Proper Grounding for Sunny Boy 6048 Inverter?
kris25
Registered Users Posts: 4 ✭
I'm currently working on setting up a SMA 6048 inverter. The DC inputs accept up to 3/0 gauge +, - and ground. Is a #6 ground acceptable? Running a 2/0 ground to match my + and - seems like way too much.
This is what's set up on it:
(1) SMA 6048 single phase, 120V
(2) Banks of 4 Renogy Sealed Gel Batteries (12V 200AH each)
30' Romex 6/2 wire from inverter to electrical box
This set-up is off grid with a generator to charge the batteries. Also, on top of the correct ground size can I run this to it's own grounding pole? The electrical box is on the other side of the cabin about 30' away.
Welcome to the forum Kris25,
Ideally, you should refer to the NEC (National Electric Code in much of USA) or similar for exact requirements.
As a simplified example, the size of current carrying conductors vs equipment/panel grounding conductors (note copper vs aluminum--AL needs heavier cable for "same" copper current ratings):
https://learnmetrics.com/ground-wire-size-chart-nec-grounding-conductor-size-chart/Size Of Copper Wire (AWG or kcmil): Copper Grounding Electrode Conductor Size (AWG or kcmil) 8 AWG Copper Wire 8 AWG Copper Ground Wire 6 AWG Copper Wire 8 AWG Copper Ground Wire 4 AWG Copper Wire 8 AWG Copper Ground Wire 3 AWG Copper Wire 8 AWG Copper Ground Wire 2 AWG Copper Wire 8 AWG Copper Ground Wire 1 AWG Copper Wire 6 AWG Copper Ground Wire 0 (1/0) AWG Copper Wire 6 AWG Copper Ground Wire 00 (2/0) AWG Copper Wire 4 AWG Copper Ground Wire 000 (3/0) AWG Copper Wire 4 AWG Copper Ground Wire 0000 (4/0) AWG Copper Wire 2 AWG Copper Ground Wire
The SMA manual should list the wiring requirements... But a quick math check:- 6,000 Watts * 1/0.85 AC inverter eff * 1/42 VDC battery cutoff voltage = 168 Amps max current
3/0 is certainly heavy enough cable (higher insulation temperature ratings, smaller AWG can be used).
Another issue to watch out for is cable resistance... ~!68 amps is a lot of current--And "too long" or "too small of AWG" cable can increase voltage drop and cause battery cutoff.
For example... 168 amps @ 3/0 cable @ 46.00 Batt voltage - 42.00 batt cutoff @ xxx feet?
https://www.calculator.net/voltage-drop-calculator.html?necmaterial=copper&necwiresize=6&necconduit=steel&necpf=1.&material=copper&wiresize=0.4066&resistance=1.2&resistanceunit=okm&voltage=46&phase=dc&noofconductor=1&distance=48&distanceunit=feet&eres=168&x=0&y=0&ctype=necResult for 48 feet of 3/0 cable @ 168 amps
Voltage drop: 4.03
Similar calculations for AC side...
Voltage drop percentage: 8.76%
Voltage at the end: 41.97- 6,000 Watts * 1/115 VAC nominal = 52 Amps max current
Note that a 48 volt @ 400 AH is a relatively small battery bank for a 6,000 Watt inverter... GEL batteries do have better high/surge current than flooded cell lead acid batteries.... Typically for a 6 kWatt inverter, would be suggesting a 600 AH@ 48 VDC battery bank minimum.
But the full answer also needs to know your planned loads (Watt*Hours per day, max surge WH, etc.).
Another possible issue--Look at the specifications for your GEL batteries. Max charging and discharging currents can be an issue... If these are your batteries:
https://www.renogy.com/deep-cycle-hybrid-gel-battery-12-volt-200ah/CHARGING PARAMETERSCharge Voltage: 13.6V~13.8V
Maximum Continuous Charging Current: 60A
Maximum Continuous Discharging Current: 20A
opc:
Standard Operation Temperature: 77°F±9°F(25°C±5°C)
Storage Temperature: -4~140°F/ -20°C~60°CThen 60 amps max charge rate per string (actually pretty high charge rate for GEL batteries) and 20 amp max continuous drain (pretty low for GEL batteries)--Almost looks like the battery charge/discharge spects have been reversed(???).
https://www.renogy.com/content/RBT200GEL12-G1/GEL200-Datasheet.pdf
The PDF (above link) has very different specifications (20 amp charging or 10%; discharging... Upwards of 3C or 600 amps discharge current).
Watch charging voltage (and current). In general GEL batteries do not like to be "over charged".
Thanks for all of the info! So I should run a DC ground and AC (main panel) ground to one single location?
What is confusing me the most is that there is currently no ground that I can see in the panel. There is a ground wire in the "generator room" outside the house but it's just coiled behind the breaker boxes and doesn't go to anything. A generator was always the only source of power. Does that explain why the coiled wire was never grounded to anything? -
"Generator Room"
Coiled ground going to nothing
8/3 Romex that runs from generator room to main panel (before I ran 6/2 from Inverter)
Inverter and batteries (30' from main panel)
Kris can you tell us a bit more about the Genset?120 or 120/240 VAC?Is your home 120 VAC only or do you have (or plan to use) 240 VAC applicants/well pumps too?It looks like your main panel is wired for 120/240 VAC and the inverter you have is 120 VAC only...Questions about Genset/inverter transfer switch?BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
I have a 9000 watt Champion generator that can run either 240 or 120 and I also just got a Honda EU3000is. The Honda is enough to run everything but the shallow well pump. I believe the Honda is only 120 but all I needed was an adapter to the large cord in the first pic.
I only plan on using 120VAC. This is a weekend type cabin. I installed a 120V shallow well pump, have a propane stove, small electric water heater no washer/dryer no AC etc... Just a real simple power usage. The biggest draw (excluding the pump) is probably the refrigerator which is about half the size of a normal fridge.