I just bought a GoodWe hybrid inverter GW20K-ET, unfortunately it only has one battery connection. On this connection the hybrid inverter can charge/discharge the battery with 50A. GoodWe offers Lynx F Plus+ batteries that can be connected in parallel. This battery can be charged/discharged with a maximum current of 25A.
The question is: if you connect two of these batteries in parallel, can you charge and discharge them with a total of 50A, or only with 25A? Does anyone have any information here?
Thanks for any insights!
Chrisgraham
Comments
-
Welcome to the forum Chris!
It appears the answer is yes, you can parallel and get 25 amps per stack... You would need to use the correct size of wiring (mm^2) to safely support the paralleled current (I.e., 25 amps for one, 50 amps for two, etc.).
HOWEVER, I have no knowledge of this system (which is a "high voltage" stack of batteries) and CAN Bus (?) communications between the Hybrid Inverter and Battery Bank(s). The documentation is here:
https://en.goodwe.com/lynxf-plus
https://en.goodwe.com/et-15-30kw
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Another question... Are you "stacking" the batteries (2-5?) first, then adding a second "tower" with another 2-5 stacks? Note that each "tower" needs to have the same number of modules stacked (I.e., each set would be 2/2, 3/3, etc. of "matched" modules to match parallel connected tower voltages).
I would guess that both 2/2 would work as would one tower of 4 modules (same amount of stored energy in either configuration--Save some costs with only one "tower head").
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:Welcome to the forum Chris!
It appears the answer is yes, you can parallel and get 25 amps per stack... You would need to use the correct size of wiring (mm^2) to safely support the paralleled current (I.e., 25 amps for one, 50 amps for two, etc.).
HOWEVER, I have no knowledge of this system (which is a "high voltage" stack of batteries) and CAN Bus (?) communications between the Hybrid Inverter and Battery Bank(s). The documentation is here:
https://en.goodwe.com/lynxf-plus
https://en.goodwe.com/et-15-30kw
Hi, my problem has been solved. but Thank u for your professional answer. Sorry, link cannot be opened
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed