Proper Grounding for Sunny Boy 6048 Inverter?
kris25
Registered Users Posts: 4 ✭
I'm currently working on setting up a SMA 6048 inverter. The DC inputs accept up to 3/0 gauge +, - and ground. Is a #6 ground acceptable? Running a 2/0 ground to match my + and - seems like way too much.
This is what's set up on it:
(1) SMA 6048 single phase, 120V
(2) Banks of 4 Renogy Sealed Gel Batteries (12V 200AH each)
30' Romex 6/2 wire from inverter to electrical box
This set-up is off grid with a generator to charge the batteries. Also, on top of the correct ground size can I run this to it's own grounding pole? The electrical box is on the other side of the cabin about 30' away.
This is what's set up on it:
(1) SMA 6048 single phase, 120V
(2) Banks of 4 Renogy Sealed Gel Batteries (12V 200AH each)
30' Romex 6/2 wire from inverter to electrical box
This set-up is off grid with a generator to charge the batteries. Also, on top of the correct ground size can I run this to it's own grounding pole? The electrical box is on the other side of the cabin about 30' away.
Comments
-
Welcome to the forum Kris25,
Ideally, you should refer to the NEC (National Electric Code in much of USA) or similar for exact requirements.
As a simplified example, the size of current carrying conductors vs equipment/panel grounding conductors (note copper vs aluminum--AL needs heavier cable for "same" copper current ratings):
https://learnmetrics.com/ground-wire-size-chart-nec-grounding-conductor-size-chart/Size Of Copper Wire (AWG or kcmil): Copper Grounding Electrode Conductor Size (AWG or kcmil) 8 AWG Copper Wire 8 AWG Copper Ground Wire 6 AWG Copper Wire 8 AWG Copper Ground Wire 4 AWG Copper Wire 8 AWG Copper Ground Wire 3 AWG Copper Wire 8 AWG Copper Ground Wire 2 AWG Copper Wire 8 AWG Copper Ground Wire 1 AWG Copper Wire 6 AWG Copper Ground Wire 0 (1/0) AWG Copper Wire 6 AWG Copper Ground Wire 00 (2/0) AWG Copper Wire 4 AWG Copper Ground Wire 000 (3/0) AWG Copper Wire 4 AWG Copper Ground Wire 0000 (4/0) AWG Copper Wire 2 AWG Copper Ground Wire
The SMA manual should list the wiring requirements... But a quick math check:- 6,000 Watts * 1/0.85 AC inverter eff * 1/42 VDC battery cutoff voltage = 168 Amps max current
https://lugsdirect.com/WireCurrentAmpacitiesNEC-Table-301-16.htm
3/0 is certainly heavy enough cable (higher insulation temperature ratings, smaller AWG can be used).
Another issue to watch out for is cable resistance... ~!68 amps is a lot of current--And "too long" or "too small of AWG" cable can increase voltage drop and cause battery cutoff.
For example... 168 amps @ 3/0 cable @ 46.00 Batt voltage - 42.00 batt cutoff @ xxx feet?
https://www.calculator.net/voltage-drop-calculator.html?necmaterial=copper&necwiresize=6&necconduit=steel&necpf=1.&material=copper&wiresize=0.4066&resistance=1.2&resistanceunit=okm&voltage=46&phase=dc&noofconductor=1&distance=48&distanceunit=feet&eres=168&x=0&y=0&ctype=necResult for 48 feet of 3/0 cable @ 168 amps
Voltage drop: 4.03
Similar calculations for AC side...
Voltage drop percentage: 8.76%
Voltage at the end: 41.97- 6,000 Watts * 1/115 VAC nominal = 52 Amps max current
Note that a 48 volt @ 400 AH is a relatively small battery bank for a 6,000 Watt inverter... GEL batteries do have better high/surge current than flooded cell lead acid batteries.... Typically for a 6 kWatt inverter, would be suggesting a 600 AH@ 48 VDC battery bank minimum.
But the full answer also needs to know your planned loads (Watt*Hours per day, max surge WH, etc.).
Another possible issue--Look at the specifications for your GEL batteries. Max charging and discharging currents can be an issue... If these are your batteries:
https://www.renogy.com/deep-cycle-hybrid-gel-battery-12-volt-200ah/CHARGING PARAMETERSCharge Voltage: 13.6V~13.8V
Maximum Continuous Charging Current: 60A
Maximum Continuous Discharging Current: 20A
opc:
Standard Operation Temperature: 77°F±9°F(25°C±5°C)
Storage Temperature: -4~140°F/ -20°C~60°CThen 60 amps max charge rate per string (actually pretty high charge rate for GEL batteries) and 20 amp max continuous drain (pretty low for GEL batteries)--Almost looks like the battery charge/discharge spects have been reversed(???).
https://www.renogy.com/content/RBT200GEL12-G1/GEL200-Datasheet.pdf
The PDF (above link) has very different specifications (20 amp charging or 10%; discharging... Upwards of 3C or 600 amps discharge current).
Watch charging voltage (and current). In general GEL batteries do not like to be "over charged".
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks for all of the info! So I should run a DC ground and AC (main panel) ground to one single location?
What is confusing me the most is that there is currently no ground that I can see in the panel. There is a ground wire in the "generator room" outside the house but it's just coiled behind the breaker boxes and doesn't go to anything. A generator was always the only source of power. Does that explain why the coiled wire was never grounded to anything? -
"Generator Room"
Coiled ground going to nothing
8/3 Romex that runs from generator room to main panel (before I ran 6/2 from Inverter)
Inverter and batteries (30' from main panel)
-
Kris can you tell us a bit more about the Genset?120 or 120/240 VAC?Is your home 120 VAC only or do you have (or plan to use) 240 VAC applicants/well pumps too?It looks like your main panel is wired for 120/240 VAC and the inverter you have is 120 VAC only...Questions about Genset/inverter transfer switch?BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
I have a 9000 watt Champion generator that can run either 240 or 120 and I also just got a Honda EU3000is. The Honda is enough to run everything but the shallow well pump. I believe the Honda is only 120 but all I needed was an adapter to the large cord in the first pic.
I only plan on using 120VAC. This is a weekend type cabin. I installed a 120V shallow well pump, have a propane stove, small electric water heater no washer/dryer no AC etc... Just a real simple power usage. The biggest draw (excluding the pump) is probably the refrigerator which is about half the size of a normal fridge.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed